Results 1 to 10 of 10
Thread: serve over chiller
-
21-10-2009, 05:10 PM #1
serve over chiller
would like to know how to chang temperature setting on serve over display cabinet,buttons at left hand are arrow pointing upwards and arrow pointing downwards,at right arrow pointing straight right and snowflake symbol.Problem is drip tray at top is freezing solid then overflowing.Thanks
-
21-10-2009, 11:02 PM #2
Re: serve over chiller
Any name on the display itself?
LAE, Eliwell, Dixell etcBrian - Newton Abbot, Devon, UK
Retired March 2015
-
22-10-2009, 05:51 PM #3
Re: serve over chiller
Frilixa,But that could be seller rather than manufacturer
-
22-10-2009, 10:56 PM #4
Re: serve over chiller
Folco.
sounds like the condensate drain is blocked, and if icing drain tray up, then set point on chiller is too cold.
Does controller have a set button?.
try www.frilixa.comLast edited by Magoo; 22-10-2009 at 11:02 PM. Reason: addition
-
23-10-2009, 06:10 PM #5
Re: serve over chiller
no set button,just buttons as described in previous post.thanks for reply.
-
24-10-2009, 12:21 AM #6
Re: serve over chiller
Hi Folco.
Sounds like a re-badged Danfoss EKC controller, but then I could be wrong, quite often the case.
Did you try and clear the condensate drain?.
Did you check the web site suggested?.
Try and hold both up and down arrows at same time for period of say 5 seconds, and what happens.
-
24-10-2009, 05:36 PM #7
Re: serve over chiller
yes,cleaned out drain hole.Will try holding both buttons,thanks for your help.PS bottom setting at 4 degrees,top at 6,is this ok?
-
25-10-2009, 01:10 AM #8
Re: serve over chiller
Hi Folco.
sounds about right, could be a case that the controller relay has failed closed and keeping the unit cooling, hence freezing problem.
I will see if I can find and send to you a set-up brochure. Can anyone else help with this, open question.
martin
-
25-10-2009, 05:34 PM #9
Re: serve over chiller
does go off and into defrost mode then back on regularly
-
30-10-2009, 06:04 PM #10
Re: serve over chiller
holding buttons for 5 seconds worked ok.thanks for info
Similar Threads
-
process chiller help
By talon771 in forum IndustrialReplies: 8Last Post: 12-01-2011, 08:42 PM -
Absorption Chiller VS Mech. Chiller
By Intern in forum IndustrialReplies: 20Last Post: 30-05-2009, 08:31 AM -
York Chiller startup when on Emergency Power
By Apollo10 in forum Trouble ShootingReplies: 3Last Post: 22-12-2008, 07:13 PM -
Trane CVHE 450 R11 Centrifugal Chiller
By albertjoseph in forum Air ConditioningReplies: 4Last Post: 06-10-2008, 03:23 PM