    help with restaurant ac system design



    Dear fellows:

    Most of the time I do refrigeration work, but a friend of mine is about to open a small restaurant and asked me for advice in regards to the ac system. I hope someone can help me out with this since I´m pretty much lost in this field.

    There is going to be a double swing door in the wall that separates the kitchen from the dining area. There is an exhaust hood in the kitchen just above the grill and stove. There are also a few self-contained refrigeration units as well as a large ice machine, therefore I believe that additional ventilation is needed to handle these heat output.
    From a previous restaurant experience, my friend believes that the only way to stop kitchen odors from entering the dining area is by allowing the kitchen exhaust to suction out some air from the dining space through the swing door. Nevertheless, I believe that if this suction action is not controlled, we might have problems with the air conditioning system performance since we are stealing away cooled air from it.
    How can these two opposing actions can be put to work together?



  2. #2
    Join Date
    Sep 2008
    Location
    england
    Posts
    427
    Rep Power
    20

    Re: help with restaurant ac system design

    Hi friocold,
    I`m doing some restaurant work myself at the moment (and ongoing project that`s being done gradually over a few months). Ideally any air removed from the kitchen should be replaced by 80% of filtered air, this will prevent odours from seeping into the dining area but still allow gas appliances to operate correctly. As I said, that`s an ideal but it gives you something to go by,
    Regards,
    Glenn

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: help with restaurant ac system design

    Quote Originally Posted by friocold2008 View Post
    Dear fellows:
    ...
    From a previous restaurant experience, my friend believes that the only way to stop kitchen odors from entering the dining area is by allowing the kitchen exhaust to suction out some air from the dining space through the swing door. Nevertheless, I believe that if this suction action is not controlled, we might have problems with the air conditioning system performance since we are stealing away cooled air from it.
    How can these two opposing actions can be put to work together?
    You're both right: your friend is completely right because you must have supply to prevent odors and you're also right that you will 'steal away' the cold.

    You can steal that much that the restaurant will never cool down.

    There's only one good solution for this: supply fresh air from outside in the same amount as you extract. Or make a hole somewhere in the kitchen wall with a grill to the outside.

    When I open the door of a restaurant, I immediately feel when opening the front door if there's supply in the kitchen.

    I should take in account all the self contained machines as a heat load but not extract them to the outside.You ten again steal cold from the restaurant. Best solution of course is putting the condensers outside
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: help with restaurant ac system design

    Don't forget to factor in the kitchen extract in the equation.(if the 20% rule is right -it seems a bit high to me?)

    ie
    kitchen extract 100m3 hr
    kitchen supply 80 m3 hr (100% fresh air)

    This will give the correct air flow from the restaurant to the kitchen and up/out the extract.

    The restaurant side ac will need to be big enough to supply it's load + the 20 m3hr fresh air to compensate the loss.

    All fast food restaurants operate this way
    Last edited by multisync; 29-07-2009 at 08:10 PM.

  5. #5
    Join Date
    Apr 2009
    Location
    Panacea, Florida
    Age
    87
    Posts
    76
    Rep Power
    16

    Re: help with restaurant ac system design

    Quote Originally Posted by friocold2008 View Post
    Dear fellows:

    Most of the time I do refrigeration work, but a friend of mine is about to open a small restaurant and asked me for advice in regards to the ac system. I hope someone can help me out with this since I´m pretty much lost in this field.

    There is going to be a double swing door in the wall that separates the kitchen from the dining area. There is an exhaust hood in the kitchen just above the grill and stove. There are also a few self-contained refrigeration units as well as a large ice machine, therefore I believe that additional ventilation is needed to handle these heat output.
    From a previous restaurant experience, my friend believes that the only way to stop kitchen odors from entering the dining area is by allowing the kitchen exhaust to suction out some air from the dining space through the swing door. Nevertheless, I believe that if this suction action is not controlled, we might have problems with the air conditioning system performance since we are stealing away cooled air from it.
    How can these two opposing actions can be put to work together?
    This topic is covered in chapter 4 of my book HVAC Design Manual – A Mechanical Designer’s Guide to Design of Small Commercial and Institutional HVAC Systems available for free download on my web site www.nettally.com/doughert. You can download the book, and print out chapter 4. You may want to print the entire book, which is written with competent contractors in mind.

    Briefly, it is necessary to bring outdoor air into the dining area in exces of all of the building exhaust, including the kitchen hood. If the kitchen is air conditioned, the system must be separate from the dining area, with no outdoor air introduced. Thus, the dining area will be at higher pressure than outside, protecting against infiltration, and also higher than the kitchen, allowing excess air to freely move from the dining area to the kitchen and be exhausted by the hood, scullery, and other fans.

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: help with restaurant ac system design

    Quote Originally Posted by dougheret0 View Post
    This topic is covered in chapter 4 of my book HVAC Design Manual – A Mechanical Designer’s Guide to Design of Small Commercial and Institutional HVAC Systems available for free download on my web site www.nettally.com/doughert. You can download the book, and print out chapter 4. You may want to print the entire book, which is written with competent contractors in mind.

    Briefly, it is necessary to bring outdoor air into the dining area in exces of all of the building exhaust, including the kitchen hood. If the kitchen is air conditioned, the system must be separate from the dining area, with no outdoor air introduced. Thus, the dining area will be at higher pressure than outside, protecting against infiltration, and also higher than the kitchen, allowing excess air to freely move from the dining area to the kitchen and be exhausted by the hood, scullery, and other fans.
    Ahhhh... A fellow author and fellow Floridian as well. Welcome to the R-E Forums.

  7. #7
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: help with restaurant ac system design

    for air replacement in the kitchen i would recommend evaporative coolling and full height doors
    mmm to beer or not to beer...........lets drink breakfast

  8. #8
    Join Date
    Oct 2008
    Location
    Panama
    Age
    41
    Posts
    36
    Rep Power
    0

    Re: help with restaurant ac system design

    Thank you very much for all of your kind and very clear comments!!
    I´ve been reading and re-reading them and I think I am getting the whole idea.
    By the way, the book download recommended by dougheretO is great and easy to follow, even for a person like me with limited knowledge on central air conditioning design.
    One more question: down here in the tropics, fresh air is heavily loaded with both heat and humidity (now I understand why ac techs try to keep it at the minimum allowed). It´s my understanding that standard commercial ac units have a limited capacity for handling humidity loads. Would it be necessary to cool/deshumidify the fresh air before it gets into the ac system in order not to impose a additional load on the equipment, posibly leading to overall poor performance?
    Best regards

  9. #9
    Join Date
    Apr 2009
    Location
    Panacea, Florida
    Age
    87
    Posts
    76
    Rep Power
    16

    Re: help with restaurant ac system design

    Quote Originally Posted by friocold2008 View Post
    Thank you very much for all of your kind and very clear comments!!
    I´ve been reading and re-reading them and I think I am getting the whole idea.
    By the way, the book download recommended by dougheretO is great and easy to follow, even for a person like me with limited knowledge on central air conditioning design.
    One more question: down here in the tropics, fresh air is heavily loaded with both heat and humidity (now I understand why ac techs try to keep it at the minimum allowed). It´s my understanding that standard commercial ac units have a limited capacity for handling humidity loads. Would it be necessary to cool/deshumidify the fresh air before it gets into the ac system in order not to impose a additional load on the equipment, posibly leading to overall poor performance?
    Best regards
    Thanks for the kind words about my book. This topic is also discussed, but I understand that it gets more technical. In general, even in Panama, if your outdoor air is less than 20% of the supply air, you should not have to worry about pre-treatment. However, for restauraunts, outdoor air induced through the air conditioner is often much more than this. It must be at least 20% larger than the total exhaust from the building. The options are: dedicated outdoor air unit by Dectron, Addison, or Desert Aire (among others); Hot gas reheat available in most packaged units; wrap-around heat pipe - only effective near design, when the unit is operating.

    I strongly recommend you contact your York, Carrier, or Trane representative for help - they have access to factory engineers and can analyze your particular problem. All have special units now designed to handle high outdoor air or low sensible heat ratio, and will work within your friend's budget and requirements. Nothing is worse than a restaurant that doesn't work!

Similar Threads

  1. High Liquid Line Temperature
    By airefresco in forum Commercial
    Replies: 37
    Last Post: 11-02-2009, 04:36 PM
  2. Refrigeration system design
    By sachin9782 in forum Refrigerants
    Replies: 4
    Last Post: 19-11-2008, 07:27 PM
  3. Ammonia system design
    By ingherrera in forum NH3
    Replies: 16
    Last Post: 08-03-2007, 02:58 PM
  4. Co2 System Design
    By Brad Chen in forum Supermarket Refrigeration
    Replies: 5
    Last Post: 18-05-2006, 12:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •