    r404a



    went to look at a LTcoldroom 2nite. Replced tev, orifice and drier, on start up coldroom at +11 on departure -1 blew cond coil through with ofn, all fan motors working, back pressure at 45ps head pressure 300psi, evap coil probe temp -10, was wandering if this sounded about right, ambient temp aprox +24c and coldroom fullyloaded , on arrival coldroom reading +6c and stock starting to thaw. Had to leave site when coldroom at -1c due to owner wanting to get to a meeting, was wandering weather head pressure to high. thanks guys any help would be great



  2. #2
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: r404a

    Quote Originally Posted by mcunliffe4 View Post
    went to look at a LTcoldroom 2nite. Replced tev, orifice and drier, on start up coldroom at +11 on departure -1 blew cond coil through with ofn, all fan motors working, back pressure at 45ps head pressure 300psi, evap coil probe temp -10, was wandering if this sounded about right, ambient temp aprox +24c and coldroom fullyloaded , on arrival coldroom reading +6c and stock starting to thaw. Had to leave site when coldroom at -1c due to owner wanting to get to a meeting, was wandering weather head pressure to high. thanks guys any help would be great

    300psi is about 20 b and that is about 45deg c.

    Doing all that work in that ambient, seems about right to me.

    It is as high as it wants to get because I bet the hp will be set to about 22b.

    taz.

  3. #3
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: r404a

    yeah mate the high heatload will make for a slow pull down and higher condensing pressures,id be shopping elsewhere for a month or so
    mmm to beer or not to beer...........lets drink breakfast

  4. #4
    Join Date
    Jun 2005
    Location
    Stoke on Trent
    Age
    62
    Posts
    588
    Rep Power
    20

    Re: r404a

    It will take a while to pull down.

    I hope they sorted out what cant be re frozen like ice cream, fish, poultry .....

  5. #5
    Join Date
    Jun 2008
    Location
    gloucester
    Age
    44
    Posts
    72
    Rep Power
    17

    Re: r404a

    thanks guys will ring this orning and see what temp it has reached

  6. #6
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    20

    Re: r404a

    i would say that this is a bit high even more so the suction presure especially if you blew condenser and all the fans are running did you vac out the system prior to opening up system?

  7. #7
    Join Date
    Jun 2008
    Location
    gloucester
    Age
    44
    Posts
    72
    Rep Power
    17

    Re: r404a

    colhibby, thanks for the reply, i pumped down prior to valve/drier change so purged refrigerant through suction.

Similar Threads

  1. Max low side pressure in R404A system
    By Wilade in forum Technical Discussions
    Replies: 8
    Last Post: 25-08-2009, 09:23 PM
  2. Accidentally mixed R404A with R134a
    By toma in forum Trouble Shooting
    Replies: 1
    Last Post: 13-08-2008, 03:33 PM
  3. R507 to R404a
    By Andy AC in forum Commercial
    Replies: 2
    Last Post: 09-08-2008, 05:36 PM
  4. Why not R404a?
    By afak in forum Technical Speculations
    Replies: 12
    Last Post: 02-04-2007, 08:58 PM
  5. R134a or R404a
    By jingua_ph in forum Refrigerants
    Replies: 4
    Last Post: 27-09-2006, 03:31 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •