    cool liquid line



    cool liquid line from condenser on 404 static coil freezer with head master valve. sea water cooled condenser. 2 ton system, any thoughts? thanks d.d.



  2. #2
    Join Date
    Dec 2008
    Location
    UAE
    Age
    42
    Posts
    171
    Rep Power
    16

    Re: cool liquid line

    1. Over Charging ?????????
    2. System partial Chock ?????

    Thanks
    Amit

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46

    Re: cool liquid line

    Too much sea water flow through condenser.

    System turned off

    Blocked filter/drier.


    I'd be looking to see what temperatures and pressures its running at and compare these to what i would expect to see.

  4. #4
    Dave D.'s Avatar
    Dave D. Guest

    Re: cool liquid line

    new condenser. new drier, new valve, new piping, pressure 200 and 05. box at 0 .

  5. #5
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: cool liquid line

    Do you have a problem, or have you just got sub cooled liquid?

  6. #6
    Join Date
    Aug 2006
    Location
    Canada
    Age
    61
    Posts
    149
    Rep Power
    18

    Re: cool liquid line

    You are running with a headmaster valve, which is designed to maintain head pressure by reducing condensor size (through occupying parts of the condensor with liquid refrigerant)

    assuming low condensor cooling water temperature, condensor will be well flooded

    By the time the refrigerant exits the condensor it will be very subcooled.

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: cool liquid line

    Quote Originally Posted by Dave D. View Post
    cool liquid line from condenser on 404 static coil freezer with head master valve. sea water cooled condenser. 2 ton system, any thoughts? thanks d.d.
    "Cool liquid line" is not a temperature, it is an opinion.

  8. #8
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17

    Re: cool liquid line

    please let us know the temperatures of cooling water inlet to condenser, and outlet.
    Pressure at suction and discharge so that we can find the corresponding temperatures for R404
    It appears the low ambient may be cause or the system overcharged, but if it is overcharged both suction and discharge pressures will be high.

  9. #9
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: cool liquid line

    Quote Originally Posted by Sledge View Post
    You are running with a headmaster valve, which is designed to maintain head pressure by reducing condensor size (through occupying parts of the condensor with liquid refrigerant)

    assuming low condensor cooling water temperature, condensor will be well flooded

    By the time the refrigerant exits the condensor it will be very subcooled.
    hi i think sledge is correct ,assuming u didnt over charge, setting your head pressure corectly will make a big diffrence ,u should check for a clogged filter drier in liqued line !!
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  10. #10
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: cool liquid line

    Originally Posted by Dave D.
    cool liquid line from condenser on 404 static coil freezer with head master valve. sea water cooled condenser. 2 ton system, any thoughts? thanks d.d.
    Gary:
    "Cool liquid line" is not a temperature, it is an opinion.
    Classic...
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  11. #11
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: cool liquid line

    did you get ALL the nitrogen out?
    mmm to beer or not to beer...........lets drink breakfast

  12. #12
    Join Date
    Aug 2006
    Location
    Canada
    Age
    61
    Posts
    149
    Rep Power
    18

    Re: cool liquid line

    Quote Originally Posted by goshen View Post
    hi i think sledge is correct ,assuming u didnt over charge, setting your head pressure corectly will make a big diffrence ,u should check for a clogged filter drier in liqued line !!
    Thanks Goshen, but I was trying to say that I dont think there is a problem here.

    It is normal for a liquid line to be cold in a system operating in low ambient with a headmaster valve (or in this case operating with cold sea water cooling the condensor).

  13. #13
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: cool liquid line

    Quote Originally Posted by Sledge View Post
    Thanks Goshen, but I was trying to say that I dont think there is a problem here.

    It is normal for a liquid line to be cold in a system operating in low ambient with a headmaster valve (or in this case operating with cold sea water cooling the condensor).
    Correct Sledge

  14. #14
    Join Date
    Nov 2009
    Location
    riyadh(k.s.a)
    Posts
    14
    Rep Power
    0

    Re: cool liquid line

    Quote Originally Posted by mad fridgie View Post
    Correct Sledge
    sledge correct

  15. #15
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    19

    Re: cool liquid line

    Is the liquid line sweating ? If yes , partial blockage resulting in pressure drop & fall in temperature whereby liquid line is cool .

    Or else measure refrigerant outlet temp at condenser outlet & liquid line temp . Note the difference ; a difference of 3 to 5 k would be sub-cooling . Hence to stop further guess work , it would be appropriate to measure temps.

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. high liquid line pressure?
    By TECH TIM in forum Commercial
    Replies: 5
    Last Post: 09-05-2009, 05:36 PM
  3. Liquid line for multi evaporators
    By Kevin Yeo in forum Supermarket Refrigeration
    Replies: 1
    Last Post: 29-12-2005, 02:29 PM
  4. Parker levels in ammonia systems
    By Friobernal in forum Industrial
    Replies: 3
    Last Post: 04-08-2005, 03:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •