Came across an open top meat bin. It has two doors as a pass through. The unit was not working. Found it was off on head pressure switch. Rest, head pressure was very high. Clean The condenser and the watched it run.
The unit has a pressure switch to control the box temp.
It is medium temp and I set it to cut in at 62psi and out at 40 psi. The unit is a r22.
Did my split on the condeser and got a 21 degree split on that.
What is troubling to me is
my super heat was at 19degrees and my sub cooling was at 2 degrees F.
I waited a few to let box cool down then checked it again once it got closer to temp
Super heat was at 10 degrees f, and the sub cooling was at 21 degrees.
Is this unit over charged. The ambient air is like 75 degrees.
-
03-08-2009, 12:41 AM #2
Re: Open top meat bin not working right or is it
Yes... but not a lot.
The subcooling should be max 15F.
-
03-08-2009, 02:07 AM #3
Re: Open top meat bin not working right or is it
I thought that my sub cooling should be at or around 2 to 5
-
03-08-2009, 02:15 AM #4
Re: Open top meat bin not working right or is it
-
03-08-2009, 02:26 AM #5
Re: Open top meat bin not working right or is it
why would I want to kick out on hp, should I make the subcooling lower
-
03-08-2009, 02:39 AM #6
Re: Open top meat bin not working right or is it
Above 15F is extra. The 21F subcooling you currently have is the extra I was referring to.
I would slowly remove refrigerant until the subcooling is 15F.Last edited by Gary; 03-08-2009 at 02:44 AM.
-
03-08-2009, 04:29 AM #7
Re: Open top meat bin not working right or is it
question: is 15 the kind of subcooling I should have on all medium temp equipment. Does this apply to a Walk in cooler also.
-
03-08-2009, 04:39 AM #8
Re: Open top meat bin not working right or is it
Yes... it pretty much works for all TXV systems.
Similar Threads
-
Working outside your home country
By US Iceman in forum Chit Chat & Service StoriesReplies: 10Last Post: 29-07-2008, 04:05 AM -
OIL SEPARATOR not working properly
By PEPELEBU in forum Trouble ShootingReplies: 14Last Post: 05-05-2008, 04:16 PM -
Hinari and how far to open valves
By stryker in forum Air ConditioningReplies: 6Last Post: 14-04-2008, 01:47 AM -
Blamed for open freezer door
By RichTea in forum DomesticReplies: 17Last Post: 22-11-2006, 07:43 PM -
is my fridge working properly?
By vincec in forum Trouble ShootingReplies: 1Last Post: 15-01-2002, 09:55 PM