Short of Gas in R404 serve over
I recently went to a job and found 2 seperate condensers short of gas, I also found the condensers blocked with dust and flour as they were in a bakery the gas was R404a, I leak testedthe system and found no leaks in the system so weighed in my gas a they ran perfectly, I was wondering due to the blocked condensers I know this might be stupid but would the gas boil off and is that why there is a shortage of gas as there was def no leaks in the system.
-
22-07-2009, 01:26 PM #2
Re: Short of Gas in R404 serve over
I presume you reclaimed it out so it's a simple matter of out v in difference isn't it?
However gas doen't boil off liquid does, but yes if it can't condense then it can't boil off again..
-
22-07-2009, 01:40 PM #3
Re: Short of Gas in R404 serve over
Sorry yes I did reclaim so there is a possibility the liquid could boil of
-
27-07-2009, 01:17 PM #4
Re: Short of Gas in R404 serve over
regardless of the state of the refrigerant there should be the same amount in as was originally charged unless there is a leak, some cowboys will let charge out to lower head pressures rather than looking at the cause, ie blocked condenser, poor ventilation etc, maybe that's what happened?
-
29-07-2009, 08:41 PM #5
Re: Short of Gas in R404 serve over
The difference between genius and stupidity is that genius has its limits.
Marc
-
29-07-2009, 09:43 PM #6
Re: Short of Gas in R404 serve over
if you have a severely blocked condenser you might have some micro leaks on the system that cant handle the high HP. I would re charge system with arglow leak dye to cover yourself and show up any leaks in the future if no pressure drop seen using OFN.
-
30-07-2009, 12:57 PM #7
Re: Short of Gas in R404 serve over
If condenser was blocked and yet could put in more gas could mean micro leaks which could surface later .
If the refrigerant has not leaked out , system would refuse to accept further gas as it would reflect on discharge pressure
Similar Threads
-
appears short of refrigerant
By TECH TIM in forum CommercialReplies: 11Last Post: 11-02-2009, 11:48 AM -
R404
By Giannis in forum RefrigerantsReplies: 22Last Post: 13-02-2008, 08:41 PM -
SCR short in soft starter.
By mrsparky in forum ElectricalReplies: 0Last Post: 14-12-2007, 12:19 PM -
Walk in Cooler (short cycling)
By Brandon in forum Trouble ShootingReplies: 11Last Post: 05-05-2003, 11:43 AM -
using R404 to chill watermixture
By fredperry in forum Technical DiscussionsReplies: 21Last Post: 21-05-2002, 10:44 PM