15-10-2009, 10:14 AM
|
 |
Veteran Poster
|
|
Join Date: Aug 2009
Location: New Zealand
Age: 45
Posts: 358
Rep Power: 1
|
|
|
Re: Refrigeration 101
Quote:
Originally Posted by ianparker0801
Thanks for you help gary, it all helps when trying to apply the theory to practical application. My next question is about high pressure and low pressure cut outs. How do you go about testing these safety features, on both courses we were told to check these but noone has ever said how.
|
Pressure switches can be tested with a nitrogen via a regulator/gauge, Raise pressure until switch changes. make a note of actual pressure, then slowly release until switch changes back. Adjust until you reach desired set points. "Note" the scale are indicators only, for rough adjustment.
On site, you sort of break a few rules, for HP (discharge) you "slowly" close discharge valve, keeping a very close eye on your gauge. Hp switch will trip (at some set point). (if manual reset then no other settings to check) if auto reset then watch as the pressure drops note switch change, for LP similar process but switch is is opposite direction
|

15-10-2009, 05:22 PM
|
 |
regular poster
I am a friend of : RE
|
|
Join Date: Apr 2009
Location: israel
Age: 36
Posts: 177
Rep Power: 1
|
|
|
Re: Refrigeration 101
hi garry very nice thread should answer a lot of newbies questions!!!
|

15-10-2009, 07:10 PM
|
 |
VIP Poster
|
|
Join Date: Apr 2001
Location: New Port Richey, Florida - USA
Age: 64
Posts: 3,525
Rep Power: 12
|
|
|
Re: Refrigeration 101
Don't forget to click the reputation button. 
__________________
Author of TECH Method troubleshooting books
|

18-10-2009, 01:12 AM
|
 |
rookie poster
|
|
Join Date: Sep 2008
Location: Australia
Posts: 16
Rep Power: 0
|
|
|
Re: Refrigeration 101
It's really useful, Garry. After 1 year of self-learning, you give me have a chance to review what I have been done and believe were right or not.
Can you write something about system balancing (using captube) and how to get the max cooling capacity out of the component we have? Or say how to tune a unit?
How the excessive Cond airflow and/or Evap airflow can bring the Capacity down? It looks like I have more SC, lower HP, so I can add more charge to control SH after drawing the Capacity line against charge amount. But it made no sense as I did not get what I had.
Capacity has always been a problem of mine since I started playing
Thanks, Gary
|

18-10-2009, 04:15 AM
|
 |
VIP Poster
|
|
Join Date: Apr 2001
Location: New Port Richey, Florida - USA
Age: 64
Posts: 3,525
Rep Power: 12
|
|
|
Re: Refrigeration 101
Insufficient (not excessive) airflow brings down capacity.
__________________
Author of TECH Method troubleshooting books
|

24-10-2009, 06:25 AM
|
 |
Registered User
Hey, I am new to : RE
|
|
Join Date: Oct 2009
Location: malaysia
Posts: 2
Rep Power: 0
|
|
|
Re: Refrigeration 101
In Freezer with capilary as metering devices, how to determine if the system is overcharged or less charged with a refirgerant? Can we decide this base on the suction line temp., discharge line temp./ before filter dryer temp.?
|

24-10-2009, 07:14 AM
|
 |
Registered User
Hey, I am new to : RE
|
|
Join Date: Oct 2009
Location: malaysia
Posts: 2
Rep Power: 0
|
|
|
Re: Refrigeration 101
Hi Gary,
I've a question for you. In Freezer system, how we can determine whether the system is overcharged or less charged base on the suction line temperature (evaporator in / out), accumulator out temperature, before filter dryer temperature, discharge line temperature? Let say the system is unsing capilalry as the metering device. Hope you can give me some hints regarding this.
|

24-10-2009, 08:30 AM
|
 |
VIP Poster
I am starting to push the Mods: of RE
|
|
Join Date: Sep 2007
Location: Split Croatia
Age: 43
Posts: 4,151
Rep Power: 8
|
|
|
Re: Refrigeration 101
Quote:
Originally Posted by shaafeq
In Freezer with capilary as metering devices, how to determine if the system is overcharged or less charged with a refirgerant? Can we decide this base on the suction line temp., discharge line temp./ before filter dryer temp.?
|
Before/or filter dryer temperature will tell the difference.
In a system that is short of refrigerant the condenser would have a gradual change in temperature from the top all the way down to the strainer. In fact the strainer will be slightly above room temperature.
In a system that is overcharged strainer will be at same tamperature as lower part off condenser.
http://www.supco.com/images/pdfs/Man...g%20Manual.pdf
__________________
This is signature folks!
There's no such thing as a dumb question..............
But they are the easiest to answer.
------------------------
Quis? Quid? Ubi? Quibus auxiliis? Cur? Quomodo? Quando?
------------------------
Si tacuisses,philosophus mansisses.
Last edited by nike123; 24-10-2009 at 08:36 AM..
|

24-10-2009, 04:05 PM
|
 |
VIP Poster
|
|
Join Date: Apr 2001
Location: New Port Richey, Florida - USA
Age: 64
Posts: 3,525
Rep Power: 12
|
|
|
Re: Refrigeration 101
Most accurate would be to weigh in the charge.
__________________
Author of TECH Method troubleshooting books
|

30-10-2009, 09:15 AM
|
 |
Registered User
Hey, I am new to : RE
|
|
Join Date: Jan 2009
Location: Kuwait
Posts: 1
Rep Power: 0
|
|
|
Re: Refrigeration 101
Hi All
I have one question recently I worked with vendor of FES Screw Chiller with 20,000kg of R 134a ref charged and 800 gallon of Lubricnt oil . Now i am envolved in commissioning of another chiller it has a Propane gas charging can some body tell me what will be the running parameters with Propane Refrigerant
|

30-10-2009, 04:23 PM
|
 |
VIP Poster
I am starting to push the Mods: of RE
|
|
Join Date: Sep 2007
Location: Split Croatia
Age: 43
Posts: 4,151
Rep Power: 8
|
|
|
Re: Refrigeration 101
Quote:
Originally Posted by Gurdev Singh
Hi All
I have one question recently I worked with vendor of FES Screw Chiller with 20,000kg of R 134a ref charged and 800 gallon of Lubricnt oil . Now i am envolved in commissioning of another chiller it has a Propane gas charging can some body tell me what will be the running parameters with Propane Refrigerant
|
Parameters will be same in temperatures as with R134a. Pressure will be saturation temperatures of Propane converted to pressures.
__________________
This is signature folks!
There's no such thing as a dumb question..............
But they are the easiest to answer.
------------------------
Quis? Quid? Ubi? Quibus auxiliis? Cur? Quomodo? Quando?
------------------------
Si tacuisses,philosophus mansisses.
|
 |
|
|
Currently Active Users Viewing This Thread: 5 (0 members and 5 guests)
|
|
|
| Thread Tools |
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
All times are GMT +1. The time now is 06:42 AM.
|