27-07-2009, 06:21 PM #1
York Reciprocating Chiller - %Motor Current
Hello I am new to the site and this is my first post here. I have been working through some issues with a York Reciprocating chiller. One plant in particular had power secured to both the controller cabinet as well as the microprocessor cabinet for the replacement of all four motor contactors. Power was removed from the system for about a month. Upon start-up the displayed % Motor Current was about twice the value it should have been. I checked the wiring to the contactors, CT's, calibration resistors(for proper seating and resistance value) and all seems to be right.
Is it possible that the EEPROM that stores the data which gives the comparison circuit basically the denominator for the microprocessor to determine % motor current somehow defaulted to another value when power was removed from the machine?
The line current for each running compressor was about 30 to 40 amps. The RLA values for both compressors were 77 and 95 amps respectively.
Thanks,
JR
-
27-07-2009, 11:54 PM #2
Re: York Reciprocating Chiller - %Motor Current
It is likely that the proccessor backup batary has gone flat and lost memory.What is the model of chiller? If there are more than one of that same chiller you could try swaping boards to comfirm(check batary first).
-
28-07-2009, 01:24 AM #3
Re: York Reciprocating Chiller - %Motor Current
The model # is YCJW56HF0-46PW.
-
28-07-2009, 05:39 PM #4
Re: York Reciprocating Chiller - %Motor Current
need to check the unloader solenoids are all energised on start up. de-energised for loading.
-
28-07-2009, 05:49 PM #5
Re: York Reciprocating Chiller - %Motor Current
Taking into account RLA current your stated running current is about right so I suspect as in the previous post that the stored memory of your controller was lost.
Similar Threads
-
York Chiller problems
By ingherrera in forum CommercialReplies: 18Last Post: 26-07-2011, 03:10 PM -
York reciprocating chiller YCAJ
By soapboxdriver in forum Refrigeration BooksReplies: 5Last Post: 27-01-2009, 02:46 PM -
York Chiller startup when on Emergency Power
By Apollo10 in forum Trouble ShootingReplies: 3Last Post: 22-12-2008, 07:13 PM -
york chiller motor rotation error
By cesarnino in forum Trouble ShootingReplies: 7Last Post: 13-12-2008, 03:43 PM -
York & Trane Reciprocating Chiller
By Gigas in forum Air ConditioningReplies: 3Last Post: 21-05-2008, 12:21 AM