17-09-2009, 06:53 AM #34
Re: AWHP superheat & sub-cooling
Fair comment.
Max SH is 25C, but not at all conditions,
Bigger the compression ratio the smaller allowable suction sh, (lower discharge) smaller comprssion ratio higher allowable SH. All limited by motor current.
I would say if your dicharge temp was under 105C and your moter current was 5% less than the name plate FLA, you would be pretty safe.Engineering Specialist - Cuprobraze, Nocolok, CD Technology