    Hi all,

    our chiller was alarm low oil different pressure. I put reset alarm. it is continue running and after that It tripped. Is this critical problem. And My mistake why don't stop chiller when It is alarm right?

    please let me understand and how can I explain and any solving method for this issue.

    Many thanks



  2. #2
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: low oil pressure different alarm

    Hi.
    It is indeed a very critical alarm.

    Maybe compressor lost its oil.
    Maybe something wrong with the oil pump and it is unable to do its work good.
    Maybe simply oil filter is clogged and needs change.

    Give the model of the unit and of the compressor, and possibly other members will advise you in more details as to how to eliminate the fault.

  3. #3
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: low oil pressure different alarm

    Or maybe simply the pressure diff relay is faulty, or its capillar get clogged.

  4. #4
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: low oil pressure different alarm

    Quote Originally Posted by jurekorgurek View Post
    Hi all,

    our chiller was alarm low oil different pressure. I put reset alarm. it is continue running and after that It tripped. Is this critical problem. And My mistake why don't stop chiller when It is alarm right?

    please let me understand and how can I explain and any solving method for this issue.

    Many thanks

    Hello.

    The oil alarm works on a positive oil pressure if the pressure drops for a set period of time (either 60, 90 or 120 seconds) then the alarm triggers and stops the comp from running thus protecting it from harm.

    I doubt you will have done it any harm ressting it once but do not do it again because there is a problem and it does need checking out.

    Hopfully it is just a blocked filter and dirty oil.

    It will need looking at though by sombody who has the correct tools and experience to do the job safely and correctly.

    All the best taz.

    .

  5. #5
    Join Date
    Jul 2009
    Location
    Vietnam
    Age
    41
    Posts
    6
    Rep Power
    0

    Re: low oil pressure different alarm

    Thank very much taz24 & YuriB,

    I am less experience in refrigeration field. Thank for your advise, So if you have the list of alarms or some alarm often happen & how to solve it. (action, reset, check, change).
    Many thanks.

    Hi Taz 24,
    as you advise, I can reset but only one time, if it is happen again. I should be stopped and check out the filter, sensor...
    is that true?
    thanks.

  6. #6
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: low oil pressure different alarm

    do you keep driving your car if the oil light is on,or check level of oil and top up if required,if light is still on do you keep driving or get a mechanic to check and remedy the situation.
    only my opinion of course.
    mmm to beer or not to beer...........lets drink breakfast

  7. #7
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    19

    Re: low oil pressure different alarm

    Low oil pressure is indeed critical to the compressor. However , in such an event , compressor needs to be shut down as it would damage it. As i understand it correctly , the compressor is not tripping , is it ? However , its control circuit can be altered to trip off the compressor

  8. #8
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: low oil pressure different alarm

    to test the oil diff swith, remove the 3ph fuses feeding the compressor, swich on, comp contactor energizes < is everything running but the comp,? test the time before the system trips out,

  9. #9
    Join Date
    Jul 2009
    Location
    New zealand
    Age
    47
    Posts
    15
    Rep Power
    0

    Re: low oil pressure different alarm

    First of all, are you getting any oil pressure? if so what is your oil pressure on the gauge? You should check these pointers as liquid could also do this.

  10. #10
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: low oil pressure different alarm

    What's the make and model of the chiller?

Similar Threads

  1. Carrier Transicold Container Problem
    By Shamel in forum Transport
    Replies: 39
    Last Post: 23-01-2012, 11:23 PM
  2. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 01:03 PM
  3. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •