29-07-2009, 04:31 PM #11
Re: AWHP superheat & sub-cooling
Yes, the valve would be installed at the water exit.
On the end of that cap tube in the picture there is a 1/4 inch flare nut, which would be connected to a standard 1/4 inch access fitting, preferably in the discharge line prior to the condenser. It might be a good idea to also install a small shutoff valve between the access fitting and the flare nut, in case the valve may someday need to be replaced.Last edited by Gary; 29-07-2009 at 04:36 PM.