    Condenser flexible connection??



    Hi all!

    I am pricing a job and the Mechanical Specification is asking for the following: "Final connections shall include bends with two degrees of movement to allow for vibration and movement for units.....".

    This refers to the installation of two hi-wall (2.5kW and 3.5kW), one 5kW split ducted and one ceiling cassette 12kW, with 4 condensers on a roof platform.

    I could not find someone to know where these bends with two degrees of movement can be sourced from... I always disregarded this requirement in the Mech Spec and nobody complained so far, but I want to better understand why is it specified in the first place... I mean... I understand why, buy why nobody seems to know about them?

    Any help will be appreciated.

    Regards,
    Chris.



  2. #2
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Condenser flexible connection??

    Its sounds like a spec for steel pipes.

    In my opinion you really don't need a flexible connection to allow a 2 degree movement. Even a short radius elbow would allow that.

    In your position I would form the bends with a set of benders that give a reasonabley long radius.

    Never heard of it for interconnecting copper piping but that doesn't mean it doesn't exist.

    Good luck
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: Condenser flexible connection??

    your specifier has totally screwed up, plucked the wrong spec sheet, challenge them on spec..,
    magoo

  4. #4
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Condenser flexible connection??

    yep they do exist,one mob is gomax whoever they are,its called gomax infinity hose
    mmm to beer or not to beer...........lets drink breakfast

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Condenser flexible connection??

    The term I have heard for the item in question is called a vibration eliminator. These are usually used to reduce transmission of equipment generated vibration to the building structure or downstream of the equipment. They will also provide some flexibility in the piping for equipment movement due to operation (starting a compressor which is mounted on flexible mounts) and for expansion and contraction of the pipe due to thermal growth.

    Most of the required flexibility for the piping can be provided by using a minimum of three changes in direction. A situation (that I call hard piped) is where the pipe is ran directly from a point to a point without any changes in direction. The expansion/contraction of piping in this type of installation can be a problem as it is stiff and not flexible.
    If all else fails, ask for help.


  6. #6
    Join Date
    Jun 2009
    Location
    Columbus Ohio
    Age
    55
    Posts
    169
    Rep Power
    15

    Re: Condenser flexible connection??

    I dont know with minisplits.. but I know in the real world in large units i have made a lot of $$ replacing vibration eliminators for on-call service calls... I used to keep them in stock (when I was in the commercial HVAC business) they seem to be a common failure point...

    with an inverter type minisplit you will notice a little vibration at slower compressor speeds.. seems to carry through through the copper piping.. with non inverter I dont notice it at all....
    however like above.. i wouldnt just "hard pipe" it in..
    -Christopher

  7. #7
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Condenser flexible connection??

    As mentioned, these are not an assurance of problems solved. I have seen these deform from freezing or extended use also. And... the have to be installed correctly. They are not flexible to allow bad piping jobs!
    If all else fails, ask for help.


  8. #8
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: Condenser flexible connection??

    In Earthquake-ville NZ [ commonly know as 'the shakey Isles' ]they could be wanting some sort of isolation. Vib-illiminators. Personally wouldn't bother. Would be the last I would be worrying about if the building fell apart in an earthquake. As for out door unit deflection from vibration, does not happen. The manufactures have that covered in system design

  9. #9
    Join Date
    Sep 2005
    Location
    Granard, Ireland
    Age
    55
    Posts
    43
    Rep Power
    0

    Re: Condenser flexible connection??

    Hi
    Any movement should be taken care of inside the condenser unit and if your units are securely mounted they should not be moving anywhere.

    FIXIT
    First time every time..

  10. #10
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: Condenser flexible connection??

    Paul


    "KEEP IT COOL"

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Clean Condenser Running too hot??
    By Chseybold in forum Trouble Shooting
    Replies: 81
    Last Post: 03-01-2010, 11:50 PM
  3. Air Cooled Condenser Leakage Problem with R-404A
    By RADHAKRISHNARAO in forum Technical Discussions
    Replies: 19
    Last Post: 30-07-2008, 12:21 PM
  4. Different brand condenser and coil connection
    By frankfrank in forum Technical Speculations
    Replies: 0
    Last Post: 23-06-2008, 07:31 AM
  5. Plate Heat Exchagers - Condenser
    By Billy Ray in forum Technical Discussions
    Replies: 9
    Last Post: 11-05-2008, 06:16 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •