Thread: pipe freezing after the TEV
-
17-07-2009, 01:03 PM #1
pipe freezing after the TEV
Hi all , I have a water chiller ( YORK made ) and I have changed the TEV but I faced a freezing pipe after the new TEV when the Copm. goes on 100% load. when I run the Comp. on 50% load , all parameters are fine and within limite.
any Ideas to help me out
I'll be great full
Rifi
-
17-07-2009, 08:44 PM #2
Re: pipe freezing after the TEV
Hello Rifi.
When the comp is on 100% it will be pulling a lower suction (evaporator) pressure, at 50% load the evap pressure will be higher. The temp of the refrigerant in the evap will change with the pressure.
You need to give more information.
Why did you change the TEV?
Did you change like for like?
Did you fit the same size orrifice?
The pipe from the TEV to the evap may freeze if the evap pressure / temp is low enough, the only thingthat has changed is the TEV so there must be somthing different there.
Thanks taz.Last edited by taz24; 17-07-2009 at 08:48 PM.
-
18-07-2009, 12:56 AM #3
Re: pipe freezing after the TEV
Have you checked super heat of TEV. Has the water flow rate changed from design, with low water rate and at 100% duty, the suction drop will possibly form ice at TEV and you risk a freeze up and busting a tube.
magoo
-
18-07-2009, 01:31 AM #4
Re: pipe freezing after the TEV
If chiller is not tripping on anti-freeze stat in leaving water, but suction pressure at compressor is lower than say -3>4 'C SST., at 100 % duty. Then the orifice size is too small, which figures if all fine at 50% duty. Go back to manual that comes with package and re-check orifice assembly number for that package.
-
28-07-2009, 08:34 PM #5
Re: pipe freezing after the TEV
thx for your replay
as for more information, I am collecting them right now
but before that I have to try to re vacuum the system again for I think that there might be a ice bubble occurring at the TEV orifice
let me try and come back to you
thankx again for your immediate replay
regards
Rifi
-
28-07-2009, 08:40 PM #6
Re: pipe freezing after the TEV
Last edited by Gary; 28-07-2009 at 08:42 PM.
-
28-07-2009, 08:41 PM #7
Re: pipe freezing after the TEV
-
28-07-2009, 09:06 PM #8
Re: pipe freezing after the TEV
So far you seem to be saying that everything is working fine... but you are somehow offended by the sight of frost on the line leaving the TXV.
Cover the line with insulation and you won't see the frost anymore...
or is there an actual problem with the system's operation that you haven't mentioned yet?Last edited by Gary; 15-08-2009 at 01:48 AM.
Similar Threads
-
A\C suction pipe freezing
By cretan in forum Air ConditioningReplies: 16Last Post: 03-09-2008, 07:32 AM -
pipe freezing just outside the compressor
By guestingmale in forum DomesticReplies: 71Last Post: 24-08-2008, 07:57 PM -
Freezing thin pipe on new a/c unit.
By mousey1986 in forum Trouble ShootingReplies: 19Last Post: 29-07-2008, 12:29 AM -
Freezing at Compresser/suction pipe
By albertjoseph in forum Trouble ShootingReplies: 8Last Post: 18-05-2008, 05:10 AM -
Mitsi split freezing HP pipe
By Bat in forum Air ConditioningReplies: 8Last Post: 13-05-2008, 12:01 AM