    Danfoss TS2 TEV outlet connection reduced



    All cold rooms in the system i'm working on are fitted with Danfoss TEV with connections 3/8" x 1/2". However, the valve outlets are directly soldered to 3/8" copper tubing immediately after the TEV's. The evaporators, about 10' away, have 3/8" inlet tubing.

    Will this affect the operation of the TEV's? Does this have to do with the frost over the TEV diaphragms?



  2. #2
    Join Date
    Feb 2007
    Location
    United Kingdom
    Age
    46
    Posts
    48
    Rep Power
    0

    Re: Danfoss TS2 TEV outlet connection reduced

    Hi mrfrost. It is good practice to fit the TEV as close to the inlet of the coil as possible as you will get a drop in duty the further away it is.

    With regards to the frost, this normally happens if the suction pressure is too low. Have you checked the inlet filter for blockage? Have you checked subcooling?

    The 1/2" to 3/8" shouldn't be a problem but the 10' distance definitely could be.
    www.compactaircon.co.uk

  3. #3
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Danfoss TS2 TEV outlet connection reduced

    danfoss used to state no more than 7 times the diameter of the pipe,7 x 12 equals length
    mmm to beer or not to beer...........lets drink breakfast

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Danfoss TS2 TEV outlet connection reduced

    Quote Originally Posted by carlfoster View Post
    ... It is good practice to fit the TEV as close to the inlet of the coil as possible as you will get a drop in duty the further away it is.
    Why's that? What about the expansion devices in AC's installed in the outdoor units?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Feb 2007
    Location
    United Kingdom
    Age
    46
    Posts
    48
    Rep Power
    0

    Re: Danfoss TS2 TEV outlet connection reduced

    Quote Originally Posted by Peter_1 View Post
    Why's that? What about the expansion devices in AC's installed in the outdoor units?
    I'm sure you've noticed that the pipe after the expansion device is cold to touch. That means it's absorbing heat. Some of the liquid is boiling off before it reaches the evaporator.

    Therefore, the evaporator doesn't receive the full amount of liquid and the TEV will have to open up more to keep the evaporator 'topped' up. This is fine as long as the condensing unit can provide sufficient liquid, but if the sizing is critical or maybe the weather is extreme then the system could suffer.

    When the supply to the evaporator is short, the pressure drops and you could get the icing up situation.

    Now, about the a/cs with the expansion device in the condensing unit; they have been specifically designed for this purpose. The pipe sizing is very rigid and maximum pipe lengths too prevent this situation from occurring. Also, you have to insulate both pipes now whereas you used to only have to insulate the suction.
    www.compactaircon.co.uk

Similar Threads

  1. Too dependent on Danfoss Valves
    By kelvin_27_84 in forum Industrial
    Replies: 8
    Last Post: 24-01-2009, 08:33 PM
  2. York ycaj Danfoss EKS65 phtq info
    By tomireland in forum Trouble Shooting
    Replies: 13
    Last Post: 22-12-2008, 06:47 PM
  3. Maximum centrifugal fan outlet velocity
    By abbasi in forum Fundamentals
    Replies: 6
    Last Post: 29-11-2008, 06:04 AM
  4. Temp. Rise at duct outlet
    By jwasir in forum Trouble Shooting
    Replies: 13
    Last Post: 10-05-2008, 04:22 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •