Re: two stage verses economized single stage
Segei brings up a good point here. Slide valve position provided by the indication (display or dial gauge) is not equal to the same percentage of capacity.
Depending on the compressor the 90% indicated could be just enough to cause the compressor to be operating where the side port is uncovered. This can affect the economizer (will need back-pressure regulators to maintain the economizer temperature/pressure).
The slide valve position can drastically affect the part load performance also. It may not be just 4% penalty. It could be more as it depends on the actual capacity developed by the compressor at the indicated slide position and the resulting power input.