How to determine the amount of refrigerant charged in a system?
Dear friends, i am a freshman in this area. Thanks for all guys helping me before in this forum.
Now, i have a question. i bought a L'UNITE HERMETIQUE (FH4518Y) refrigeration unit. There is a oil separator after compressor and accumulator before compressor. The medium is R134a. i want keep the evaporator temperature at about 20 to 25 degree C.
How can i determine the amount of R134a charged in this system? Any corrolation is useful?
Thanks a lot.
-
27-05-2009, 07:28 PM #2
Re: How to determine the amount of refrigerant charged in a system?
Till your SH becomes within the desired range, +/- 5 to 7 K.
Or a full sightglass if fitted.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
27-05-2009, 07:43 PM #3
Re: How to determine the amount of refrigerant charged in a system?
Has the seller said you the unit is filled with R134 - not with nitrogen ?
-
28-05-2009, 02:52 AM #4
Re: How to determine the amount of refrigerant charged in a system?
What is this, trade training by remote control ?.
magoo
-
28-05-2009, 04:23 AM #5
Re: How to determine the amount of refrigerant charged in a system?
hi ya frank,
Can't help much, dunno whether this chart will help you
Good luck dude
-
28-05-2009, 06:22 AM #6
-
28-05-2009, 06:25 AM #7
-
28-05-2009, 06:27 AM #8
-
28-05-2009, 06:28 AM #9
-
28-05-2009, 03:41 PM #10
Re: How to determine the amount of refrigerant charged in a system?
Hi Frank. Thank you for the inadvertent bit of "trade training", now I know FH4518Ys and the like ones ref. units are being sold pre-filled with the charge of the corresponding refrigerant - simply like ACs are.
-
29-05-2009, 03:34 AM #11
-
29-05-2009, 04:20 AM #12
Re: How to determine the amount of refrigerant charged in a system?
find out what is the design suction &discharge temperature and chage and after operating for some time measure the sub cooling and Super heat so that is correct.
all the above is done preferably closer to design conditions.
-
29-05-2009, 05:03 PM #13
-
21-06-2009, 08:34 AM #14
-
22-06-2009, 04:52 AM #15
Re: How to determine the amount of refrigerant charged in a system?
manufacturers usually rate capacities on coils,add a bit for receiever and liquid line for a rough guide and complete charge with a sight glass,next time you discharge unit use a recovery machine with a bottle and a set of scales.the hierachy also reckons it helps save the planet
mmm to beer or not to beer...........lets drink breakfast
-
22-06-2009, 11:31 AM #16
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: How to determine the amount of refrigerant charged in a system?
If the room temperature is 25°C than target evaporation temperature of your evaporator is between 5 and 10°C (depending on evaporator air flow and evaporator superheat).
You cannot have evaporator and room air temperature (evaporator air entering) same, since there will be no heat transfer in that case.
Depending on expansion device type (capillary tube or TEV) you should charge to about 7K subcooling (TEV) or by superheat table (capillary) when room temperature is near designed and condensation temperature around 40°C.
http://www.mediafire.com/?wzgtwmyhzty
Similar Threads
-
Leak Testing?
By Thana in forum Trouble ShootingReplies: 36Last Post: 31-08-2010, 02:57 PM -
automating a chilled brine refrigeration system using ammonia refrigerant
By luciom in forum IndustrialReplies: 29Last Post: 02-10-2008, 09:48 PM -
Non condensables??
By ChillTechnican in forum Trouble ShootingReplies: 80Last Post: 09-03-2008, 11:45 AM -
R507 in an R134a compressor: system design
By DaBit in forum Technical SpeculationsReplies: 17Last Post: 01-05-2003, 09:25 AM -
Refrigeration system proposal; comments please.
By DaBit in forum Technical SpeculationsReplies: 13Last Post: 01-01-2003, 03:42 PM