Thread: Economiser port
    Nov 2007
    India
    Economiser port
    Dear all,
    I have a problem with howden screw compressor, My problem is the economiser port gets red hot.
    I had connected the oil line from oil separator to the economiser port.
    The refrigerant is ammonia.
    Can any one suggest what is the reason for this and how to solve this problem.
    regards, and thanks in advance.
    Re: Economiser port
    Don't know this compressor or your pipe layout but it sounds as though hot gas is coming straight back to the compressor.
    Is the oil return line cool, warm or hot?
    Nov 2007
    India
    Re: Economiser port
    Oil line is warm
    3,363
    Re: Economiser port
    Have seen this on other machines also .
    I think its same gas being recirculated in and out of this port , so gas is getting more and more superheated .
    If oil return is not returning this will happen especially on VFD units when at low speeds .
    Best is return it into suction if possible .
    Mar 2006
    Philippines
    124
    Re: Economiser port
    What is the type of your oil cooler? Oil temp? Oil pressure? discharge pressure?
    If I'm not mistaken the pressure in economizer port is the pressure between your suction & discharge pressure.
    Make sure your oil pressure is higher than economizer port.
    Jan 2009
    INDIA
    40
    Re: Economiser port
    Quote Originally Posted by Rajkumar View Post
    Dear all,
    I think you have connected secondary oil seperator , coalescing element , drain to economiser port. In my view , you must connect it to suction line with restriction orifice in between so that pressure can be equalised to suction line. Hope this solves your problem. Orifice must be sized for the required pressure drop.
  1. extra expansion valve and dryer port
    By CoolWell in forum Fundamentals
    Last Post: 07-10-2008, 03:10 AM
  2. Understanding Balance port TX valves
    By Mobbsy in forum Technical Discussions
    Last Post: 23-07-2008, 04:32 AM
  3. Looking for a source for stainless side port distributor
    By 128cyclist in forum Technical Discussions
    Last Post: 21-06-2007, 10:07 PM
  4. Problematic Economiser
    By Kevin Yeo in forum Supermarket Refrigeration
    Last Post: 22-07-2005, 04:06 AM
  5. Balanced port TEVs
    By Prof Sporlan in forum Fundamentals
    Last Post: 25-02-2002, 03:43 PM