Thread: AWHP superheat & sub-cooling
Threaded View
-
29-07-2009, 02:51 PM #11
Re: AWHP superheat & sub-cooling
Now that we are maximizing the heat absorption on the low side, what remains is to transfer that heat to the water flowing through the condenser.
As heat is transferred from the refrigerant to the water, the refrigerant temp drops, having lost heat, and the leaving water temp rises, having gained heat.
The two temperatures "approach" each other. Thus the difference between the SCT temp and the leaving water temp is called the approach temp.
By installing a water regulating valve at the condenser outlet (which senses and controls SCT) we can regulate the flow to give us a steady SCT of 75C, which is the upper limit of the compressor.
Since the SCT is thereby fixed at 75C, the variable in our approach becomes the water leaving temp. The better the heat transfer, the higher the leaving water temp.
We need to have a condenser large enough to give us 65C leaving water temp, giving us an approach temp of 75-65=10K approach.
By increasing the condenser size beyond this minimum we can increase water temp and reduce the approach, but this again involves a point of diminishing returns.
I'm thinking a reasonable approach target would be about 5K (75-70=5K).Last edited by Gary; 29-07-2009 at 02:57 PM.
Similar Threads
-
9 superheat & subcooling scenarios
By nike123 in forum FundamentalsReplies: 39Last Post: 19-07-2011, 03:16 AM -
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
Some information on the aplication of suction gas/liquid line heat exchangers
By SteinarN in forum FundamentalsReplies: 5Last Post: 14-09-2009, 07:33 AM -
Low superheat and sucooling
By jayaeros in forum Trouble ShootingReplies: 23Last Post: 05-07-2009, 06:21 AM -
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM