Thread: overload problem
-
26-10-2009, 05:25 PM #1
overload problem
my liquid cooled york chiller ykbbbdp5 is working with 100-102%FLA, under high suction and discharge pressure,low superheat(2-3 degC), NO GOOD LEAVING TEMP(9-10DEGC) and the discharge temp is about 37 degc.the vanes are 100-85% openning.
How to get a good leaving temp(7degc setpoint) with a good current load?
If the cause is refrigerant overcharging, how to process to remove some refrigerant from the system while the chiller is working?
-
26-10-2009, 05:39 PM #2
Re: overload problem
Which refrigerant is in the system?
-
27-10-2009, 11:09 AM #3
Re: overload problem
the refrigerant is 134a
-
27-10-2009, 07:50 PM #4
Re: overload problem
In that case, connect your recycle unit to the suction port and start pumping out the refrigerant until you get bubles in the sight glass.
Let the unit balance to see if you need to add or empty refrigerant.
-
27-10-2009, 07:56 PM #5
Re: overload problem
THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
-
04-11-2009, 01:34 PM #6
Re: overload problem
subcooling=7.4degc
Similar Threads
-
problem with GE air con power problem
By Richie101 in forum Air ConditioningReplies: 6Last Post: 05-11-2009, 04:00 PM -
Current Overload Trip
By Meer Abdulrehma in forum Trouble ShootingReplies: 7Last Post: 19-10-2009, 03:29 PM -
Samsung Vivace Problem AQV24VBCN
By goldpau in forum Air ConditioningReplies: 0Last Post: 18-09-2009, 06:28 PM -
Saunier Duval Problem
By mallorcanangel in forum Air ConditioningReplies: 1Last Post: 10-07-2009, 01:26 AM -
Furance problem
By ALONEI in forum Trouble ShootingReplies: 10Last Post: 14-05-2008, 11:32 AM