Thread: eliwell controller problems
23-07-2009, 05:53 PM #1
I have an eliwell controller ID COOL series, problem is on the 240v supply in to the controller i am getting 240v out of the neutral, controller works but puts 240v accross all neutrals on the cabinet disabling compressor etc, controller is brand new, anyone else had similar problems
23-07-2009, 06:27 PM #2
Re: eliwell controller problems
Hi Northdude.
Have you tried swapping Terminals 6 and 7 over?
23-07-2009, 07:36 PM #3
Sounds like you've got a broken neutral. Work backwards from the neutral at the power supply until you find the break - its probably a loose connection somewhere.
23-07-2009, 07:53 PM #4
yes tried swapping them over and still getting live down neutral. I disconnected my neutral off the controller so all i had was the live in, i tested the neutral terminal on the back of the controller and it had 240v on it so it must be the controller. Just seems strange
23-07-2009, 09:31 PM #5
you've lost your neutral mate.
23-07-2009, 10:12 PM #6
I agree with Frosty and Chillyblue.
I suspect they are correct.
Good luck and plesae let us know how you get on.
24-07-2009, 07:24 PM #7
You have a floating neutral. Try to find a fixed neutral point and connect all your neutral wiring to this point.
I am not always right, but I'm never wrong!
25-07-2009, 07:05 AM #8
does the display light up?
Eliwell 901 Controller Parameters
By Northdude in forum CommercialReplies: 18Last Post: 09-12-2009, 12:22 AM -
Daikin controller
By mchild in forum Air ConditioningReplies: 8Last Post: 02-10-2009, 07:14 PM -
Eliwell EWPX172AR controller
By fridgability in forum ElectricalReplies: 7Last Post: 19-12-2008, 12:32 AM -
Eliwell ID961E & 985E controller
By SPBDASAN in forum ElectricalReplies: 3Last Post: 01-12-2008, 07:10 AM -
Daikin Controller
By mchild in forum Air ConditioningReplies: 11Last Post: 24-11-2008, 02:34 AM