Re: AWHP superheat & sub-cooling
And let's not forget:
3. CPR valve.
Of these three, the MOP would be the least suitable. It reduces the Te,sat and compressor load by reducing refrigerant flow through the evaporator, but this raises the superheat and thus reduces the compressor cooling. The reduced compressor load would probably compensate for the high superheat to control the compressor heat.
The CPR would do the job and in fact would be the simplest. The evaporator pressure increases with the load, but the CPR will allow no more than setpoint pressure to enter the compressor.
The fan control strategy responds directly to the compressor heat and I'm thinking will be the best in safeguarding the compressor.Last edited by Gary; 12-08-2009 at 05:07 AM.