15-06-2004, 12:01 AM #29
Re: R407 C wall mount LG 7 Kw
Ok, this is an update on the troublesome LG Air Con.
I rang LG Distribution boffin with symtoms...........Guess what ??? He said wire the condenser fan direct !!!! He even sent me a wiring diagram..........Well, well........
That fan kicking in and out must have played hell with both back and high pressures......and the scroll compressor
Anyway, I put in a "fresh" charge of refrigerant......bypassed condenser fan...........and this is what I get.
Outdoor Unit
Air on 29C
Air Off 37C
Back Pressure ..........Steady on 60 Psi
Indoor Unit Air On 24 C
Air Off 7.6C
Customer says............Wow its cold in here!!!
The outdoor unit, tripped, cut off once, completely
But after that stayed on..........and ran
So we will see what happens, The LG guy says indoor unit air off must be no lower then 12C
Im getting 7.6C. Is he right?????
He said any lower then 12C and the coil will ice up.
Well on some of my units it gets to 5C and lower...
What Ive learnt.......from this
I dont think LG and R407C make good company. The way they have designed their systems dont seem to work in harmony, thats my view.
Hey Mark, fancy letting me have some of your Daikins at your preferential new prices????
Similar Threads
-
Fujitsu wall controller
By iceman007 in forum Air ConditioningReplies: 4Last Post: 02-03-2006, 04:32 PM -
R407 refrigerant
By JCole21961 in forum RefrigerantsReplies: 10Last Post: 29-08-2005, 05:25 PM -
R22 in a R407 system
By Abe in forum RefrigerantsReplies: 9Last Post: 20-06-2003, 08:51 AM -
Cold wall vs. Forced-Air, which is better?
By pezagent in forum Technical DiscussionsReplies: 4Last Post: 23-05-2003, 04:34 AM -
Mitsu High Wall
By Abe in forum Air ConditioningReplies: 4Last Post: 07-05-2002, 05:59 PM