Results 1 to 6 of 6
  1. #1
    bah.koko's Avatar
    bah.koko Guest

    Question overload problem



    my liquid cooled york chiller ykbbbdp5 is working with 100-102%FLA, under high suction and discharge pressure,low superheat(2-3 degC), NO GOOD LEAVING TEMP(9-10DEGC) and the discharge temp is about 37 degc.the vanes are 100-85% openning.
    How to get a good leaving temp(7degc setpoint) with a good current load?
    If the cause is refrigerant overcharging, how to process to remove some refrigerant from the system while the chiller is working?



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: overload problem

    Which refrigerant is in the system?

  3. #3
    bah.koko's Avatar
    bah.koko Guest

    Re: overload problem

    the refrigerant is 134a

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: overload problem

    In that case, connect your recycle unit to the suction port and start pumping out the refrigerant until you get bubles in the sight glass.

    Let the unit balance to see if you need to add or empty refrigerant.

  5. #5
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: overload problem

    Quote Originally Posted by bah.koko View Post
    my liquid cooled york chiller ykbbbdp5 is working with 100-102%FLA, under high suction and discharge pressure,low superheat(2-3 degC), NO GOOD LEAVING TEMP(9-10DEGC) and the discharge temp is about 37 degc.the vanes are 100-85% openning.
    How to get a good leaving temp(7degc setpoint) with a good current load?
    If the cause is refrigerant overcharging, how to process to remove some refrigerant from the system while the chiller is working?
    Hi there
    what is your subcooling??
    before u remove gas check this factor it will tell u exactly if u are over charged!!
    what is ambient temp ?
    i assume unit is air cooled are condenser coiles clean??
    what is water drop on evap??
    what is your delta -t??
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  6. #6
    bah.koko's Avatar
    bah.koko Guest

    Re: overload problem

    subcooling=7.4degc

Similar Threads

  1. problem with GE air con power problem
    By Richie101 in forum Air Conditioning
    Replies: 6
    Last Post: 05-11-2009, 04:00 PM
  2. Current Overload Trip
    By Meer Abdulrehma in forum Trouble Shooting
    Replies: 7
    Last Post: 19-10-2009, 03:29 PM
  3. Samsung Vivace Problem AQV24VBCN
    By goldpau in forum Air Conditioning
    Replies: 0
    Last Post: 18-09-2009, 06:28 PM
  4. Saunier Duval Problem
    By mallorcanangel in forum Air Conditioning
    Replies: 1
    Last Post: 10-07-2009, 01:26 AM
  5. Furance problem
    By ALONEI in forum Trouble Shooting
    Replies: 10
    Last Post: 14-05-2008, 11:32 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •