    Copeland Discus Disc failures



    I have a customer with 5 Low Temperature Century Low Temperature Condensing units and respective 10 evaporators. Electric defrost 3 per day temperature terminated default time set to 40 min. Each 6DT3-300E-TSK handles 1 evaporator, 2 Compressors per unit. We are breaking up the valve plates (the disc is blowing out) causing oil washout etc. I know this is caused by Slugging of refrigerant or oil. But we check on the units weekly and are keeping the return gas between 25 and 30 degree superheat, subcooling is 12 -16 degrees. I have removed oil to 1/3 sight glass. I now have a suction pressure and temperature recorder on the latest failure. Any suggestions?



  2. #2
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: Copeland Discus Disc failures

    Hi geno are you using the right valve plates ,because there are 2 different types,one has stronger springs behind the poppet and the other slightly soft spring,are you using genuine copeland plates or remanufactured.When the springs get hot they might become flat and cause the discharge poppet to bounce around in the plate and break up.

  3. #3
    Join Date
    Mar 2009
    Location
    New Zealand
    Posts
    10
    Rep Power
    0

    Re: Copeland Discus Disc failures

    have you checked your compression ratio?

  4. #4
    geno's Avatar
    geno Guest

    Re: Copeland Discus Disc failures

    I took apart the last failure and I've looked at alot of discus over the years and the spring seemed very soft. It's a remanufactured compressor and I'll bet it may have the wrong valve plate. Also my graphs are showing the compressor is leaking by during defrost to the tune of 4 times in 45 mins. Copland says 7 times in an hour is ok. Another problem is the sytem is still setup for low head operation 140# cutout for #1 condenser fan motor. 404A should be at 210#

  5. #5
    geno's Avatar
    geno Guest

    Re: Copeland Discus Disc failures

    mike
    I'll bet the low head is contributing to these failures. The latest info I found on these units has the head pressure settings at 200# and above. Thanks

  6. #6
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Copeland Discus Disc failures

    Do you think that the condenser fan is cutting out on too low a temp setting - so reducing condenser capacity, & ultimately raising suction pressure, hence discharge pressure/temp. So giving the disc a tough environment, leading to a softening of the spring?

  7. #7
    Join Date
    Sep 2009
    Location
    UK
    Age
    72
    Posts
    13
    Rep Power
    0

    Re: Copeland Discus Disc failures

    I know this is an old post but these compressor suction disc/reed damage is an old problem. you can catch them early before they do serious damage by checking the surface temp on the head above each piston, and they should all be about even at say 80c depending on operating conditions, if you get an odd temp thats a lot lower on one say 45 to 60c, it is a good indication of a cracked suction reed in the early stage

  8. #8
    Join Date
    Sep 2008
    Location
    Florida
    Age
    53
    Posts
    7
    Rep Power
    0

    Re: Copeland Discus Disc failures

    Quote Originally Posted by geno View Post
    I have a customer with 5 Low Temperature Century Low Temperature Condensing units and respective 10 evaporators. Electric defrost 3 per day temperature terminated default time set to 40 min. Each 6DT3-300E-TSK handles 1 evaporator, 2 Compressors per unit. We are breaking up the valve plates (the disc is blowing out) causing oil washout etc. I know this is caused by Slugging of refrigerant or oil. But we check on the units weekly and are keeping the return gas between 25 and 30 degree superheat, subcooling is 12 -16 degrees. I have removed oil to 1/3 sight glass. I now have a suction pressure and temperature recorder on the latest failure. Any suggestions?
    First of all make yourself clear, Do you have 2 evaporator per unit or two compressors per unit?

  9. #9
    Join Date
    Sep 2008
    Location
    Florida
    Age
    53
    Posts
    7
    Rep Power
    0

    Re: Copeland Discus Disc failures

    What kind of ambient temp this is running at, does it have crankcase heaters, how high above the evaporators are located,does it have pumpdown solenoid valves? make sure the TXV's are not affected by sub-cooling, it wiil tend to increase the mass flow rate in the evaporators causing floodbacks

  10. #10
    Join Date
    Sep 2008
    Location
    Florida
    Age
    53
    Posts
    7
    Rep Power
    0

    Re: Copeland Discus Disc failures

    Also COPELAND likes 30 to 40F compressor superheat, especially on Discus

Similar Threads

  1. Frick Premature Seal Failures
    By Steve Wright in forum Industrial Compressors
    Replies: 32
    Last Post: 11-06-2010, 02:34 PM
  2. Oil Regulator Failures
    By icv7 in forum Trouble Shooting
    Replies: 11
    Last Post: 19-06-2008, 08:33 PM
  3. IPM Failures
    By icecap in forum Air Conditioning
    Replies: 14
    Last Post: 07-08-2007, 09:51 PM
  4. High Disc Temp
    By road31 in forum Industrial
    Replies: 9
    Last Post: 15-09-2006, 08:47 AM
  5. Frequent Failures
    By abdulazman in forum Trouble Shooting
    Replies: 21
    Last Post: 08-01-2006, 07:40 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •