Results 1 to 5 of 5
-
28-08-2009, 04:51 PM #1
High suction and liquid pressures
I looked at a residential heat pump that would run for 10 mins and start to blow semi cold air with the pressures maintaining 70 low and 225 high. After 15 mins both low and high pressures would increase together until the unit goes out on high pressure.
I asked the home owner if anyone has added ref and he said not in the last 3 years.
This unit is 17 yrs old. Im thinking theirs an obstruction in the system or the valves on the compressor are defective. What do you think I should check?
-
28-08-2009, 05:08 PM #2
-
28-08-2009, 05:12 PM #3
Re: High suction and liquid pressures
I cleaned the evap coil. I could clean it again. I didnt clean the cond because it didnt look dirty. Thier is about 10% of the cooling fins bent over but its been like that for the 3 years he has lived thier and it worked fine.
-
28-08-2009, 05:17 PM #4
Re: High suction and liquid pressures
-
28-08-2009, 08:32 PM #5
Re: High suction and liquid pressures
The difference between genius and stupidity is that genius has its limits.
Marc