    Adjust TXV



    last thursday i replaced 1 compressor tecumseh & 3 days later received call back for the same compressor got same problem locked rotor, i'm thinking it's the txv, replaced txv but still got liquid refrigerant on suction line i'm stuck please help me, what do you think friends in my puzzle? appreciate any comment to help me.



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Adjust TXV

    Check evaporator for cleanness and enough air/water. Check fan/pump proper function/direction. Check if it is frosted and defrost it. Check if you have enough load.
    If anything above is wrong, you cannot have enough heat to boil all refrigerant.
    Check TEV bulb position. Check your subcooling is below 8.5K at design temperature and at 40°C condensation temperature (indication of overcharge).

  4. #4
    Join Date
    Mar 2008
    Location
    England
    Age
    55
    Posts
    273
    Rep Power
    17

    Re: Adjust TXV

    The system is possibly overcharged causing floodback or orifice oversized for application.
    Transvestites are men who like to eat, drink, and be Mary.

  5. #5
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Adjust TXV

    liquid refrig could be bypassing tev and evap if heat exchanger is fitted to evap that is
    mmm to beer or not to beer...........lets drink breakfast

  6. #6
    KenXL's Avatar
    KenXL Guest

    Re: Adjust TXV

    Do you have an accumulator?
    You can try with increase the superheat setting (clockwise the superheat setting screw on TXV, every 1/2 round after half hour running by measure the acture SH.)

Similar Threads

  1. T.E.V. adjustment.
    By FreezerGeezer in forum Ye Old Wifes Tales
    Replies: 46
    Last Post: 22-06-2010, 11:58 PM
  2. TXV's To Adjust or Not to Adjust - That is ....
    By Refrigerologist in forum Commissioning
    Replies: 94
    Last Post: 20-06-2009, 11:03 AM
  3. How to adjust head on a water cooled condenser
    By kengineering in forum Technical Speculations
    Replies: 5
    Last Post: 30-05-2007, 10:37 PM
  4. heat pump capacity adjust
    By Lc_shi in forum Fundamentals
    Replies: 5
    Last Post: 14-02-2006, 07:32 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •