    Trane Chiller Fault



    Hi,

    I have a Trane ECGAL500A Water Chiller giving a fault: 'A COM I/O 4'. The manual with the unit states that there is 'no communicatioon between the main module and I/O 4'. However, the unit is operating fine except that the remote alarm is acivated. Would appreciate it if anyone could shed some light on this?



  2. #2
    Join Date
    Sep 2005
    Location
    uk
    Age
    53
    Posts
    499
    Rep Power
    21

    Re: Trane Chiller Fault

    Quote Originally Posted by dawfake View Post
    Hi,

    I have a Trane ECGAL500A Water Chiller giving a fault: 'A COM I/O 4'. The manual with the unit states that there is 'no communicatioon between the main module and I/O 4'. However, the unit is operating fine except that the remote alarm is acivated. Would appreciate it if anyone could shed some light on this?
    Sorry no idea, however my advice would be to remove the alarm link. Trane will be happy to send you an engineer sometime within the next 2 months who earns 4 times the rest of us.
    If it was me i would remove the entire control system (as i have done several times) and replace with dixell or carel. You and your customer will benifit in the long run.
    This is not limited to trane. carrier, airedale and york have been subject to a full rip out and start again where their stupid baffling controllers have caused me problems.
    If there is a BMS link there are systems you can use to integrate this.
    Just my thoughts.
    Takes a licking, keeps on ticking.

  3. #3
    Duncanc's Avatar
    Duncanc Guest

    Re: Trane Chiller Fault

    Is it a carel controller rebadged as a trane controller? they had a known fault where the digital inputs were locking up and the software needed to be reloaded.

  4. #4
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Trane Chiller Fault

    Set D-01 to none and problem solved!

    This one is for free, juststopswapping sound controllers on chillers. If you don't understand how something works doesn't make it a sh*t controller!!!!!!

  5. #5
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Trane Chiller Fault

    hi had the same problem do as lowrider said if this dosent help check all flatcable connections drop the main switch for 5 minutes it usualy works and if all else failes u wont have a choice but to reset the controller or replace it
    be warned they are not cheap

  6. #6
    Join Date
    Sep 2005
    Location
    uk
    Age
    53
    Posts
    499
    Rep Power
    21

    Re: Trane Chiller Fault

    Quote Originally Posted by Lowrider View Post
    Set D-01 to none and problem solved!

    This one is for free, juststopswapping sound controllers on chillers. If you don't understand how something works doesn't make it a sh*t controller!!!!!!
    I understand exactly how chiller control systems work. However when TRANE market their own and only their engineers can work on them, i prefer to save my customers time and money by removing said control systems and replacing with universal off the shelf control systems anyone can use.

    Have you ever had a customer who has contacted you mid summer who has just been told by trane he will have to wait 2 weeks for an engineer to look at his chiller.

    I have, and i threw his controller away and started again. Problem solved.

    Do you fit splits boy?
    Takes a licking, keeps on ticking.

  7. #7
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Trane Chiller Fault

    Here's Slingblades PM he posted!


    Read and digest.

    I have worked on a lot of plant in the last 20 years, and my family much more. Trane is not the master of the fridge trade. Please do not question me on this website as you will encounter my wrath. Suggest you read what i post, take notes and shut your claptrap.

    Savvy? mouse brain.

    Annoyed

    Slingblade.
    So Slingblade, I hope you will not make a habbit of this, because you will not get loved on forums!

    I could have toned my comment down a bit but didn't deserve this kind of comments!!!

  8. #8
    Join Date
    Sep 2005
    Location
    uk
    Age
    53
    Posts
    499
    Rep Power
    21

    Re: Trane Chiller Fault

    Quote Originally Posted by Lowrider View Post
    Here's Slingblades PM he posted!




    So Slingblade, I hope you will not make a habbit of this, because you will not get loved on forums!

    I could have toned my comment down a bit but didn't deserve this kind of comments!!!
    I will post as i see fit, loved or not. If you intend to sling mud at people then trust me it will be returned with favour. Good luck with the rest of your existence.

    Number 2 on my ignore list.
    Takes a licking, keeps on ticking.

  9. #9
    Join Date
    Sep 2005
    Location
    uk
    Age
    53
    Posts
    499
    Rep Power
    21

    Re: Trane Chiller Fault

    Posted on my personal homepage by Lowrider.

    Slingblade,
    Let's not fight! I do understand your view about Trane's response in some issues and it's true not all controllers are easy to understand. But from an economical point of view, if anyone can do it, there is no need for an expert, you have to agree on that at least. We both be out of a job if guys, normally doing the dishes at a restaurant, not that that is a bad thing, could understand our job.

    So if I have offended you, which if I find hard with the remark I made, but could be taken that way, I apologies.

    Apology accepted, you are now removed from my ignore list.
    Keep up the good work, but i still think trane in the UK take advantage of paying customers. Why use complicated computer based nonsense when a mechanical 4 stage thermostat will do the same job.
    Takes a licking, keeps on ticking.

  10. #10
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Trane Chiller Fault

    Quote Originally Posted by slingblade View Post
    Posted on my personal homepage by Lowrider.

    Slingblade,
    Let's not fight! I do understand your view about Trane's response in some issues and it's true not all controllers are easy to understand. But from an economical point of view, if anyone can do it, there is no need for an expert, you have to agree on that at least. We both be out of a job if guys, normally doing the dishes at a restaurant, not that that is a bad thing, could understand our job.

    So if I have offended you, which if I find hard with the remark I made, but could be taken that way, I apologies.

    Apology accepted, you are now removed from my ignore list.
    Keep up the good work, but i still think trane in the UK take advantage of paying customers. Why use complicated computer based nonsense when a mechanical 4 stage thermostat will do the same job.
    As I have said on more than one occation, I don't know how the other Trane offices opperate. The one I work for doesn't let customers wait for two weeks!

    A four stage thermostat will do the trick as well, but that is not what the customers want anymore! They all want stageless control from 0-100%. So that boat has sailed!
    I now some engineers who can work on chillers with the electronic controllers but are at a loss on the older ones with 40 odd pages off control wiring and indeed a 4 stage thermostat!
    If it ain't broke, don't fix it!

Similar Threads

  1. AEC Pinical chiller with trane comp
    By cptrdbrd in forum Commercial
    Replies: 1
    Last Post: 28-10-2009, 09:47 PM
  2. trane ertaa213 EEV fault (1AA)
    By knight rider in forum Technical Discussions
    Replies: 4
    Last Post: 11-06-2009, 06:40 AM
  3. Trane CVHE 450 R11 Centrifugal Chiller
    By albertjoseph in forum Air Conditioning
    Replies: 4
    Last Post: 06-10-2008, 03:23 PM
  4. Chiller fault
    By iceman007 in forum Trouble Shooting
    Replies: 9
    Last Post: 27-06-2006, 06:15 AM
  5. Chiller Fault
    By iceman007 in forum Air Conditioning
    Replies: 2
    Last Post: 13-05-2006, 07:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •