    pipe freezing after the TEV



    Hi all , I have a water chiller ( YORK made ) and I have changed the TEV but I faced a freezing pipe after the new TEV when the Copm. goes on 100% load. when I run the Comp. on 50% load , all parameters are fine and within limite.

    any Ideas to help me out

    I'll be great full



    Rifi



  2. #2
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: pipe freezing after the TEV

    Quote Originally Posted by nassrifi View Post
    Hi all , I have a water chiller ( YORK made ) and I have changed the TEV but I faced a freezing pipe after the new TEV when the Copm. goes on 100% load. when I run the Comp. on 50% load , all parameters are fine and within limite.

    any Ideas to help me out

    I'll be great full



    Rifi

    Hello Rifi.

    When the comp is on 100% it will be pulling a lower suction (evaporator) pressure, at 50% load the evap pressure will be higher. The temp of the refrigerant in the evap will change with the pressure.


    You need to give more information.

    Why did you change the TEV?
    Did you change like for like?
    Did you fit the same size orrifice?

    The pipe from the TEV to the evap may freeze if the evap pressure / temp is low enough, the only thingthat has changed is the TEV so there must be somthing different there.

    Thanks taz.
    Last edited by taz24; 17-07-2009 at 08:48 PM.

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: pipe freezing after the TEV

    Have you checked super heat of TEV. Has the water flow rate changed from design, with low water rate and at 100% duty, the suction drop will possibly form ice at TEV and you risk a freeze up and busting a tube.
    magoo

  4. #4
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: pipe freezing after the TEV

    If chiller is not tripping on anti-freeze stat in leaving water, but suction pressure at compressor is lower than say -3>4 'C SST., at 100 % duty. Then the orifice size is too small, which figures if all fine at 50% duty. Go back to manual that comes with package and re-check orifice assembly number for that package.

  5. #5
    Join Date
    Jul 2009
    Location
    Aden
    Age
    65
    Posts
    13
    Rep Power
    0

    Re: pipe freezing after the TEV

    thx for your replay
    as for more information, I am collecting them right now
    but before that I have to try to re vacuum the system again for I think that there might be a ice bubble occurring at the TEV orifice

    let me try and come back to you


    thankx again for your immediate replay

    regards


    Rifi

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: pipe freezing after the TEV

    Quote Originally Posted by nassrifi View Post
    Hi all , I have a water chiller ( YORK made ) and I have changed the TEV but I faced a freezing pipe after the new TEV when the Copm. goes on 100% load. when I run the Comp. on 50% load , all parameters are fine and within limite.
    So... what makes you think there is a problem?
    Last edited by Gary; 28-07-2009 at 08:42 PM.

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: pipe freezing after the TEV

    Quote Originally Posted by nassrifi View Post
    thx for your replay
    as for more information, I am collecting them right now
    but before that I have to try to re vacuum the system again for I think that there might be a ice bubble occurring at the TEV orifice
    So... what makes you think there might be an ice bubble?

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: pipe freezing after the TEV

    So far you seem to be saying that everything is working fine... but you are somehow offended by the sight of frost on the line leaving the TXV.

    Cover the line with insulation and you won't see the frost anymore...

    or is there an actual problem with the system's operation that you haven't mentioned yet?
    Last edited by Gary; 15-08-2009 at 01:48 AM.

Similar Threads

  1. A\C suction pipe freezing
    By cretan in forum Air Conditioning
    Replies: 16
    Last Post: 03-09-2008, 07:32 AM
  2. pipe freezing just outside the compressor
    By guestingmale in forum Domestic
    Replies: 71
    Last Post: 24-08-2008, 07:57 PM
  3. Freezing thin pipe on new a/c unit.
    By mousey1986 in forum Trouble Shooting
    Replies: 19
    Last Post: 29-07-2008, 12:29 AM
  4. Freezing at Compresser/suction pipe
    By albertjoseph in forum Trouble Shooting
    Replies: 8
    Last Post: 18-05-2008, 05:10 AM
  5. Mitsi split freezing HP pipe
    By Bat in forum Air Conditioning
    Replies: 8
    Last Post: 13-05-2008, 12:01 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •