  #1  
Old 07-11-2009, 01:41 AM
Niyo's Avatar
Niyo Niyo is offline
Registered User
Hey, I am new to : RE
 
Join Date: Nov 2009
Location: USA
Age: 25
Posts: 12
Rep Power: 0
Niyo is on a distinguished road
Unhappy Low side freezing

My main A/C system's (Marine grade, sea water condenser, 16 ton) low side from the TXV to the compressor is freezing up during the night/morning on the vessel I work in. It happens within minutes so it makes it very difficult to catch before it becomes critical. We normally run it around 240 psig high side and 53 psig low side. Once that certain time hits the high side will drop to 220 and low 38 causing it to frost over.

I just shut it down and let it sit for about 30 minutes to dethaw then turned it back on, it dropped back to the pressures at which it freezes then slowly climbed back up (I believe because of the increased heat in the vessel's air). I am still fairly new to refrigeration and troubleshooting, my senior's believe it is a faulty txv or the drier/filter. I wanted to ask any of you if there is any other possibilities before replacing the txv.
Reply With Quote
  #2  
Old 07-11-2009, 02:18 AM
Gary's Avatar
Gary Gary is online now
VIP Poster
 
Join Date: Apr 2001
Location: New Port Richey, Florida - USA
Age: 64
Posts: 3,525
Rep Power: 12
Gary will become famous soon enough
Re: Low side freezing

The pressures don't tell us anything if we don't know what refrigerant is in the system.

And the very first thing you should check is airflow.

What are the temperatures of the air entering and leaving the evap coil?
__________________
Author of TECH Method troubleshooting books
Reply With Quote
Sponsored links
  #3  
Old 07-11-2009, 02:43 AM
Niyo's Avatar
Niyo Niyo is offline
Registered User
Hey, I am new to : RE
 
Join Date: Nov 2009
Location: USA
Age: 25
Posts: 12
Rep Power: 0
Niyo is on a distinguished road
Re: Low side freezing

R-22 refrigerant and the air temps going into/out of the evaporator is in:72 out:64 Fahrenheit.
Reply With Quote
  #4  
Old 07-11-2009, 02:45 AM
Niyo's Avatar
Niyo Niyo is offline
Registered User
Hey, I am new to : RE
 
Join Date: Nov 2009
Location: USA
Age: 25
Posts: 12
Rep Power: 0
Niyo is on a distinguished road
Re: Low side freezing

Oh ya airflow is good
Reply With Quote
  #5  
Old 07-11-2009, 02:50 AM
Gary's Avatar
Gary Gary is online now
VIP Poster
 
Join Date: Apr 2001
Location: New Port Richey, Florida - USA
Age: 64
Posts: 3,525
Rep Power: 12
Gary will become famous soon enough
Re: Low side freezing

Next check the subcooling. We need to know the liquid line temp near the receiver outlet, the liquid line temp near the TXV inlet and the current high side pressure.
__________________
Author of TECH Method troubleshooting books
Reply With Quote
  #6  
Old 07-11-2009, 03:12 AM
Niyo's Avatar
Niyo Niyo is offline
Registered User
Hey, I am new to : RE
 
Join Date: Nov 2009
Location: USA
Age: 25
Posts: 12
Rep Power: 0
Niyo is on a distinguished road
Re: Low side freezing

txv inlet is 86 degrees, receiver outlet is 55 degrees, and high side pressure is 225 psig
Reply With Quote
  #7  
Old 07-11-2009, 03:22 AM
Gary's Avatar
Gary Gary is online now
VIP Poster
 
Join Date: Apr 2001
Location: New Port Richey, Florida - USA
Age: 64
Posts: 3,525
Rep Power: 12
Gary will become famous soon enough
Re: Low side freezing

I assume we are talking degrees F, not C?
__________________
Author of TECH Method troubleshooting books
Reply With Quote
  #8  
Old 07-11-2009, 03:27 AM
Niyo's Avatar
Niyo Niyo is offline
Registered User
Hey, I am new to : RE
 
Join Date: Nov 2009
Location: USA
Age: 25
Posts: 12
Rep Power: 0
Niyo is on a distinguished road
Re: Low side freezing

Yes F not C, I apologize. I am tired.
Reply With Quote
Sponsored links
  #9  
Old 07-11-2009, 03:32 AM
Gary's Avatar
Gary Gary is online now
VIP Poster
 
Join Date: Apr 2001
Location: New Port Richey, Florida - USA
Age: 64
Posts: 3,525
Rep Power: 12
Gary will become famous soon enough
Re: Low side freezing

The system has plenty of refrigerant... if anything maybe too much.

Now we need to check the superheat. We need to know the suction line temp at the TXV bulb and the current low side pressure.
__________________
Author of TECH Method troubleshooting books
Reply With Quote
  #10  
Old 07-11-2009, 05:46 PM
Gary's Avatar
Gary Gary is online now
VIP Poster
 
Join Date: Apr 2001
Location: New Port Richey, Florida - USA
Age: 64
Posts: 3,525
Rep Power: 12
Gary will become famous soon enough
Re: Low side freezing

Quote:
Originally Posted by Niyo View Post
txv inlet is 86 degrees, receiver outlet is 55 degrees, and high side pressure is 225 psig
I would insulate that liquid line. It is picking up way too much heat along the way. This is not the cause of your problems, but insulating the line will increase efficiency.

At this point the primary suspect is plugged inlet screen on the TXV.
__________________
Author of TECH Method troubleshooting books
Reply With Quote
  #11  
Old 07-11-2009, 07:44 PM
Niyo's Avatar
Niyo Niyo is offline
Registered User
Hey, I am new to : RE
 
Join Date: Nov 2009
Location: USA
Age: 25
Posts: 12
Rep Power: 0
Niyo is on a distinguished road
Re: Low side freezing

thank you, alot of my responsibilities are on the job and I greatly appreciate the help/knowledge
Reply With Quote
  #12  
Old 07-11-2009, 07:57 PM
Gary's Avatar
Gary Gary is online now
VIP Poster
 
Join Date: Apr 2001
Location: New Port Richey, Florida - USA
Age: 64
Posts: 3,525
Rep Power: 12
Gary will become famous soon enough
Re: Low side freezing

I'm wondering why the receiver outlet is so cold. Is the room temp that cold? Is the condenser outlet that cold?
__________________
Author of TECH Method troubleshooting books
Reply With Quote
Sponsored links
  #13  
Old 07-11-2009, 08:02 PM
Niyo's Avatar
Niyo Niyo is offline
Registered User
Hey, I am new to : RE
 
Join Date: Nov 2009
Location: USA
Age: 25
Posts: 12
Rep Power: 0
Niyo is on a distinguished road
Re: Low side freezing

The vessel's house air is approx 60ish-70ish degrees Fahrenheit. We tried adjusting the thermostat up to allow the compressor some breaks in between freezes but on a vessel the crew is not to happy when they are sweating. The temp of the space that the 16ton is in is in the 80-90's.
Reply With Quote
  #14  
Old 07-11-2009, 08:06 PM
Gary's Avatar
Gary Gary is online now
VIP Poster
 
Join Date: Apr 2001
Location: New Port Richey, Florida - USA
Age: 64
Posts: 3,525
Rep Power: 12
Gary will become famous soon enough
Re: Low side freezing

What I'm wondering about is how that receiver outlet got to 55F? The only way that line temp could drop lower than its surroundings is if it is restricting. What is the liquid line temp at the condenser outlet?
__________________
Author of TECH Method troubleshooting books
Reply With Quote
  #15  
Old 07-11-2009, 08:26 PM
Niyo's Avatar
Niyo Niyo is offline
Registered User
Hey, I am new to : RE
 
Join Date: Nov 2009
Location: USA
Age: 25
Posts: 12
Rep Power: 0
Niyo is on a distinguished road
Re: Low side freezing

I am retarded, our accumulator is right next to the receiver, same shape and everything but condenser outlet is 78 degrees F and receiver outlet is 90 degrees F. I hit the accumulator outlet the first time
Reply With Quote
  #16  
Old 07-11-2009, 09:09 PM
mad fridgie's Avatar
mad fridgie mad fridgie is online now
Veteran Poster
 
Join Date: Aug 2009
Location: New Zealand
Age: 45
Posts: 356
Rep Power: 1
mad fridgie will become famous soon enough
Re: Low side freezing

Many boats us AEV (AXV) not TEV (TXV) can you confirm that you actually have a TEV (has a sensor bulb on the evap outlet)
Reply With Quote
Sponsored links
  #17  
Old 07-11-2009, 09:12 PM
Niyo's Avatar
Niyo Niyo is offline
Registered User
Hey, I am new to : RE
 
Join Date: Nov 2009
Location: USA
Age: 25
Posts: 12
Rep Power: 0
Niyo is on a distinguished road
Re: Low side freezing

yes the sensor bulb is on the evap outlet
Reply With Quote
  #18  
Old 07-11-2009, 09:19 PM
mad fridgie's Avatar
mad fridgie mad fridgie is online now
Veteran Poster
 
Join Date: Aug 2009
Location: New Zealand
Age: 45
Posts: 356
Rep Power: 1
mad fridgie will become famous soon enough
Re: Low side freezing

Good, Do you have a control valve on the water at the condensor (small pipe form compressor or condensor is also connected)
Reply With Quote
  #19  
Old 07-11-2009, 09:21 PM
Niyo's Avatar
Niyo Niyo is offline
Registered User
Hey, I am new to : RE
 
Join Date: Nov 2009
Location: USA
Age: 25
Posts: 12
Rep Power: 0
Niyo is on a distinguished road
Re: Low side freezing

ya if it still works, this system is old and needs upgraded
Reply With Quote
  #20  
Old 07-11-2009, 09:28 PM
mad fridgie's Avatar
mad fridgie mad fridgie is online now
Veteran Poster
 
Join Date: Aug 2009
Location: New Zealand
Age: 45
Posts: 356
Rep Power: 1
mad fridgie will become famous soon enough
Re: Low side freezing

Quote:
Originally Posted by Niyo View Post
ya if it still works, this system is old and needs upgraded
From what you have indicated I would say you have a problem here.
What I want you to do is to wind in this valve (along way) this will make your head pressure rise. (if not totally goosed) If it does make a presure difference, then wind in and out, then reset.
Reduce the water pressure entering the condensor slightly.
Reply With Quote
  #21  
Old 07-11-2009, 09:40 PM
Niyo's Avatar
Niyo Niyo is offline
Registered User
Hey, I am new to : RE
 
Join Date: Nov 2009
Location: USA
Age: 25
Posts: 12
Rep Power: 0
Niyo is on a distinguished road
Re: Low side freezing

I will have to try that tomorrow unless I get woke up tonight over the low side freezing. I believe that valve may need some work to cooperate. Thanks.
Reply With Quote
  #22  
Old 07-11-2009, 09:51 PM
mad fridgie's Avatar
mad fridgie mad fridgie is online now
Veteran Poster
 
Join Date: Aug 2009
Location: New Zealand
Age: 45
Posts: 356
Rep Power: 1
mad fridgie will become famous soon enough
Re: Low side freezing

If you are lucky it may just be seized.
More than likely the seat is "drawn" (lots of scratches) which is allowing to much water through. Good luck?
Reply With Quote
  #23  
Old 07-11-2009, 10:46 PM
Gary's Avatar
Gary Gary is online now
VIP Poster
 
Join Date: Apr 2001
Location: New Port Richey, Florida - USA
Age: 64
Posts: 3,525
Rep Power: 12
Gary will become famous soon enough
Re: Low side freezing

I'm still betting on the TXV inlet screen.
__________________
Author of TECH Method troubleshooting books
Reply With Quote
  #24  
Old 07-11-2009, 10:52 PM
Niyo's Avatar
Niyo Niyo is offline
Registered User
Hey, I am new to : RE
 
Join Date: Nov 2009
Location: USA
Age: 25
Posts: 12
Rep Power: 0
Niyo is on a distinguished road
Re: Low side freezing

Quote:
Originally Posted by Gary View Post
I'm still betting on the TXV inlet screen.
I bet your right, we are trying to get a new condenser fabricated since we cannot buy a replacement (to out of date), so when we do that we are taking out the TXV. Just trying to see if there are ways to manage this problem a little easier or else anything else we have left out of our T/S. Thanks everyone for the help.
Reply With Quote
Sponsored links
  #25  
Old 08-11-2009, 12:24 AM
Magoo's Avatar
Magoo Magoo is offline
VIP Poster
 
Join Date: May 2007
Location: Auckland
Age: 59
Posts: 701
Rep Power: 3
Magoo is on a distinguished road
Re: Low side freezing

Chilled water regulation control at plant room not fine enough, check dead band control. Step unloading is not reacting quickly enough, so chilled water temp drops and suction pressure drops and you risk freezing chiller HX, being an older system the controls will have been played with by everyone twisting knobs etc., start again and re-commission system controls, double check condenser water control valves and regulators as well.
Reply With Quote
Sponsored links
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Raising GE side by side for ventilation? sandcruiser Domestic 2 12-09-2009 07:45 PM
Quick freeze in brine solultion vs blast freezing seafood?? lhwang78 Commercial 5 25-09-2008 10:08 PM
samsung side by side sr-s2028css sork Technical Discussions 2 26-06-2008 09:06 PM
High Side Pressure is ... SULTAN Trouble Shooting 5 14-08-2007 12:53 PM


All times are GMT +1. The time now is 09:10 AM.

 

Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
This forum and its pages must not be copied or reprinted without the written consent of Refrigeration Engineer.com.
This forum is a free and open discussion board.
Refrigeration-Engineer.com, the administrators and Moderators of this site are not responsible for content posted here.Ad Management by RedTyger