Old 15-10-2009, 10:14 AM
mad fridgie's Avatar
mad fridgie mad fridgie is online now
Veteran Poster
 
Join Date: Aug 2009
Location: New Zealand
Age: 45
Posts: 358
Rep Power: 1
mad fridgie will become famous soon enough
Re: Refrigeration 101

Quote:
Originally Posted by ianparker0801 View Post
Thanks for you help gary, it all helps when trying to apply the theory to practical application. My next question is about high pressure and low pressure cut outs. How do you go about testing these safety features, on both courses we were told to check these but noone has ever said how.
Pressure switches can be tested with a nitrogen via a regulator/gauge, Raise pressure until switch changes. make a note of actual pressure, then slowly release until switch changes back. Adjust until you reach desired set points. "Note" the scale are indicators only, for rough adjustment.
On site, you sort of break a few rules, for HP (discharge) you "slowly" close discharge valve, keeping a very close eye on your gauge. Hp switch will trip (at some set point). (if manual reset then no other settings to check) if auto reset then watch as the pressure drops note switch change, for LP similar process but switch is is opposite direction
Reply With Quote
  #102  
Old 15-10-2009, 05:22 PM
goshen's Avatar
goshen goshen is offline
regular poster
I am a friend of : RE
 
Join Date: Apr 2009
Location: israel
Age: 36
Posts: 177
Rep Power: 1
goshen is on a distinguished road
Re: Refrigeration 101

hi garry very nice thread should answer a lot of newbies questions!!!
Reply With Quote
  #103  
Old 15-10-2009, 07:10 PM
Gary's Avatar
Gary Gary is online now
VIP Poster
 
Join Date: Apr 2001
Location: New Port Richey, Florida - USA
Age: 64
Posts: 3,525
Rep Power: 12
Gary will become famous soon enough
Re: Refrigeration 101

Don't forget to click the reputation button.
__________________
Author of TECH Method troubleshooting books
Reply With Quote
  #104  
Old 18-10-2009, 01:12 AM
Uni's Avatar
Uni Uni is offline
rookie poster
 
Join Date: Sep 2008
Location: Australia
Posts: 16
Rep Power: 0
Uni is on a distinguished road
Re: Refrigeration 101

It's really useful, Garry. After 1 year of self-learning, you give me have a chance to review what I have been done and believe were right or not.

Can you write something about system balancing (using captube) and how to get the max cooling capacity out of the component we have? Or say how to tune a unit?

How the excessive Cond airflow and/or Evap airflow can bring the Capacity down? It looks like I have more SC, lower HP, so I can add more charge to control SH after drawing the Capacity line against charge amount. But it made no sense as I did not get what I had.

Capacity has always been a problem of mine since I started playing

Thanks, Gary
Reply With Quote
Sponsored links
  #105  
Old 18-10-2009, 04:15 AM
Gary's Avatar
Gary Gary is online now
VIP Poster
 
Join Date: Apr 2001
Location: New Port Richey, Florida - USA
Age: 64
Posts: 3,525
Rep Power: 12
Gary will become famous soon enough
Re: Refrigeration 101

Insufficient (not excessive) airflow brings down capacity.
__________________
Author of TECH Method troubleshooting books
Reply With Quote
  #106  
Old 24-10-2009, 06:25 AM
shaafeq's Avatar
shaafeq shaafeq is offline
Registered User
Hey, I am new to : RE
 
Join Date: Oct 2009
Location: malaysia
Posts: 2
Rep Power: 0
shaafeq is on a distinguished road
Re: Refrigeration 101

In Freezer with capilary as metering devices, how to determine if the system is overcharged or less charged with a refirgerant? Can we decide this base on the suction line temp., discharge line temp./ before filter dryer temp.?
Reply With Quote
  #107  
Old 24-10-2009, 07:14 AM
shaafeq's Avatar
shaafeq shaafeq is offline
Registered User
Hey, I am new to : RE
 
Join Date: Oct 2009
Location: malaysia
Posts: 2
Rep Power: 0
shaafeq is on a distinguished road
Re: Refrigeration 101

Hi Gary,

I've a question for you. In Freezer system, how we can determine whether the system is overcharged or less charged base on the suction line temperature (evaporator in / out), accumulator out temperature, before filter dryer temperature, discharge line temperature? Let say the system is unsing capilalry as the metering device. Hope you can give me some hints regarding this.
Reply With Quote
  #108  
Old 24-10-2009, 08:30 AM
nike123's Avatar
nike123 nike123 is online now
VIP Poster
I am starting to push the Mods: of RE
 
Join Date: Sep 2007
Location: Split Croatia
Age: 43
Posts: 4,151
Rep Power: 8
nike123 will become famous soon enoughnike123 will become famous soon enough
Re: Refrigeration 101

Quote:
Originally Posted by shaafeq View Post
In Freezer with capilary as metering devices, how to determine if the system is overcharged or less charged with a refirgerant? Can we decide this base on the suction line temp., discharge line temp./ before filter dryer temp.?
Before/or filter dryer temperature will tell the difference.


In a system that is short of refrigerant the condenser would have a gradual change in temperature from the top all the way down to the strainer. In fact the strainer will be slightly above room temperature.

In a system that is overcharged strainer will be at same tamperature as lower part off condenser.

http://www.supco.com/images/pdfs/Man...g%20Manual.pdf
__________________
This is signature folks!

There's no such thing as a dumb question..............
But they are the easiest to answer.

------------------------
Quis? Quid? Ubi? Quibus auxiliis? Cur? Quomodo? Quando?

------------------------
Si tacuisses,philosophus mansisses.

Last edited by nike123; 24-10-2009 at 08:36 AM..
Reply With Quote
  #109  
Old 24-10-2009, 04:05 PM
Gary's Avatar
Gary Gary is online now
VIP Poster
 
Join Date: Apr 2001
Location: New Port Richey, Florida - USA
Age: 64
Posts: 3,525
Rep Power: 12
Gary will become famous soon enough
Re: Refrigeration 101

Most accurate would be to weigh in the charge.
__________________
Author of TECH Method troubleshooting books
Reply With Quote
  #110  
Old 30-10-2009, 09:15 AM
Gurdev Singh's Avatar
Gurdev Singh Gurdev Singh is offline
Registered User
Hey, I am new to : RE
 
Join Date: Jan 2009
Location: Kuwait
Posts: 1
Rep Power: 0
Gurdev Singh is on a distinguished road
Re: Refrigeration 101

Hi All
I have one question recently I worked with vendor of FES Screw Chiller with 20,000kg of R 134a ref charged and 800 gallon of Lubricnt oil . Now i am envolved in commissioning of another chiller it has a Propane gas charging can some body tell me what will be the running parameters with Propane Refrigerant
Reply With Quote
  #111  
Old 30-10-2009, 04:23 PM
nike123's Avatar
nike123 nike123 is online now
VIP Poster
I am starting to push the Mods: of RE
 
Join Date: Sep 2007
Location: Split Croatia
Age: 43
Posts: 4,151
Rep Power: 8
nike123 will become famous soon enoughnike123 will become famous soon enough
Re: Refrigeration 101

Quote:
Originally Posted by Gurdev Singh View Post
Hi All
I have one question recently I worked with vendor of FES Screw Chiller with 20,000kg of R 134a ref charged and 800 gallon of Lubricnt oil . Now i am envolved in commissioning of another chiller it has a Propane gas charging can some body tell me what will be the running parameters with Propane Refrigerant
Parameters will be same in temperatures as with R134a. Pressure will be saturation temperatures of Propane converted to pressures.
__________________
This is signature folks!

There's no such thing as a dumb question..............
But they are the easiest to answer.

------------------------
Quis? Quid? Ubi? Quibus auxiliis? Cur? Quomodo? Quando?

------------------------
Si tacuisses,philosophus mansisses.
Reply With Quote
Sponsored links
Reply


Currently Active Users Viewing This Thread: 5 (0 members and 5 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
advanced refrigeration technology Lc_shi Fundamentals 3 27-02-2009 03:46 AM


All times are GMT +1. The time now is 06:42 AM.

 

Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
This forum and its pages must not be copied or reprinted without the written consent of Refrigeration Engineer.com.
This forum is a free and open discussion board.
Refrigeration-Engineer.com, the administrators and Moderators of this site are not responsible for content posted here.Ad Management by RedTyger