Evaporating and Condensing Temperatures
Hello everyone. I am a design engineer for ground source heat pumps and a greenie in refrigeration. I am curious what the design evaporating and condensing temperatures would be for the following ground loop heat pump system (water to refrig and then refrig to air).
The refrigerant is R410A, the unit uses the Copeland compressor ZPS51K4EPFV. This would be sized for 64,000 BTU output at 70 deg ground loop entering water and 80 deg house entering air temperature. According to my figures, and using the information supplied by ClimateMaster, Series: Tranquility 27 (TT) Model: 064, I get the following evap and condensing temperatures:
Evap temp: 50.5 (144 psi)
Cond temp: 106 (347 psi)
at 70 EWT and 80 EAT
My question is if 50 sounds reasonable for an evaporation temperature...?
It is a high efficiency unit, probably 18 SEER?? (although I don't know if the SEER rating directly applies to ground source heat pumps). The airflow is 1825 CFM.
Next, what is the normal temperature difference between the Leaving Air Temperature (cold air going to the house) and the refrigerant saturation temperature in the evaporator? (for a ground source heat pump?)
At low EAT conditions like 65 EAT & 41.5 Leaving Air Temp, I get a negative TD of around 4 deg. That would be 41.5 (LAT) - 45.5 (Sat Evap Temp) = -4 TD. Is this possible?
Meaning my LAT is colder than my saturated evaporation temperature...?
Thanks in advance for the help!!
And thanks all the veterans of this post ... I have read through a number of items here and am quite impressed with the quality of this forum and the answers given and have found the topics covered here very helpful. Thanks!
Aaron
-
02-10-2009, 06:21 AM #2
Re: Evaporating and Condensing Temperatures
Are you a designer of ground source systems or a designer of the heat pumps themselves
-
02-10-2009, 10:56 AM #3
Re: Evaporating and Condensing Temperatures
AJS, I think that you may have mistaken your units. Under ASHRAE 13256-1 (Testing standard for Ground Water Heat Pumps) the conditions are as follows:
Cooling DB/WB 27/19C
Entering Water Temp 25C
Heating DB/WB 20C
Entering Water Temp 0C
To calculate the suction pressure you will need the flow rate and the composition of the liquid. If the system runs the risk of freezing you will naturally dilute the water with glycol which effects the transfer constant.
Never forget that the superheated gas exiting the coil will cool the body of the compressor before being compressed within so that condensing can take within the ambient conditions.
So its very difficult to predict an exact suction pressure however given that 0C/R410a is @ 7Barg a figure between 9-10Barg would not be unrealistic
Hope this helps. tmm
-
02-10-2009, 02:14 PM #4
Re: Evaporating and Condensing Temperatures
Mad Fridgie,
I am both a designer of the loop system and heat pumps.
-
02-10-2009, 02:20 PM #5
Re: Evaporating and Condensing Temperatures
tmm,
You are right about the design conditions. However, since ClimateMaster submitted conditions for 70 EWT and 80 EAT, I would like to address the saturation temperature at those conditions (so I don't have to do any adjustments or figuring for the other "test" conditions).
-
02-10-2009, 02:43 PM #6
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Evaporating and Condensing Temperatures
Normal evaporator TD is 10K (10*(5/9) °F).
You should expect that evaporation saturation temperature is ≈20°F lower than evaporator water entering temperature.
Depending on Condenser air flow your condenser TD could be 10-20K and that mean that condenser saturation temperature should lie between 20-40 °F higher than condenser air temperature
For given conditions:
at 70 EWT and 80 EAT
It look like your numbers fit in above rules.
-
02-10-2009, 02:51 PM #7
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
02-10-2009, 03:53 PM #8
-
02-10-2009, 08:29 PM #9
Re: Evaporating and Condensing Temperatures
MMMMMMMMMMMMMMMMMMMM.
The object of efficiency is to keep, SCT as low as possible and the SST as high as possible whilst still give the desired end results, and ensuring sysytem reliability.
You need to check your basic fundementals.
If you are buying a package unit, then it is what it is.
Why would you even consider cooling your house if the air on the evap is 65f, thus the issue would never arise, but if did, no the air can be colder of than the SST
-
02-10-2009, 09:59 PM #10
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
03-10-2009, 12:41 AM #11
Re: Evaporating and Condensing Temperatures
The situation is an odd one but we have some customers that insist on running their AC when the EAT is 65 degrees. They must really like it cold.... or perhaps also for dehumidication. Besides the unit should be able to handle 65 EAT but this would be about the lowest end of the envelope.
You say that the leaving air temp can be lower than the SST? And if that is what you meant, can you explain?
-
03-10-2009, 12:44 AM #12
-
03-10-2009, 12:56 AM #13
Re: Evaporating and Condensing Temperatures
Sorry about that pure "typo" "no" the air can not be colder than the SST (double negative I answer the question first)
Brain not ingaged first thing in the morning, after a Friday Night.
65F is really cold, your SST would drop to compensate for the lower EAT, equalibrium is always reached in a fridge system or trips on a safety device.
If you want to make this really efficient, why do you not put a pre-cooler before your evap.
Water is 70F, air is 80F, counter flow with right thermal length should be able to get reasonable close to approach
-
03-10-2009, 01:32 AM #14
Re: Evaporating and Condensing Temperatures
-
03-10-2009, 01:34 AM #15
Re: Evaporating and Condensing Temperatures
I;m confused ... are you using the system as an air con unit, for comfort cooling? Or a ground source heat pump, for heating?
Or, are you trying to use a groundsource heat pump for cooling?Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]
-
03-10-2009, 04:23 AM #16
-
03-10-2009, 06:50 AM #17
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
03-10-2009, 06:54 AM #18
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
03-10-2009, 10:14 AM #19
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
05-10-2009, 09:06 PM #20
Re: Evaporating and Condensing Temperatures
Great, thanks for the definition & temperatures chart! Much appreciated!
-
05-10-2009, 09:34 PM #21
Re: Evaporating and Condensing Temperatures
Nike123,
Correct me if I'm wrong but according to the table you gave,
Air conditioning (evaporator) :Tai-Tao = 8 to 10 K Evaporatordelta T (dt)
Tai-Te=16 to 20 K (evaporator dt) take low dt for high relative humidityTao-Te=8 to 10 K Evaporator approach
Gives a 4.4-5.5 degree F temperature drop of the air going through the DX coil for Air Conditioning (8*5/9=4.4). This table doesn't seem right to me as I think it should be around 18-25 degree drop in air temperature.
-
06-10-2009, 12:48 AM #22
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
06-10-2009, 02:15 PM #23
Similar Threads
-
This a long one - AKV
By Peter_1 in forum IndustrialReplies: 6Last Post: 26-12-2008, 11:47 AM -
Pressures at Evaporating & Condensing Sides
By stephen.t in forum Technical DiscussionsReplies: 4Last Post: 31-01-2008, 12:34 AM -
Evaporating / condensing temperatures
By Contactor in forum FundamentalsReplies: 46Last Post: 22-07-2007, 11:19 PM -
evaporating temperatures
By MrsFreeze in forum FundamentalsReplies: 11Last Post: 31-05-2007, 02:15 AM