    High suction and liquid pressures



    I looked at a residential heat pump that would run for 10 mins and start to blow semi cold air with the pressures maintaining 70 low and 225 high. After 15 mins both low and high pressures would increase together until the unit goes out on high pressure.

    I asked the home owner if anyone has added ref and he said not in the last 3 years.

    This unit is 17 yrs old. Im thinking theirs an obstruction in the system or the valves on the compressor are defective. What do you think I should check?



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: High suction and liquid pressures

    Clean the coils.

  3. #3
    bth0mas20's Avatar
    bth0mas20 Guest

    Re: High suction and liquid pressures

    I cleaned the evap coil. I could clean it again. I didnt clean the cond because it didnt look dirty. Thier is about 10% of the cooling fins bent over but its been like that for the 3 years he has lived thier and it worked fine.

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: High suction and liquid pressures

    Quote Originally Posted by bth0mas20 View Post
    I cleaned the evap coil. I could clean it again. I didnt clean the cond because it didnt look dirty. Thier is about 10% of the cooling fins bent over but its been like that for the 3 years he has lived thier and it worked fine.
    Clean the condenser coil and make sure the fan is operating properly (turning in the right direction, blades clean, not recirculating hot discharge air, etc.)... and straighten the fins. The condenser needs all the airflow it can get.

  5. #5
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: High suction and liquid pressures

    Quote Originally Posted by bth0mas20 View Post
    I didnt clean the cond because it didnt look dirty. Thier is about 10% of the cooling fins bent over but its been like that for the 3 years he has lived thier and it worked fine.
    Just because it looked clean doesn't mean it is clean.
    If it was a blockage you wouldn't have high suction pressure.
    It does sound like an airflow fault or overcharge from the limited information you have given.
    The difference between genius and stupidity is that genius has its limits.

    Marc

Similar Threads

  1. Refrigeration 101
    By Gary in forum Fundamentals
    Replies: 201
    Last Post: 01-11-2011, 10:18 PM
  2. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  3. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  4. Parker levels in ammonia systems
    By Friobernal in forum Industrial
    Replies: 3
    Last Post: 04-08-2005, 03:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •