    Question Scotsman ACM225 on high condenser temperature



    Hi,

    I have been back and forward to this ice machine a few times now and have ran out of ideas on why it keeps tripping off.
    The original problem I found was a lack of water in the sump causing the machine to run dry by the second or third batch. I removed the inlet valve, cleaned the filter and replaced the fill hose which appeared to solve the problem.
    Now the machine will run for a few days to a week then trip off on high condenser temp fault.

    The condenser is clear and fan is running
    The refrigerant charge is fine
    The The coil is freezing all over



  2. #2
    Join Date
    Aug 2009
    Location
    Scotland
    Posts
    3
    Rep Power
    0

    Question Scotsman ACM225 on high condenser temperature

    Hi,

    I have been back and forward to this ice machine a few times now and have ran out of ideas on why it keeps tripping off.
    The original problem I found was a lack of water in the sump causing the machine to run dry by the second or third batch. I removed the inlet valve, cleaned the filter and replaced the fill hose which appeared to solve the problem.
    Now the machine will run for a few days to a week then trip off on high condenser temp fault.

    The condenser is clear and fan is running
    The refrigerant charge is fine
    The coil is freezing all over

    Any advice would be appreciated

    Thanks

  3. #3
    Join Date
    Jul 2009
    Location
    South Africa
    Age
    79
    Posts
    195
    Rep Power
    17

    Re: Scotsman ACM225 on high condenser temperature

    Can you say for everyone what gas is it using? What is low and high side pressures?

    Thank you.

  4. #4
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Scotsman ACM225 on high condenser temperature

    However, I have not worked for a long time on ice machines, does the fan goes on on the command from a sensor in the condenser?

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Scotsman ACM225 on high condenser temperature

    Quote Originally Posted by hyndovich View Post
    Hi,

    I have been back and forward to this ice machine a few times now and have ran out of ideas on why it keeps tripping off.
    The original problem I found was a lack of water in the sump causing the machine to run dry by the second or third batch. I removed the inlet valve, cleaned the filter and replaced the fill hose which appeared to solve the problem.
    Now the machine will run for a few days to a week then trip off on high condenser temp fault.

    The condenser is clear and fan is running
    The refrigerant charge is fine
    The coil is freezing all over

    Any advice would be appreciated

    Thanks
    What is condenser air on and off temperature?
    What is subcooling and superheat?
    What are saturation evaporation and condensation temperatures?
    What is ambient temperature where ice maker is placed?

  6. #6
    Join Date
    Mar 2008
    Location
    England
    Age
    55
    Posts
    273
    Rep Power
    17

    Re: Scotsman ACM225 on high condenser temperature

    Is ventilation adequate all the time ?
    Transvestites are men who like to eat, drink, and be Mary.

  7. #7
    Join Date
    Jun 2008
    Location
    gloucester
    Age
    44
    Posts
    72
    Rep Power
    17

    Re: Scotsman ACM225 on high condenser temperature

    could have intermitent fault with probe

  8. #8
    Join Date
    Mar 2008
    Location
    England
    Age
    55
    Posts
    273
    Rep Power
    17

    Re: Scotsman ACM225 on high condenser temperature

    Water inlet solenoid faulty
    Transvestites are men who like to eat, drink, and be Mary.

  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Scotsman ACM225 on high condenser temperature

    Quote Originally Posted by philfridge View Post
    Water inlet solenoid faulty
    What is that got to do with high pressure error on air cooled condenser?

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Scotsman ACM225 on high condenser temperature

    NOTE. In case the condenser temperature
    probe senses that the condenser temperature
    has rised to 70°C (160°F) - on air cooled
    versions - or 62°C (145°F) - on water cooled
    versions - for one of the following reasons:
    CLOGGED CONDENSER (Air cooled
    version)
    INSUFFICIENT FLOW OF COOLING
    WATER (Water cooled version)
    FAN MOTOR OUT OF OPERATION (Air
    cooled version)
    AMBIENT TEMPERATURE HIGHER THEN
    40°C (100°F)
    it causes the total and immediate SHUT-OFF
    of the machine in order to prevent the unit
    from operating in abnormal and dangerous
    conditions.
    When the ice maker stops on account of this
    protective device, there is a simultaneous
    glowing of the RED LED, warning the user of
    the Hi Temperature situation.
    After having eliminated the source of the
    condenser hi-temperature, to restart the
    machine it is necessary first to rotate for a
    while the program selector on RE-SET
    position then again on OPERATION position
    or to unplug (wait few seconds) and plug in
    again the unit. The ice machine resumes its
    normal operation by going through the 5
    minutes water filling phase.
    http://www.scotsice.com.au/mainsite/Service%20Manuals/Scotsman/07%20AC%2085-225%20-%20REV%2001-2001.pdf

  11. #11
    Join Date
    Mar 2008
    Location
    England
    Age
    55
    Posts
    273
    Rep Power
    17

    Re: Scotsman ACM225 on high condenser temperature

    Quote Originally Posted by nike123 View Post
    What is that got to do with high pressure error on air cooled condenser?
    Original fault was insufficent water supply, so we have to go with that first. Now it is highly likely that this solenoid
    Could now be' letting by 'allowing 'warm' water to continually enter the machine causing a high temperature cutout.
    Transvestites are men who like to eat, drink, and be Mary.

Similar Threads

  1. LG heat pump problem
    By back2space in forum Heat Pumps
    Replies: 132
    Last Post: 01-02-2009, 11:23 PM
  2. This a long one - AKV
    By Peter_1 in forum Industrial
    Replies: 6
    Last Post: 26-12-2008, 11:47 AM
  3. Temperature drop in condenser
    By sullie in forum Fundamentals
    Replies: 4
    Last Post: 18-05-2008, 04:41 AM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM
  5. Article in ACH&R News
    By Gary in forum Fundamentals
    Replies: 8
    Last Post: 20-05-2003, 12:27 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •