  #1  
Old 10-10-2009, 01:06 AM
Mike_w's Avatar
Mike_w Mike_w is online now
Registered User
Hey, I am new to : RE
 
Join Date: Oct 2009
Location: usa
Age: 27
Posts: 5
Rep Power: 0
Mike_w is on a distinguished road
Trane tracer Communications problems

Well I will do my best to explain the problem we seem to be experiencing. First off we have 3 Chillers on site, about 4 years ago from what I have heard they started to experience problems with communication with Unit 3 and Unit 1. They would reset the BCU by shutting off power and powering back on. Communications would stay on for about 4-6 and then drop out. Reading some of the work orders from Trane the BCU seemed to always have the diag. code F. I know they tried tons of things over the years as far as sending the DB out to tech support. swapping cards and upgrading the firmware. From what I have been told Unit 2 seems to be the best one.

As far as i understand the Communication link goes from the BCU to the PCM (ICS) then to the two chiller control panels(I forget what they call them).
I am now putting an effort forward to try to identify the problem and am turning the experts lol

I know Unit was the one that they were not able to communicate with at all for a long time so i started there today. I Swaped the COMM5 card and the ENET/BACNET interface card with Unit 2. Went to Unit 1 and Tried to swap the standard capacity card and the high capacity card with unit 2. When i did so I found out that Unit 1's high capacity card does not work so I put it back in unit one and will try to replace it when I get one.

Some things I noticed.
Today when I went to Unit 3 to start some testing the Diag. Code was 8 and that cleared when I cycled the BCU. On the UPCM the ICS LED indications ST1 TX and RX If I recall I remember seeing the ST1 LED have like one pulse then like a half pulse(a weak short pulse) then cylce over again with no RX or anything

all 3 chillers are suppose to be controlled by the tracer summit program in a control room if we had comm.... I know I have been jumping all over the place in this thread I hope someone can understand it



BCU is a BMTW000AA0A14440A87000
pcm IS A BTWU000AAA54542100000200

Some Images at
hxxp://s901,photobucket,com/albums/ac217/hoststuff/
Reply With Quote
  #2  
Old 10-10-2009, 01:24 AM
Magoo's Avatar
Magoo Magoo is offline
VIP Poster
 
Join Date: May 2007
Location: Auckland
Age: 59
Posts: 701
Rep Power: 3
Magoo is on a distinguished road
Re: Trane tracer Communications problems

Hi Mike W
I am not familar with your system, but sounds like a noise ( electrical ) problem. Common grounding/bonding with multiple systems is a real problem, analogue inputs, C/T inputs, digital inputs, contactors and snubbers, regulated power supplys are all just a start.
First to try is fitting and monitoring a power anyliser and plot power fluctuations, these days you can rent them, basically an oscyliscope with data trend logging.
Hoe this helps.
magoo
Reply With Quote
Sponsored links
  #3  
Old 10-10-2009, 08:36 AM
Lowrider's Avatar
Lowrider Lowrider is online now
VIP Poster
I am starting to push the Mods: of RE
 
Join Date: Aug 2003
Location: Netherlands
Age: 34
Posts: 597
Rep Power: 7
Lowrider is on a distinguished road
Re: Trane tracer Communications problems

F means failure during normal operation, 8 means unit in reset.

Can you tell me what comm boards are in the BCU? What type of chillers?

Do you know what image file is in the BCU?

Is the BCU communicating with an other BMS through BACnet/IP?
__________________
If it ain't broke, don't fix it!
Reply With Quote
  #4  
Old 10-10-2009, 05:50 PM
goshen's Avatar
goshen goshen is online now
regular poster
I am a friend of : RE
 
Join Date: Apr 2009
Location: israel
Age: 36
Posts: 177
Rep Power: 1
goshen is on a distinguished road
Re: Trane tracer Communications problems

Hi why dont u make a schematic of how your system is connected and post it then i think things will be a little easier to relate!
Reply With Quote
  #5  
Old 13-10-2009, 12:01 AM
Mike_w's Avatar
Mike_w Mike_w is online now
Registered User
Hey, I am new to : RE
 
Join Date: Oct 2009
Location: usa
Age: 27
Posts: 5
Rep Power: 0
Mike_w is on a distinguished road
Re: Trane tracer Communications problems

Quote:
Originally Posted by Magoo View Post
Hi Mike W
I am not familar with your system, but sounds like a noise ( electrical ) problem. Common grounding/bonding with multiple systems is a real problem, analogue inputs, C/T inputs, digital inputs, contactors and snubbers, regulated power supplys are all just a start.
First to try is fitting and monitoring a power anyliser and plot power fluctuations, these days you can rent them, basically an oscyliscope with data trend logging.
Hoe this helps.
magoo
I was on the exact same path your going with this becuase the Comm wires that communicate with two chiller control units are in the same cable tray as the 4160V for the motors but the only thing that threw me off was that it was fine for 4 years prior. And we "HAD" a nice portable scope meter but it was damaged either by transcat or UPS....... cause i guess we have another problem with the unit alarming of Phase inbalance i think it is. When it see a current differential of more then 5% that i wanted to look into with the scope meter.....


[quote=goshen]Hi why dont u make a schematic of how your system is connected and post it then i think things will be a little easier to relate![\quote]

I sure can when i get back to work but when you say connected do you mean communications wise? or power? or what? I did post a Image of the Comm print

Ill have to get back to you on the Comm card specs i dont know off the top of my head


And yes it uses BACNET
Reply With Quote
  #6  
Old 15-10-2009, 05:13 PM
Lowrider's Avatar
Lowrider Lowrider is online now
VIP Poster
I am starting to push the Mods: of RE
 
Join Date: Aug 2003
Location: Netherlands
Age: 34
Posts: 597
Rep Power: 7
Lowrider is on a distinguished road
Re: Trane tracer Communications problems

Quote:
Ill have to get back to you on the Comm card specs i dont know off the top of my head


And yes it uses BACNET
If it uses BACnet to an other vendor than Trane, please let me what image file is in the bcu and what vendor it's communicating with!

Have you had anyone from Trane over?

Had a look at the pictures. The Units have the UCP2 modules, so they communicate with the BCU through Comm3 (Trane Protocol).

The BCU only contains an Arcnet/ethernet card, a standard and high capacity card, a BCU I/o card and the comm 3 card.
__________________
If it ain't broke, don't fix it!

Last edited by Lowrider; 15-10-2009 at 05:18 PM..
Reply With Quote
  #7  
Old 17-10-2009, 01:28 AM
Mike_w's Avatar
Mike_w Mike_w is online now
Registered User
Hey, I am new to : RE
 
Join Date: Oct 2009
Location: usa
Age: 27
Posts: 5
Rep Power: 0
Mike_w is on a distinguished road
Re: Trane tracer Communications problems

There is no other vendor involved as far as i know the 3 units communicate with a trane tracer HMI program, And as far as pulling the image off the BCU I am not 100% sure I understand how to do that
Reply With Quote
  #8  
Old 17-10-2009, 01:38 AM
Magoo's Avatar
Magoo Magoo is offline
VIP Poster
 
Join Date: May 2007
Location: Auckland
Age: 59
Posts: 701
Rep Power: 3
Magoo is on a distinguished road
Re: Trane tracer Communications problems

Mike W
I am thinking that the current C/T's are a prime source of funny trips, particually if comms cables are trunked with high voltage motor cables, separate them if you can and ground them at the source only. Next change the current monitoring C/T's and replace with same ratio items and double check they are balanced.
hope this helps.
Reply With Quote
Sponsored links
  #9  
Old 17-10-2009, 08:11 AM
Lowrider's Avatar
Lowrider Lowrider is online now
VIP Poster
I am starting to push the Mods: of RE
 
Join Date: Aug 2003
Location: Netherlands
Age: 34
Posts: 597
Rep Power: 7
Lowrider is on a distinguished road
Re: Trane tracer Communications problems

Quote:
Originally Posted by Mike_w View Post
There is no other vendor involved as far as i know the 3 units communicate with a trane tracer HMI program, And as far as pulling the image off the BCU I am not 100% sure I understand how to do that
Go to Setup, site configuration, OK. Then you can see what version software is in it!
__________________
If it ain't broke, don't fix it!
Reply With Quote
  #10  
Old 07-11-2009, 06:30 PM
Mike_w's Avatar
Mike_w Mike_w is online now
Registered User
Hey, I am new to : RE
 
Join Date: Oct 2009
Location: usa
Age: 27
Posts: 5
Rep Power: 0
Mike_w is on a distinguished road
Re: Trane tracer Communications problems

Ok now to continue the troubleshoot process, I have been swamped with other things in the plant.
But the Image version is 16.086


Going
Reply With Quote
  #11  
Old 07-11-2009, 06:45 PM
Mike_w's Avatar
Mike_w Mike_w is online now
Registered User
Hey, I am new to : RE
 
Join Date: Oct 2009
Location: usa
Age: 27
Posts: 5
Rep Power: 0
Mike_w is on a distinguished road
Re: Trane tracer Communications problems

Ok back to the troubleshooting process, I have been swamped with other issues at the plant.

But the Image version is 16.086
Its a comm 4 card if you need the serial number or something else let me know

And going over the MANY trane work orders it appears they first said we had 300:5 and that we needed to go to 250:5
Then a month later they came out and said that our CTs are hooked up to the 250:5 tap and they need to be on the 200:5
Reply With Quote
  #12  
Old 07-11-2009, 09:53 PM
Lowrider's Avatar
Lowrider Lowrider is online now
VIP Poster
I am starting to push the Mods: of RE
 
Join Date: Aug 2003
Location: Netherlands
Age: 34
Posts: 597
Rep Power: 7
Lowrider is on a distinguished road
Re: Trane tracer Communications problems

Quote:
Originally Posted by Mike_w View Post

And going over the MANY trane work orders it appears they first said we had 300:5 and that we needed to go to 250:5
Then a month later they came out and said that our CTs are hooked up to the 250:5 tap and they need to be on the 200:5
Can you give me the model numbers, serial numbers of the chillers and compressors? Then I can see what are suppoused to be in!
__________________
If it ain't broke, don't fix it!
Reply With Quote
Sponsored links
Reply


Currently Active Users Viewing This Thread: 3 (1 members and 2 guests)
Mike_w
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
trane chiller problems. johnny cool Trouble Shooting 5 10-08-2009 08:22 PM
Trane Chiller Communications Triggerman Air Conditioning 0 02-02-2009 06:48 PM
New to Forum, Facing problems related with TRANE Chiller neerajpuranik Air Conditioning 3 10-12-2008 03:43 AM
Trane RTAD125 Problems Latte Trouble Shooting 9 14-12-2006 08:25 PM
Trane CGCE207 Problems AWCarillion Trouble Shooting 2 09-08-2005 08:58 AM


All times are GMT +1. The time now is 12:07 PM.

 

Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
This forum and its pages must not be copied or reprinted without the written consent of Refrigeration Engineer.com.
This forum is a free and open discussion board.
Refrigeration-Engineer.com, the administrators and Moderators of this site are not responsible for content posted here.Ad Management by RedTyger