Results 1 to 5 of 5
  1. #1
    cesarf's Avatar
    cesarf Guest

    Trane CVAD 27 270Ton won't start "be2.Momentary power loss"



    Hello everyone!...

    Im having trouble restarting a Trane Chiller after a brief power failure... we have two of them... the first one started right after the power came back, but the faulty one still shows "BE2" even after restarting the chiller...

    Any suggestions? Master Reset procedure? part Replacement?

    Please Help!!! Thanks very much!!!



  2. #2
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Trane CVAD 27 270Ton won't start "be2.Momentary power loss"

    hi what type of controler are u dealing with?

  3. #3
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: Trane CVAD 27 270Ton won't start "be2.Momentary power loss"

    Hi cesarf
    You could first try to power down chiller for about 15 seconds then repower. Is it controlled by a tracer? If so you could try to rest that but it is risky and best reset through software - you may loose both chillers by trying this. You could also call Trane and ask them if there are a couple of simple checks to make before placing a service call for a Trane technician. let us know how you go.

  4. #4
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    54
    Posts
    282
    Rep Power
    15

    Re: Trane CVAD 27 270Ton won't start "be2.Momentary power loss"

    TRANSFORMERS IS ABOUT TO TAKE THE STARTER voltage and converts it to UCM 5VCD THIS AS THE VOLTAGE AS INTREPRETA, they are securely connected CHECK NO distorts SOMETIMES WORKING THE CHILLER current transformers (AMPERJE) NO VOLTAGE TO SEND YOUR MODULE AND If not detected voltage that I see it as temporary loss VOLTAGE

  5. #5
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    54
    Posts
    282
    Rep Power
    15

    Re: Trane CVAD 27 270Ton won't start "be2.Momentary power loss"

    Cesarf

    enviame tu email para darte manual de fallas del panel ucml

Similar Threads

  1. Hermetic analyzer " ANNIE" how do they work
    By kengineering in forum Tools and Calculators
    Replies: 11
    Last Post: 02-03-2008, 06:10 PM
  2. SR2 50 models electric SBY diagonostics made simple
    By absolute-zero in forum Transport
    Replies: 5
    Last Post: 04-01-2008, 05:11 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •