    Re: AWHP superheat & sub-cooling

    Quote Originally Posted by desA View Post
    ^^ Thanks for the pic.

    That would be fairly easy to implement. Install valve on water ?exit? line - install bulb in discharge line prior to condenser, or at entry.
    Yes, the valve would be installed at the water exit.

    On the end of that cap tube in the picture there is a 1/4 inch flare nut, which would be connected to a standard 1/4 inch access fitting, preferably in the discharge line prior to the condenser. It might be a good idea to also install a small shutoff valve between the access fitting and the flare nut, in case the valve may someday need to be replaced.