    York Recip Millenium Chiller
    Been to site to look at a chiller fault. Both circuits tripping out on LWT sens fault. No manuals on site. Looked at the PCB two red LEDs on top right both lit. Any ideas.
    a problem shared is a problem halved
    Jul 2005
    INDIA
    14
    Re: York Recip Millenium Chiller
    check the two wires sensor LWT,for loose connection , or corrosion , check its connector, or replace the connector with normal screw type connector, repair the wires if damage, or replace the thermistor.
    Feb 2004
    Australia
    286
    Sorted it out now thanks. LW temp sensor had to be removed and the chiller run down to design temps before replacing it. I think it had gone off on a low current/MP/HP fault making the water temp rise too high
    Thanks for the reply
    Jun 2006
    Portugal
    10
    The latest EPROMīs resolve the problem as they allow the chiller to run longer before tripping, thus allowing the water temp to lower.
    clarkster's Avatar
    clarkster Guest
    having simular problem cant find manuals for this machine, cpu trouble and remote control problem trouble,ugg if you find something please let me know,, clarkster
    Feb 2004
    Australia
    286
    I've got manuals for most of the York machines, all the Carrier and Trane ones
    May 2006
    Burminam town!
    49
    12
    mmm, ive had that fault a few times and changed several sensors. think i'll take the connecter out and solder straight through. - dont suppose anyone got the specific manual for the york 'ISN millenium recip pak' controller, its a bitch to get hold of.
    ireland
    1,452
    Koolio
    it may not be the connection, water in the pockets kills the feckers as well, change them on a monthly basis on the YCAL chillers.
    al
    Apr 2009
    israel
    778
    hi i have the manual will try to upload on sunday
    May 2006
    Burminam town!
    49
    12
    Quote Originally Posted by al View Post
    Koolio
    al
    thx al = i'll fill the pocket full of heat transfer paste nex time
    May 2006
    Burminam town!
    49
    12
    Quote Originally Posted by goshen View Post
    thx goshen, where is it i'd find them then? once you've uploaded?
    May 2006
    Burminam town!
    49
    12
    bearing in mind - i have the manual for the chiller / it's the manual for the ISN millenium recip pak controller im after.
    Apr 2009
    israel
    778
    hi there i sent u the manual via email hope it is ok if notlet me know i will try to get it
    http://dl.owneriq.net/b/bd843a30-488...b4334830e0.pdf try this in case what i sent was not ok
  1. York Millenium Screw Chiller
    By iceman007 in forum Industrial Compressors
    Last Post: 15-01-2011, 11:56 PM
  2. York Chiller
    By HVACGod in forum Commercial
    Last Post: 11-09-2010, 06:05 AM
  3. York Chiller
    By RubenJLL in forum Trouble Shooting
    Last Post: 18-04-2008, 04:08 PM
  4. York Screw Chiller How low will it go?????
    By bruceboldy in forum Industrial Compressors
    Last Post: 10-08-2007, 10:29 PM
  5. York process chiller repairs
    By Matt in forum Commercial
    Last Post: 23-03-2004, 11:07 PM