30-07-2009, 01:54 AM #11
Re: AWHP superheat & sub-cooling
More of thinking out aloud.
TXV's excell at handling variable loads... and for this they need surplus refrigerant.
To extend the condenser storage idea & TXV a little further, on such systems. Would it be feasible to further over-size the condenser so that it sub-cools beyond the typical ~8K amount?
For example, to try & force a larger sub-cooling in the condenser through a combination of design over-surface & liquid-line design.Engineering Specialist - Cuprobraze, Nocolok, CD Technology