    Dear friends, are there any hvac Engineers in the forum who can help me out here? In the late 80s I worked offshore on gas production platforms, part of the refrig contract was to carry out hvac perfomance testing. I feel a complete twonk,asking because Ive done it hundreds of times, However Ive forgotten the procedure and the math to get air change rates per hour, I know I used to record inlet velocity in mps, and work out the room total area but thats all I can recall, mind you, It was a long time ago,anyway, it may be needed again soon so if you can help, drop me a line. many thanks.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: HVAC Performance test. HELP!

    Room volume is W x H x L, do in metric, eg 4m x 2.4m x 5m = 48 cu.m

    Duct/grille size 0.25m x 0.3m = 0.075 sq.m

    Air velocity in duct measured at 2.5 m/s

    Air volume (air flow rate) = 2.5 m/s x 0.075 sq.m = 0.1875 cu.m/s

    Flow rate per hour = 0.1875 x 3600 = 675 cu.m/h

    AIr change rate = 675 cu.m/h / 48 cu.m = 14

    I think
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jan 2009
    Location
    united kingdom
    Age
    71
    Posts
    31
    Rep Power
    0

    Re: HVAC Performance test. HELP!

    Hello Brian, I think you have nailed it in one. Its all starting to make sense again. Sorry for delay in reply, been busy. I remain in your debt, Thankyou very very much.Now off to buy an anemometer,and thanks again.


    ****.

  4. #4
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: HVAC Performance test. HELP!

    Brian UK.
    You are a legend. The only thing I would add is to use a hood arrangement when testing grille flow rate,so as to accurately check air volume.
    magoo

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: HVAC Performance test. HELP!

    Thank you one and several, I will now sit in the corner with a warm beer
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Suction gas <-> liquid line heat exchange and performance gains
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 18-05-2010, 01:52 PM
  2. Replies: 3
    Last Post: 17-01-2009, 03:17 PM
  3. performance test
    By Mr. Boon in forum Fundamentals
    Replies: 0
    Last Post: 02-03-2008, 05:45 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •