Thread: running 2 core sensor cable
-
22-05-2009, 11:36 AM #1
running 2 core sensor cable
greetings gentleman
advice required please... on a job running sensor cables eg supply air,ambient,return air, on coil, from a air con unit on a roof to a control panel in a plant room.
I know your not supposed to run it with your mains cable how ever if you have no other way but to go the same route as your mains is run on cable tray to your control panel is there any serious inplications if you do it that way /long term?
thank you in advance for your replys gentleman...
-
22-05-2009, 12:25 PM #2
Re: running 2 core sensor cable
sensorman,
you are right that sensor cable should not be run with power lines.Static,distortion and in accuracy in transmitting signals from sensor to electronic modules will result to errors.abet
-
22-05-2009, 03:10 PM #3
Re: running 2 core sensor cable
If you use a good quality shielded cable you shoudn't have any problems.
PP
-
22-05-2009, 05:02 PM #4
Re: running 2 core sensor cable
use screened cable,cost more but will do the job!
-
22-05-2009, 11:09 PM #5
Re: running 2 core sensor cable
As they say, used screened cable but, please, only earth one end of the shield.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
30-06-2009, 06:16 PM #6
Re: running 2 core sensor cable
Agree with pp, wandowski and Brian. Get the fully screened cable, the one with the woven screen around the leads.
-
30-06-2009, 07:23 PM #7
Re: running 2 core sensor cable
Hi
Don't know weather this is correct but i got told standard PTC or NTC probes can be run using any old cable up to 1000mtrs as they measure a very large resisitance between deg's.
i've seen loads run in .75mm 3 core flex along side, wrapped around and on top of swa cables and never presented problems in years, they work fine.
P.S. this is probes used on temp controllers for Lae, elliwel, etc, etc
i'm not saying it's right, just what i've seen and been told
CB
-
30-06-2009, 08:17 PM #8
Re: running 2 core sensor cable
as others say, we use CY cable 1.5mm (not sure what cy stands for :-P)if long runs, with the screened earthed at one end only.
-
01-07-2009, 07:09 AM #9
Re: running 2 core sensor cable
as chillyblue says i agree given maximum distance recommended by manufacturers,but have had the rare occasion where interference was giving problems.shielded is definitely the way to go.
mmm to beer or not to beer...........lets drink breakfast
-
01-07-2009, 08:37 PM #10
Similar Threads
-
Problems with compressor running too cold
By abrando1 in forum Trouble ShootingReplies: 8Last Post: 12-05-2009, 10:08 PM -
Core drill for rock
By paul_h in forum Tools and CalculatorsReplies: 20Last Post: 17-05-2008, 12:47 AM -
Walkin cooler running to warm need help
By The Butcher in forum Trouble ShootingReplies: 7Last Post: 03-08-2007, 09:19 PM -
Running Costs
By Abe in forum Air ConditioningReplies: 4Last Post: 09-04-2007, 12:58 AM