low evaporator chiller water flow & chiller water overdue alarm
Hi all,
Please help me how to solve this alarm?
Thanks very much
-
01-08-2009, 02:26 PM #2
Re: low evaporator chiller water flow & chiller water overdue alarm
Are your chilled water pumps running?
The difference between genius and stupidity is that genius has its limits.
Marc
-
01-08-2009, 03:22 PM #3
-
01-08-2009, 05:21 PM #4
Re: low evaporator chiller water flow & chiller water overdue alarm
We need more data...
The alarm is actived based in what circunstances? low water flow? low outlet chilled water?
Are the pumps "feeling" a big pressure at the outlet maybe by a clogged filter or stop valve closed?
This would mades the VFD down the flow rate if the operating VFD is based on the pressure. However if the operating of the VFD is based on the differential pressure (pump outlet minus inlet) this shouldn' happened
Give us more information
BaptistaTo make progress is never good enough, I want to do better and better and better
-
02-08-2009, 10:34 AM #5
Re: low evaporator chiller water flow & chiller water overdue alarm
hey,
whats your minimum hz on your drive? your drive should not go below 15hz. also do you have any faults on your vfd?
Similar Threads
-
Carrier Transicold Container Problem
By Shamel in forum TransportReplies: 39Last Post: 23-01-2012, 11:23 PM -
Chilled water flow (Entering water Temp) Alarm of Trane chiller (RTAC-170D)
By masum in forum CommercialReplies: 3Last Post: 13-06-2009, 01:39 PM -
York Chiller evap water flow direction
By mechillers in forum Technical DiscussionsReplies: 6Last Post: 30-03-2009, 05:37 PM -
Water Chiller High Water Flow
By assadp in forum FundamentalsReplies: 15Last Post: 22-05-2008, 06:41 PM -
Building a wine cabinet
By Rory in forum Technical DiscussionsReplies: 38Last Post: 13-07-2004, 08:28 PM