    Pipe size?



    Can anyone tell me what size suction line i would require for a load of 23kw @-35 on r404a the distance would be about 50 metres with two risers.



  2. #2
    Join Date
    Jun 2007
    Location
    South Africa
    Age
    66
    Posts
    120
    Rep Power
    17

    Re: Pipe size?

    Based on 23 kw @-35 C and 40 C condensing for R-404A at a 50m pipe run:
    Suction Line = 2 5/8"
    Liquid Line = 3/4"
    Suction Riser= 2 1/8"