Results 1 to 17 of 17
    doggie's Avatar
    doggie Guest
    Parallel compressors single condenser
    Good day gentlemen...
    I have 2unit 15HP Semi Hermetic Compressors and in order to increase cooling capacity I have to add one more 10HP Compressor... another thing is, I have to replace the existing condensers due to old age.
    Now the question is... is it possible to use 3 compressors working together on a single "appropriate" condenser? Why?....
    Thanks for your time....
    subramanyam's Avatar
    subramanyam Guest
    Re: Parallel compressors single condenser
    yes i think u can use single condensor, which should be designed to take the load of the three compressors, but when one of the compressors is put off, there is a un necessary energy waste,
    doggie's Avatar
    doggie Guest
    Quote Originally Posted by subramanyam View Post
    Thanks for the reply... I expect the 3 compressors to be running full load most of the time so I don't expect to shut down any of the compressors
    Is there any thing I should be aware of just in case I have to install my system this way?
    May 2006
    India
    399
    You can use three compressors in parallel , it should preferably have an equal volumetric displacement . Besides, a very effective oil return system is key to success , probably use oil reservoir & oil level regulator for each compressor . Moreover, head pressure regulation will be essential in the event that one or two compressors are cylced off . I can help in designing high side system for the application. PM ddk0123@gmail.com
    Feb 2008
    adelaide sth.oz
    1,015
    dont forget balance line for sumps,one oil reservoir,one oil level control per compressor,check valves in discharge lines,correct suction header for oil return,maybe someone has a drawing out there somewhere,basically your making a rack.
    Feb 2008
    adelaide sth.oz
    1,015
    Quote Originally Posted by lowcool View Post
    go to your wholsalers engineer give him conditions of operation it would be more probable financially to run single comp than build up a hashed rack,2 old donks,one new donk,rehash add extras try and make it look trade quality.im sure bitzer would have a packaged job to suit.new pipework,new evap,less warranty problems more reliability.
    Jan 2007
    59
    145
    You need to find someone that knows what there doing. The information you need is beyond the scope of this website. If it's not done properly you will have nothing but issues
    Feb 2008
    adelaide sth.oz
    1,015
    Quote Originally Posted by joe magee View Post
    psst dont let gary hear you say that
    flavenido's Avatar
    flavenido Guest
    Adding compressor does not necesarrily mean, you can acheive additional cooling capacity. You must check the design of entire system to acheive desired result result.
    Jun 2007
    South Africa
    66
    120
    Adding another compressor to the existing system, will need a re- assesment of the complete system, including piping design. That means suction header, discharge header, liquid line, suction line, condenser, receiver, oil management and controlling. You can add a different size compressor to the rack, as long as the smaller compressor is the lag compressor.
    Sep 2003
    ISRAEL
    72
    4,248
    Adding a third compressor to existing unit is impossible!
    The condenser is designed to reject heat from the existing compressors.
    If you want to add more compressors, you will need to design a new condenser, new pipes, new TXV....
    Actually, you will be building a new unit.
    Oct 2003
    5,630
    I never install check valves in the discharge lines. This gives an additional DP and decreases system performance.
    If you install floats on the sumps, then you don't need balance lines neither.
    Oct 2003
    5,630
    Why is their an unnecessary energy waste? I should think just the opposite
    Oct 2003
    5,630
    Quote Originally Posted by D.D.KORANNE View Post
    You can use three compressors in parallel , it should preferably have an equal volumetric displacement . Moreover, head pressure regulation will be essential in the event that one or two compressors are cylced off . I can help in designing high side system for the application. ...[/EMAIL]
    I have several packs running since decades with following compressors on it: 0.5 - 1 - 2 - 4 - 7.5 - 15 HP and eventually a 30 HP added to it or a second 15HP.
    Feb 2008
    adelaide sth.oz
    1,015
    gday peter where i was coming from about balance line was maintaining the same sump pressure in all comps essentally where their is a large difference between compressor capacities,thats how we used to make em.
    Oct 2003
    5,630
    You only need a balance line if all the sumps are linked together, if you work with floats then you don't need them.
    Shingoshi's Avatar
    Shingoshi Guest
    Should there be a problem if you're building a new system with parallel compressors, and have chosen a condenser from the beginning to handle the load?
    Seems that if this was designed from the start, you could eliminate problems before they could exist.
    Shingoshi
  1. how to put compressors in parallel
    By Lc_shi in forum Technical Speculations
    Last Post: 19-12-2009, 07:30 AM
  2. Compressors - screw or reciprocating?
    By Josip in forum Industrial Compressors
    Last Post: 27-01-2009, 10:36 PM
  3. changing condenser and compressors
    By seraaco in forum Supermarket Refrigeration
    Last Post: 17-01-2009, 11:55 PM
  4. parallel flow condenser design for appliance a.c
    By saurabh_23jan in forum Air Conditioning
    Last Post: 14-11-2008, 06:12 AM
  5. Replies: 1
    Last Post: 11-10-2006, 08:32 PM