    Re: AWHP superheat & sub-cooling

    Quote Originally Posted by desA View Post
    What are your thoughts on COP,hp optimisation?

    How to force the heat-pump system to operate on maximum COP,hp throughout the heating cycle?

    Now that we are maximizing the heat absorption on the low side, what remains is to transfer that heat to the water flowing through the condenser.

    As heat is transferred from the refrigerant to the water, the refrigerant temp drops, having lost heat, and the leaving water temp rises, having gained heat.

    The two temperatures "approach" each other. Thus the difference between the SCT temp and the leaving water temp is called the approach temp.

    By installing a water regulating valve at the condenser outlet (which senses and controls SCT) we can regulate the flow to give us a steady SCT of 75C, which is the upper limit of the compressor.

    Since the SCT is thereby fixed at 75C, the variable in our approach becomes the water leaving temp. The better the heat transfer, the higher the leaving water temp.

    We need to have a condenser large enough to give us 65C leaving water temp, giving us an approach temp of 75-65=10K approach.

    By increasing the condenser size beyond this minimum we can increase water temp and reduce the approach, but this again involves a point of diminishing returns.

    I'm thinking a reasonable approach target would be about 5K (75-70=5K).
    Last edited by Gary; 29-07-2009 at 02:57 PM.

Similar Threads

  1. 9 superheat & subcooling scenarios
    By nike123 in forum Fundamentals
    Replies: 39
    Last Post: 19-07-2011, 03:16 AM
  2. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  3. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  4. Low superheat and sucooling
    By jayaeros in forum Trouble Shooting
    Replies: 23
    Last Post: 05-07-2009, 06:21 AM
  5. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •