404 flashing b4 TXV
cornellius xrc1444 machine, machine has run fine for three years, low production lately, quick inspection found pressure switch at condenser was bad, (would not close swith on pressure rise and stay out), replaced, ran fine for two weeks and now customer states low production, checked condenser fan and running fine, line set very hot and no "heat" pulling through condenser. i am thinking the 404 is flashing before txv, but why and why no heat off condenser?????
thanks in advance
-
08-10-2009, 04:59 AM #2
Re: 404 flashing b4 TXV
sounds to me like your compressor is inefficient/damaged reeds.
mmm to beer or not to beer...........lets drink breakfast
-
08-10-2009, 07:48 AM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: 404 flashing b4 TXV
Check subcooling before TXV. If you dont have 2K or more than it is possibly flashing (2K is minimum required subcooling if you don't have liquid receiver).
Check proper fan rotation direction and RPM. Check and clean condenser.
We also need more data to be able to help you in meaningful way.
http://www.refrigeration-engineer.co...12&postcount=5
Last edited by nike123; 08-10-2009 at 08:16 AM.
-
09-10-2009, 05:10 PM #4
Re: 404 flashing b4 TXV
i have no temp diff across txv's and the pressures at remote cond are 175/175. the pressures at machine are 40/180. when the machine starts freeze cycle, the pressures are 60 and 260, after 5 minutes the flashing begins ( i am assuming this is what is happening) and pressures are back to the 40/180. Could the vales be going out in this hrermetic??? would it run for a few mins and then go wacko??
-
09-10-2009, 05:24 PM #5
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
09-10-2009, 06:36 PM #6
Re: 404 flashing b4 TXV
no temp diff at drier, subcool is 60*.
-
09-10-2009, 06:41 PM #7
Re: 404 flashing b4 TXV
btw.. nike123, i do have a receiver, if that helps
-
09-10-2009, 08:00 PM #8
Re: 404 flashing b4 TXV
more info.....
pressures-15/125
before txv temp. 96*
after txv 77*
77*entrering plates, 57*out.
suction temp at comp. 73*
subcool is 30*, temps are raising longer machine runs. acts like it is low on charge, already 6oz. over weigh in charge.
Similar Threads
-
BEKO AP930 Flashing Error/Fault Code E8 - advice needed
By tamba001 in forum Trouble ShootingReplies: 7Last Post: 02-11-2010, 09:28 PM -
Toshiba controller flashing check?!?!?!?!
By leety in forum Air ConditioningReplies: 6Last Post: 20-07-2010, 08:45 AM -
fujitsu asya09lcc lights flashing indoors
By fumagallair in forum Air ConditioningReplies: 2Last Post: 07-07-2009, 12:34 AM -
Urgent flashing indoor lights please anyone
By fridge doctor in forum Air ConditioningReplies: 11Last Post: 15-06-2009, 05:24 PM -
fuji inverter, all LEDs flashing
By paul_h in forum Air ConditioningReplies: 2Last Post: 16-11-2007, 01:15 PM