    trane chiller problems.



    hi all wonder if anyone has come across this problem. ive been working on a trane ERTAA215 and it keeps on coming up with the fault CHILLER MOD TO OPTION MOD COMM FAILURE. its set to tracer and theres another identical chiller next to it with the same settings but no faults. ive tryed powering down but no joy.ive tested both comps and exv,but cant get it to runon its own. please help



  2. #2
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: trane chiller problems.

    hi check if somone changed one of the options that are disabled to enable and the card is actully not installed .
    does your comm with the bcu work proparly ???

  3. #3
    Join Date
    Feb 2009
    Location
    england
    Age
    49
    Posts
    21
    Rep Power
    0

    Re: trane chiller problems.

    thanks for reply goshen,ive gone through all the settings on the chiller and they are the same as the chiller next to it [both independent].and thats working fine. what is the bcu?. thanks, any more advice or what to test and how would be great.

  4. #4
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: trane chiller problems.

    A BCU is a Building Control Unit. Not at hand here, I think.

    In both machines a A9 module would be installed. This can either be a CSR or a LCI-C. Either one is not communication with the main module.

  5. #5
    moggs's Avatar
    moggs Guest

    Re: trane chiller problems.

    Check the comms wire between the two mods wire No 22 & 23 between the A1 chiller mod and the A9 options mod they are daisy chained to all the Mods.

  6. #6
    Join Date
    Feb 2009
    Location
    england
    Age
    49
    Posts
    21
    Rep Power
    0

    Re: trane chiller problems.

    thank you for all your help, chiller running now turned out to be maintenance staff on site telling porkys about them not touching the chiller

Similar Threads

  1. York Chiller problems
    By ingherrera in forum Commercial
    Replies: 18
    Last Post: 26-07-2011, 03:10 PM
  2. chiller problems
    By iceman6869 in forum Technical Discussions
    Replies: 8
    Last Post: 19-11-2009, 07:47 AM
  3. AEC Pinical chiller with trane comp
    By cptrdbrd in forum Commercial
    Replies: 1
    Last Post: 28-10-2009, 09:47 PM
  4. New to Forum, Facing problems related with TRANE Chiller
    By neerajpuranik in forum Air Conditioning
    Replies: 3
    Last Post: 10-12-2008, 02:43 AM
  5. Trane CVHE 450 R11 Centrifugal Chiller
    By albertjoseph in forum Air Conditioning
    Replies: 4
    Last Post: 06-10-2008, 03:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •