    Repeated tube failure in chiller



    Hi everybody

    There is frequently tube failure problem in chiller since last 06 months. we are using R-22 in tube side and calcium chloride brine in shell side. this chiller was installed in 2006. We are adding chromate as a corrosion inhibitor in brine and maintaining the chromate 400 to 600 ppm.
    We have made some changes in brine flow circuit in 2007.
    Earlier circuit
    process plant- brine pump-chiller-process plant
    Changed Circuit
    Chiller- brine tank- brine pump - process plant-chiller

    Kindly help me to come out from this problem.

    Regards,
    DNG



  2. #2
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: Repeated tube failure in chiller

    Are you using cupranicle tubes? Are the replaced tubes failing or old ones? Is it corrosion or errosion? What pressure does the tube and shell side get up to? What is your flow rate and what was it? What is the chiller model and make? Take a high resolution photo then crop a failed section and put on post if you can. Are there any vibration issues? Is there any sign of errosion on the end plate dividers? Are there any sacrificial anodes? Please answer some of these questions so we can help you with more informed answers. All the chillers I have worked on the water is in the tube, Opps except some york chillers.
    Last edited by Tesla; 15-08-2009 at 04:59 PM. Reason: Last five words

  3. #3
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17

    Re: Repeated tube failure in chiller

    Calcium Chloride brine is corrosive.The brine off temperature must be sub zero temperature.
    Concentration of Calcium chloride by weight for the temperature has to be maintained and necessary corrosion inhibitor to be used.Probable cause of tube failure must be due to freezing of ice near tubes mainly due to brine not meeting the density requirement causing freezing.
    Best thing is to switch over to Mono ethylene glycol solution, here again we have to maintain the concentration for the brine off temperature.

  4. #4
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: Repeated tube failure in chiller

    Are the tube failures due to crushing tubes, or fracture, or pin hole corrossion, or failing at the rolling point to tube sheet.
    magoo

Similar Threads

  1. Carrier Transicold Container Problem
    By Shamel in forum Transport
    Replies: 39
    Last Post: 23-01-2012, 11:23 PM
  2. Repeated tubes failure in absorption chiller unit
    By nostalgia in forum Trouble Shooting
    Replies: 5
    Last Post: 17-08-2009, 06:35 AM
  3. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 01:03 PM
  4. Cap Tube Design Program - Results
    By Chef in forum Fundamentals
    Replies: 3
    Last Post: 01-09-2008, 09:49 AM
  5. metric capillary tube
    By tralex in forum Fundamentals
    Replies: 5
    Last Post: 21-02-2006, 06:57 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •