    Repeated tubes failure in absorption chiller unit





    Hi every body,

    In one of our plant we are facing a repeated tubes failure in the tubes of high temperature generator of the double effect absorption chiller since 2008.
    the chiller used water as a refrigerant, LiBr as an absorpant and used Lithium Chromate as an inhibitor. Lithium Chromate dosing stopped since 2006 since it is not environment friend.
    Do thing that that failure because of stopping dosing the inhibitor OR by leaked air into the chiller?
    In general, what is the possible cause of this repeated failure?
    I will be grateful to you for answering those questions.

    BR




  2. #2
    nostalgia's Avatar
    nostalgia Guest

    Re: Repeated tubes failure in absorption chiller unit

    up

    up

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: Repeated tubes failure in absorption chiller unit

    Have you had a chemical analysis of the refrigerant mixture?

    have you carried out any preventative maintenance on the tubes?

    Water quality is paramount on Absorption chillers

  4. #4
    Join Date
    Jul 2008
    Location
    india
    Posts
    2
    Rep Power
    0

    Re: Repeated tubes failure in absorption chiller unit

    It may be due to stopping dosing of inhibitor. if chromate is banned, some other inhibitor may be used. check the quality of steem also if using in generator.

  5. #5
    Join Date
    Feb 2009
    Location
    Japan
    Posts
    5
    Rep Power
    0

    Re: Repeated tubes failure in absorption chiller unit

    How the vacuum condition in the chiller ? If the ambient air is leaking in, oxygen in the air will cause corrosion of metals and consume the inhibitor rapidly. You had better to check air-tightness of the chiller.

  6. #6
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17

    Re: Repeated tubes failure in absorption chiller unit

    In Vapour absorption Machine total system need to be under vacuum and a small leak in to the system makes Oxygen gets in to the Absorbent Lithium Bromide which makes it highly corrosive.
    Maintaining Vacuum in the system is critical in any vapour absorption system.
    Cooling water quality and quantity is critical for VAM as the heat rejection factor is as high as 1.8 and possibility of scaling is directly proportional to water quality

Similar Threads

  1. Absorption Chiller
    By frank in forum Air Conditioning
    Replies: 47
    Last Post: 06-08-2010, 08:15 PM
  2. Small Chiller unit problems
    By theapprentice in forum Commercial
    Replies: 19
    Last Post: 02-04-2008, 07:38 PM
  3. Absorption chiller in winter
    By igorb73 in forum Technical Discussions
    Replies: 2
    Last Post: 16-03-2007, 08:09 AM
  4. Connecting Trane Water chiller to air handling unit
    By celtictech in forum Fundamentals
    Replies: 10
    Last Post: 08-03-2007, 06:14 PM
  5. Replies: 8
    Last Post: 16-06-2006, 01:55 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •