    Question Low Pressure problem - please help urgently



    Hi,
    We have a Fridge Container on board, giving problems. Compressor, Drier & T.E.V. all replaced. Now it gets down to -15 degs, but suction pressure is zero and discharge pressure is about 9 bar. There is icing up at suction side of Compressor and only a couple of smally bubbles in sight glass.
    We have 2.5 tons of meat ashore, waiting to come on board, so I'm not the most popular of persons around here right now. Any help would be much appreciated - thanks.



  2. #2
    Join Date
    Apr 2005
    Location
    England
    Age
    48
    Posts
    62
    Rep Power
    20

    Re: Low Pressure problem - please help urgently

    Can you give us the refrigerant and confirm the suction/discharge pressure/temperatures?

  3. #3
    Join Date
    Oct 2008
    Location
    Liverpool
    Age
    68
    Posts
    8
    Rep Power
    0

    Re: Low Pressure problem - please help urgently

    Hi, thanks for replying. forgot to mention refrigerant is R134a. Suction at Compressor is just less than zero and discharge pressure at Compressor is about 9 bar. Pressure in liquid line after the Drier is about 7 bar.

  4. #4
    Join Date
    Apr 2005
    Location
    England
    Age
    48
    Posts
    62
    Rep Power
    20

    Re: Low Pressure problem - please help urgently

    Hi Mike

    You should have a constant pressure on the high side of the system and you state a 2 bar drop.

    Suction pressure if 0 bar gauge gives an evaporating temp of -25oC on 134a. What is the suction temp so we can calculate the superheat?

    Did you fully evacuate the system to <3mbar after changing the components you mention?

    Discharge and ambient temperature would be useful?

    Sturt.

  5. #5
    Join Date
    Oct 2008
    Location
    Liverpool
    Age
    68
    Posts
    8
    Rep Power
    0

    Re: Low Pressure problem - please help urgently

    Hi Sturt,
    Apologies for not getting back to you sooner, but lots of problems here...
    Ambient is 21 degs, suction temp is -11 degs, liquid temp after Drier is 38 degs, discharge gas temp is 64 degs. We vacuumed the system for about ten hours yesterday, and installed new Drier before recharging the system.
    What I cannot understand is why the suction is icing up. Evap coils look good. Could it be oil in the Evap? Several people had a play with this Fridge before I got dragged in.

    Mike.

  6. #6
    Join Date
    Oct 2008
    Location
    Liverpool
    Age
    68
    Posts
    8
    Rep Power
    0

    Re: Low Pressure problem - please help urgently

    Hi Sturt - also forgot to mention that I re-checked Comp'r discharge pressure and liquid pressure after the Drier using a more accurate gauge, and got the same pressure both times - 9 bar.

    Mike.

  7. #7
    Join Date
    Apr 2005
    Location
    England
    Age
    48
    Posts
    62
    Rep Power
    20

    Re: Low Pressure problem - please help urgently

    Hi Mike

    So we have a low suction gauge and high suction superheat. This could then be:

    Undercharged
    Moisture in system
    Choked liquid or suction strainer
    Faulty BPV - not on this type of system
    Faulty expansion valve (closed)
    Liquid line obstructed

    Thats my best guess, anyone else have thoughts on this?

    Sturt.

  8. #8
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: Low Pressure problem - please help urgently

    Suction at -11C is well below frezing, thus ice on the suction pipe. This is normal as long as the compressor itself is warm. I supose you dont have any suction gas/liquid line heat exchanger......

    Exactly what is the suction pressure?
    Can you confirm whether the system has a suction gas/liquid line heat exchanger?
    What is the make and type of the expansion valve? What adjustment have you done to the valve?
    Can you confirm the evaporator fan(s) is working properly and that nothing is restricting the airflow like dirty fins?

  9. #9
    Join Date
    Oct 2008
    Location
    Liverpool
    Age
    68
    Posts
    8
    Rep Power
    0

    Re: Low Pressure problem - please help urgently

    Hi SteinarN,
    We don't have a Heat Exchanger on gas / liquid lines. The Expansion valve has been replaced (ALCO TLE 2 1/2 MW 65 3C). I cannot see any adjustment on this Valve. Evap Fans are working well and there appears to be no blocking up of Evap cooling fins. Cooling coils seem to ice up nicely. If T.E.V. is closed, would we not get high pressure at Comp'r? If I add more gas, the Comp'r will ice up even more. The Fridge Container is on a ship, out at sea, so getting a Service Engineer out here is a logistics nightmare. I did speak to a guy this morning ashore, but having told him the symptoms, he was scratching his head more than me....

    Thanks,
    Mike.

  10. #10
    Join Date
    Apr 2005
    Location
    England
    Age
    48
    Posts
    62
    Rep Power
    20

    Re: Low Pressure problem - please help urgently

    Sorry Mike I was going to finish off with saying open the expansion valve and monitor the results.

    If you are happy with the system as a whole and the system is a packaged unit and or the correct charge has gone in and the expansion valve/orifice and the phial position are all correct it probably may just need the superheat setting up.

    Sturt.

  11. #11
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: Low Pressure problem - please help urgently

    Based on the information so far the only thing I can say is that it seems as the superheat is a thad to high. If the suction pressure is -0,2 bar, that is -30C, then the evaporator Dt is 15C. (-15C box-(-30C) evaporating is 15C difference) This in combination with your measured suction temp indicates high evaporator super heat. However if it is not any adjustment on the valve....

    Was it not any adjustment on the old valve either? Is the new valve exactly the same as the old?
    Last edited by SteinarN; 02-10-2008 at 01:49 PM.

  12. #12
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: Low Pressure problem - please help urgently

    Quote Originally Posted by mike fisher View Post
    If T.E.V. is closed, would we not get high pressure at Comp'r? If I add more gas, the Comp'r will ice up even more.

    Thanks,
    Mike.
    Both suction and discharge will be lower with closed/closing tev.

    What happens to the pressure if you add more gas? Does the compressor itself ice up then? Where on the compressor? What type of compressor is it?

  13. #13
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: Low Pressure problem - please help urgently

    Quote Originally Posted by mike fisher View Post
    We vacuumed the system for about ten hours yesterday, and installed new Drier before recharging the system.

    Mike.
    Did you change the drier before or after the vacuuming?

  14. #14
    Join Date
    Oct 2008
    Location
    Liverpool
    Age
    68
    Posts
    8
    Rep Power
    0

    Re: Low Pressure problem - please help urgently

    Hi SteinarN,
    Thanks for the help with this one.
    The new T.E.V. is exactly the same as the old one. spring loaded valve and power assembly were renewed. The only thing that worries me now is running the unit with negative suction pressure. By the way, this Reefer was modified about six months ago, due to problems with the Controller. The system was then modified to a basic Fridge system, and operated fine until recently. Then we started to get the Comp'r short-cycling on HP. I know the system is gas tight, as it held a vacuum for four hours (having had a vacuum pump on it for about 8 hours), so I'm just concerned about drawing in air, if a leak should develop.

    Mike.

  15. #15
    Join Date
    Oct 2008
    Location
    Liverpool
    Age
    68
    Posts
    8
    Rep Power
    0

    Re: Low Pressure problem - please help urgently

    Hi SteinarN - after vacuuming.

  16. #16
    Join Date
    Oct 2008
    Location
    Liverpool
    Age
    68
    Posts
    8
    Rep Power
    0

    Re: Low Pressure problem - please help urgently

    Hi SteinarN - it's a standard six cylinder Compressor. Adding more gas does seem to cause suction temp to decrease, as we then get ice all the way to the cylinder head covers at suction valve area.

  17. #17
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: Low Pressure problem - please help urgently

    Quote Originally Posted by mike fisher View Post
    Hi SteinarN - after vacuuming.
    Are you sure you didnt get any air into the system when you changed the drier? Usually I change the drier first, and then vacuum the whole system.

  18. #18
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: Low Pressure problem - please help urgently

    Quote Originally Posted by mike fisher View Post
    Hi SteinarN - it's a standard six cylinder Compressor. Adding more gas does seem to cause suction temp to decrease, as we then get ice all the way to the cylinder head covers at suction valve area.
    Ice all the way to the sylinder head is a clear sign of severe liquid flodback. I supose the suction is at the motor end, opposite of the sylinder end.

    It seems to be something wrong here. Adding refrigerant shouldnt result in any severe flodback if the tev is function corectly. I supose the tev is labeled for R134A.

    If the system has a receiver, then adding refrigerant shouldnt do any difference until the receiver gets completely filled up with liquid refrigerant. After that the discharge pressure should start to increase and the condenser outlet temperature should start to decrease. But severe liquid floodback should still not occur.

  19. #19
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: Low Pressure problem - please help urgently

    Quote Originally Posted by mike fisher View Post
    The Expansion valve has been replaced (ALCO TLE 2 1/2 MW 65 3C)
    I cant find the valve you mention. The valves for R134A is TCLE........
    That valve is adjustable.

  20. #20
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Low Pressure problem - please help urgently

    did you placed the bulb on the tubes correctly ?? is the orifice correctly ??

    did you take measurements at the TEV ? before and after the valve.
    what is youre sub-cooling ??

    Ice

  21. #21
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Low Pressure problem - please help urgently

    Quote Originally Posted by mike fisher View Post
    We vacuumed the system for about ten hours yesterday, and installed new Drier before recharging the system.
    _Cut_
    Several people had a play with this Fridge before I got dragged in.

    As SteinarN pointed before, you changed filter-dryer after evacuation. How did you done that without introducing air in system? Is that filter with replaceable core and with isolating valves? Also, how did you established that your vacuum level is OK except with evacuating time of 10 hours?

    TLE 2 1/2 MW is two and half ton bi-flow TEV for R134A and with MOP and fixed superheat designated for OEM and made by their specification.

    That container is probably for air conditioning purpose or for keeping temperature at, say, 14°C with cooling or heating (what ever is needed) and control has been changed to cooling meat at 2°C .
    Last edited by nike123; 02-10-2008 at 11:59 PM.

  22. #22
    Join Date
    Sep 2006
    Location
    New Zealand
    Age
    54
    Posts
    17
    Rep Power
    0

    Smile Re: Low Pressure problem - please help urgently

    Hi
    More information about the container model might be more helpful.Some reefers have suction solenoid valves and quench valves, so your problem may not be the tx vlve at all. If it doesnt have these then you could always pump the system down and manually adjust spring tension on tx orifice to prevent the floodback.The compressor wont last long under the present conditions, hope this helps.

  23. #23
    Join Date
    Dec 2005
    Location
    Upper left hand corner of the USA
    Age
    64
    Posts
    203
    Rep Power
    19

    Re: Low Pressure problem - please help urgently

    Ditto what 'Below 0' said, a container model # and brand name would be really helpful.

  24. #24
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Low Pressure problem - please help urgently

    For a proper evaluation, we need the following information:

    Low side:

    Evap air in temp
    Evap air out temp
    Saturated suction temp (SST) converted from pressure
    Suction line temp at evap outlet

    High side:

    Cond air in temp
    Cond air out temp
    Saturated condensing temp (SCT) converted from pressure
    Liquid line temp at receiver outlet

  25. #25
    Join Date
    Sep 2009
    Location
    UK
    Age
    72
    Posts
    13
    Rep Power
    0

    Re: Low Pressure problem - please help urgently

    Your problem may be just the current limiter setting on the controller and has caught me out a few times. factory setting is about 21amps, it works by unloading the compressor via the modulation valve giving you the low/vacume pressure reading. worth checking

  26. #26
    Join Date
    Sep 2009
    Location
    UK
    Age
    72
    Posts
    13
    Rep Power
    0

    Re: Low Pressure problem - please help urgently

    Another thought Carrier ML2i evap fan motors CAN run backwards, esp if they have had new bearings after a seize up, dark spots on the start winding will give you an indication that they may run backwards

    i know this is an old post and you may have sorted it by now but stick the back of your mind

  27. #27
    Join Date
    Aug 2006
    Location
    Canada
    Age
    61
    Posts
    149
    Rep Power
    18

    Re: Low Pressure problem - please help urgently

    I guess this is an old post, but have a question...

    How does unloading the compressor cause a low suction pressure?

    If the compressor is unloaded when it is not necessary to be unloaded, the suction pressure would rise.

    If this was operating correctly for a number of months, but has recently failed, I am thinking components are correct.

    Conditions stated of reasonable head pressure (have no idea what 9 Bar means in PSI) and starved evaporator sounds like a restriction in the liquid line. I would be thinking along the lines of a filter-drier that has blown apart.

  28. #28
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    19

    Re: Low Pressure problem - please help urgently

    Any time suction going to vac means , system could be picking up air/moisture through a low side leak in system . And enters moisture which may be freezing up and ends up in low suction pressure.

  29. #29
    Join Date
    Sep 2009
    Location
    UK
    Age
    72
    Posts
    13
    Rep Power
    0

    Re: Low Pressure problem - please help urgently

    Ok, Carrier have been using a current limiter on all 69NT40's It works by enrgizing the modulation valve to reduce the flow of refrigerant back to the compressor, hence the low suction/vacuum reading and a need for a quench valve for compressor cooling. Ships often use this current limiter to control thr load on the ships generators

Similar Threads

  1. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  2. Oil pressure problem of aerzen VMY 346 HR
    By CrimsonK in forum Trouble Shooting
    Replies: 7
    Last Post: 09-03-2008, 07:08 PM
  3. Replies: 27
    Last Post: 27-10-2006, 03:19 AM
  4. Interesting Problem
    By NH3LVR in forum Industrial Compressors
    Replies: 13
    Last Post: 12-08-2006, 10:27 PM
  5. water pressure problem
    By Renato RR in forum Technical Speculations
    Replies: 3
    Last Post: 13-02-2006, 07:54 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •