    McQuay PHH079



    Hi .. it's eng.Khaled from Egypt

    I've already bought a chiller from McQuay International and its model is PHH079 from 1988 and now there's a problem in it, when it starts up with Star connection it works normally but when it converts the electrical signal to Delta connection it stops !!!! so may be there's a problem in contactors or another thing ?!!!

    I need just a technical support to how deal with this problem ?! .. please inform me with solution.

    thanks



  2. #2
    Join Date
    Jul 2008
    Location
    UK
    Age
    60
    Posts
    94
    Rep Power
    16

    Re: McQuay PHH079

    Hi Khaled,
    Does the motor actually run in delta before tripping or does it not go into delta? If it goes into delta it should make some auxiliary contact to prove transition. These contacts will be on the delta contactor. What type of control panel do you have and what fault is indicated?

Similar Threads

  1. McQuay PSF Flooded screw reset problem
    By Superheatman in forum Industrial
    Replies: 6
    Last Post: 19-08-2011, 06:19 PM
  2. McQuay Centrifugal Oil pressure
    By setrite in forum Trouble Shooting
    Replies: 10
    Last Post: 13-01-2011, 01:17 PM
  3. McQUAY CHILLERS...
    By DoD in forum Commercial
    Replies: 44
    Last Post: 10-12-2010, 05:21 PM
  4. Aaaargh Mcquay!!!
    By pb smash in forum Electrical
    Replies: 13
    Last Post: 11-02-2010, 03:27 PM
  5. McQuay chiller tripping
    By moideen in forum Trouble Shooting
    Replies: 1
    Last Post: 09-05-2008, 11:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •