Results 1 to 5 of 5
  1. #1
    subdude's Avatar
    subdude Guest

    York Reciprocating Chiller - %Motor Current



    Hello I am new to the site and this is my first post here. I have been working through some issues with a York Reciprocating chiller. One plant in particular had power secured to both the controller cabinet as well as the microprocessor cabinet for the replacement of all four motor contactors. Power was removed from the system for about a month. Upon start-up the displayed % Motor Current was about twice the value it should have been. I checked the wiring to the contactors, CT's, calibration resistors(for proper seating and resistance value) and all seems to be right.

    Is it possible that the EEPROM that stores the data which gives the comparison circuit basically the denominator for the microprocessor to determine % motor current somehow defaulted to another value when power was removed from the machine?

    The line current for each running compressor was about 30 to 40 amps. The RLA values for both compressors were 77 and 95 amps respectively.

    Thanks,
    JR



  2. #2
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: York Reciprocating Chiller - %Motor Current

    It is likely that the proccessor backup batary has gone flat and lost memory.What is the model of chiller? If there are more than one of that same chiller you could try swaping boards to comfirm(check batary first).

  3. #3
    subdude's Avatar
    subdude Guest

    Re: York Reciprocating Chiller - %Motor Current

    The model # is YCJW56HF0-46PW.

  4. #4
    Alan 01's Avatar
    Alan 01 Guest

    Re: York Reciprocating Chiller - %Motor Current

    need to check the unloader solenoids are all energised on start up. de-energised for loading.

  5. #5
    Join Date
    May 2008
    Location
    Malta
    Age
    68
    Posts
    67
    Rep Power
    17

    Re: York Reciprocating Chiller - %Motor Current

    Taking into account RLA current your stated running current is about right so I suspect as in the previous post that the stored memory of your controller was lost.

Similar Threads

  1. York Chiller problems
    By ingherrera in forum Commercial
    Replies: 18
    Last Post: 26-07-2011, 03:10 PM
  2. York reciprocating chiller YCAJ
    By soapboxdriver in forum Refrigeration Books
    Replies: 5
    Last Post: 27-01-2009, 02:46 PM
  3. York Chiller startup when on Emergency Power
    By Apollo10 in forum Trouble Shooting
    Replies: 3
    Last Post: 22-12-2008, 07:13 PM
  4. york chiller motor rotation error
    By cesarnino in forum Trouble Shooting
    Replies: 7
    Last Post: 13-12-2008, 03:43 PM
  5. York & Trane Reciprocating Chiller
    By Gigas in forum Air Conditioning
    Replies: 3
    Last Post: 21-05-2008, 12:21 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •