Thread: walkin freezer help
18-08-2009, 02:46 AM #1
walkin freezer help
Hi guys Would you be able to guid me on a few things i been in ac four a few years i just started with the working on the freezer im having problems with a 404a -10f box its stops at 20f i have clean cond and evap good air flow my suc was 32g i was getting 19 deg super back to compressor and the coming from evap i had 4deg superheat i did notice that i check the pull down on the compressor and it would only go to 0 but held it would not go any lower is that normal for a copeland semi hermetic i thought that it should be able to pull a vacuum with no problem could this be just compressor problem the amps were normal and btw what is the most common problems with the freezer that they seam to be i seen this a few times were the boxes 20f no colder and it seams that every things is good but it cant be give me a clue LOL thanks
18-08-2009, 07:12 AM #2
Re: walkin freezer help
I'm not sure what your suction is but for a -10 it would be aprox14 lbs for 404a. Check your txv screen. If there was a problem with your compressor it would not pull down to the proper suction for your temp.As far as checking the compressor It should pull in a vacuum and hold granted your ssv holds. Make sure the proper pwr head is on the valve, sz in this case. There could be other issues but check those first.
18-08-2009, 07:50 AM #3
- Sep 2007
- Split Croatia
- 57
- 6,151
- 6
- 36
Yes, but you should start writing in manner that we old timers understand. Like more than one sentence and some text editing.
- evaporator air in/out temperature
- condenser air in/out temperature
- Suction pressure
- Discharge pressure
- Suction line temperature at TXV bulb location and near compressor
- Discharge line temperature near compressor
- Liquid line temperature before TXV
- Compressor model #
- Compressor running current
18-08-2009, 12:11 PM #4
First thing Pulleing downn the the pressure to vac.. Levels was not and will not be a good practise specially in positive displacement compressors.secondhy why do we have to get zero pressure in the system.
Blast Freezer Within Freezer
By rickmor in forum Technical DiscussionsReplies: 4Last Post: 18-06-2009, 03:37 AM -
out door walkin freezer
By innovative in forum FundamentalsReplies: 8Last Post: 17-12-2008, 12:35 AM -
Hotpoint FFA71 Freezer High Temp Light / Fridge is Freezing
By sumnerpa in forum Trouble ShootingReplies: 1Last Post: 19-08-2008, 03:16 PM -
Freezer compressor running 20 Hours/day
By rickcw in forum DomesticReplies: 12Last Post: 08-03-2008, 11:50 PM -
Trolley freezer & blast freezer
By smpsmp45 in forum NH3Replies: 0Last Post: 25-08-2007, 07:29 AM