    Display cabinet problem



    Hi Folks,

    This is my first post here.

    By way of introduction, I am a fridgy by trade but have been out of the industry for about 10 years. My focus has always been Air Conditioning and I have very little experience in the refrigeration side.

    I was looking at a small display cabinet containing slices and cakes. Located in a cafe. The evaporator was located at the top and was icing up. The drain tray beneath it was warped in the middle due to ice build up on the tray itself which meant that condensate was dripping into the cabinet rather than the drain. This is easily fixed so no big deal there.

    After fitting guages I recorded the following details.

    Refrigerant: R22
    Head Pressure: 1900kpa (amb. temp. 21degC)
    Suction Pressure: 200kpa (cabinet temp 10degC)

    I assume the desired cabinet temperature would be 3degC with a 5K TD giving evap. temp of -2degC or 370kpa. I am not sure about the 5K TD. I don't have data for cakes. Are they best kept at a lower humidity than say vegetables.

    In either case it seems the suction pressure is too low and the discharge pressure way too high for the ambient. I cleaned the condenser fins and checked the fan blades but could not reduce the high discharge pressure. At 21degC I would expect a condensing temp around 35degC or 1250kpa not 1900kpa.

    My thought were either air in the system or a blockage in the capillary or somewhere else on the high side. Being a bit rusty in my technical skills Iam not really sure what the problem could be and how to diagnose it.

    I really would appreciate some help from those with more experience and knowledge than I have.

    Thanks, Dale.



  2. #2
    Join Date
    Mar 2005
    Location
    New Zealand
    Age
    43
    Posts
    64
    Rep Power
    20

    Re: Display cabinet problem

    I would doubt there is a blockage on the high side, has anyone worked on the cabinet before you? If you have a partial blockage in the capillary, often this will confuse guys and they'll start charging more refrigerant thinking it's short, this will cause the high HP. I would recover the refrigerant, change the drier, re-commision system (check if a weighed charge is stated) if not you need to charge slowly untill the cabinet gets close to set point, then charge untill you get a little ice on the suction line to the comp then bleed the gas off slowly untill the ice melts, this is a good way to get the charge right. If when you are adding refrigerant the HP keeps rising and the suction presure stays low it would indicate most probably a blocked capillary, you can sometimes clear them with nitrogen, otherwise replace it. Is the evaporator passive or does it have fans, if it's passive remember it will evaporate much colder. I would expect it to have about 300 - 400 grms. Also make sure your not getting any air re circulation on the condenser. Hope this helps

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Display cabinet problem

    What is expansion device type? If it is capillary, it looks like restriction and overcharged.
    To check:
    The strainer on a restricted cap tube should be about room temperature because of the sub cooled liquid that has backed up, and running your hand down slowly from the top of the condenser the temperature should be warm then suddenly cool to room temperature to the level where the liquid refrigerant has backed up.
    Last edited by nike123; 06-10-2009 at 09:03 AM.

  4. #4
    Join Date
    Oct 2009
    Location
    Melbourne
    Age
    54
    Posts
    5
    Rep Power
    0

    Re: Display cabinet problem

    Thanks for the replies.

    The compressor was replaced by another company several months back and I suspect they overcharged the unit to try to raise the suction pressure.

    I did not check the temperature of the condenser u bends but did check the drier and it was room temp (not too sure though)

    Evap is forced draft.

    What cabinet temp. humidity should I be aiming for?

    Dale.

  5. #5
    Join Date
    Dec 2008
    Location
    UAE
    Age
    42
    Posts
    171
    Rep Power
    16

    Re: Display cabinet problem

    Dear Diljan,

    There are following possibilities :
    1. Comp is undersize
    2. Comp is fan cooled and fan is not working
    3. Condenser air flow is getting chocked
    4. System defrost cycle faulty
    5. Eva fan blade not working
    6.For over charging, check the temp. of the suction compared to ambient temp.
    7. Also check for the cycling percentage as i feel unit is not healthy with the operating conditions mentioned.

    Check for the above points and return back with some temp, as comp dome, suction etc.
    Thanks
    Amit Saxena

  6. #6
    Join Date
    Dec 2007
    Location
    lebanon
    Posts
    130
    Rep Power
    17

    Re: Display cabinet problem

    hi
    u mention that other company has change the compressor
    i assume that is not the same and i am leaning to a long capillary tube causing these symptom
    can u provide the cap size so we can help
    long cap act like a restriction

Similar Threads

  1. Glass Sandwich Display Cabinet
    By Windsor123 in forum Trouble Shooting
    Replies: 4
    Last Post: 12-10-2009, 01:28 AM
  2. help with display cabinet info
    By jonjon in forum Trouble Shooting
    Replies: 0
    Last Post: 13-08-2009, 10:24 PM
  3. Freezer cabinet problem
    By klimek in forum Technical Discussions
    Replies: 6
    Last Post: 17-03-2008, 11:28 AM
  4. Replies: 10
    Last Post: 11-12-2007, 09:07 AM
  5. small display cabinet keeps seizing up CF motors
    By paul_h in forum Commercial
    Replies: 8
    Last Post: 11-11-2007, 01:56 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •