Thread: r404a
25-06-2009, 11:27 PM #1
r404a
went to look at a LTcoldroom 2nite. Replced tev, orifice and drier, on start up coldroom at +11 on departure -1 blew cond coil through with ofn, all fan motors working, back pressure at 45ps head pressure 300psi, evap coil probe temp -10, was wandering if this sounded about right, ambient temp aprox +24c and coldroom fullyloaded , on arrival coldroom reading +6c and stock starting to thaw. Had to leave site when coldroom at -1c due to owner wanting to get to a meeting, was wandering weather head pressure to high. thanks guys any help would be great
26-06-2009, 12:19 AM #2
26-06-2009, 03:06 AM #3
Re: r404a
yeah mate the high heatload will make for a slow pull down and higher condensing pressures,id be shopping elsewhere for a month or so
26-06-2009, 07:17 AM #4
Re: r404a
It will take a while to pull down.
I hope they sorted out what cant be re frozen like ice cream, fish, poultry .....
26-06-2009, 07:56 AM #5
Re: r404a
thanks guys will ring this orning and see what temp it has reached
26-06-2009, 08:41 PM #6
Re: r404a
i would say that this is a bit high even more so the suction presure especially if you blew condenser and all the fans are running did you vac out the system prior to opening up system?
26-06-2009, 09:06 PM #7
Re: r404a
colhibby, thanks for the reply, i pumped down prior to valve/drier change so purged refrigerant through suction.
Max low side pressure in R404A system
By Wilade in forum Technical DiscussionsReplies: 8Last Post: 25-08-2009, 09:23 PM -
Accidentally mixed R404A with R134a
By toma in forum Trouble ShootingReplies: 1Last Post: 13-08-2008, 03:33 PM -
R507 to R404a
By Andy AC in forum CommercialReplies: 2Last Post: 09-08-2008, 05:36 PM -
Why not R404a?
By afak in forum Technical SpeculationsReplies: 12Last Post: 02-04-2007, 08:58 PM -
R134a or R404a
By jingua_ph in forum RefrigerantsReplies: 4Last Post: 27-09-2006, 03:31 PM