Results 51 to 95 of 95
14-04-2008, 12:21 AM #51
Re: TXV's To Adjust or Not to Adjust - That is ....
i have enjoyed reading this discussion so far but would like to ask what should the procedure be when, in these times of energy saving, consulting engineers are requesting that operating condensing pressures be reduced from 14.5 bar to 11 bar. if the performance of the valve is in part based on the pressure drop across it, then surely a 3 to 3.5 bar decrease in pressure drop would naturally change the valve/orifice combination's capacity. this surely would therefore force a change of orifice or superheat setting. we do not however receive instruction on this with the comment "the change is not large enough to warrant replacement or adjustment". i have not yet made the time to measure any change, but the 25% change in pressure drop woluld surely have a significant effect on the system operation. does anybody have experience of this?
14-04-2008, 02:58 AM #52
Hav to say one of the best discussions in a long time. Spent 7 yrs at a counter now 14 years field with 7 owning my company. Same rule stands... don't mess with a valve unless you have a spare on hand. Totally agree that some techs like to think they know how to read and set properly. A couple of nightmare situations and a " good " tech learns not to touch what he can't understand. I am learning everyday MY LIMITS and look for the problem before I apply the solution. Again....great discussion!!! Thanks.
14-04-2008, 04:43 AM #53
Originally Posted by bill1983
The colder liquid tends to increase the valve capacity, while the lower differential pressure causes the valve capacity to be reduced.
Therefore, what you loose in one condition the other helps to increase. You have to look at the manufacturers ratings and correction factors to see where indeed this balances out in the this condition.
On the other hand, trying to lower the condensing pressure in the summer is a limit of the condensing heat transfer surface available. If the condenser was sized to reject the full load heat at 14.5 bar, then that is where it will want to operate.If all else fails, ask for help.
14-04-2008, 09:56 AM #54
Personally, I will agree with this statement, many TXV is already pre-set from the factory.
But certain case, only by "professional" in refrigeration, you may do some adjustment, which you can find in instruction letter come along with TXV packaging, mentioned to turn clock-wise or anticlockwise vice versa. But straightly recommend only for "professional", which they may spend whole day or even couple days for "tune" and "adjust" TXV into the right proper system they want it to be.
Hope this is usefull.
Regards,
14-04-2008, 01:57 PM #55
You are right - don't touch what you don't understand, but if you can't adjust a txv to maximise its operation and just change them whenever they don't do what you want, then... well.... um... I'm lost for words.
How would you go getting a butcher's coldplate to flood fully and not smash valveplates? They don't always do what you want out of the box and no amount of changing parts will help you. Sometimes you need to use the old noggin (aka grey matter) and spend the time to watch the evap operation.
Most danfoss valves require a PD of between 10 and 12 bar across the valve before capacity is dramatically reduced and as mentioned before the subcooled liquid temps decrease the percentage of flash gas and thereby allow capacity to be increased....and she said "give it to me you big fridgie"
14-04-2008, 02:37 PM #56
- Sep 2007
- Split Croatia
- 57
- 6,151
- 6
- 36
I just want to add here, that most of the tools we have to measure superheat, are not calibrated, low accuracy and repeatability, and measurement's (pressure) are often not taken at evaporator. That fact of life also makes few more arguments in favor to not adjust TEV unless you are 100% sure that it is needed and that your measured data are of any good.
14-04-2008, 03:34 PM #57
Originally Posted by nike123
At low pressures the equivalent saturation temperature can significantly change due a small pressure loss (or bad data from gauge). While at higher pressures the effect of pressure loss ( or again bad data) present much less of an issue.
If you will forgive the IP units... A difference of 1 psi in the gauge reading can amount to as much as 5 or 6 degrees temperature change at low temperature (depending on the refrigerant). At high temperatures, a pressure difference of 1 psi may only be equivalent to 1 degree or less.
So yes, the accuracy of the gauges and data used is very important. On a low temperature display case that might be set for 6-8 degrees (evaporator superheat in Fahrenheit scale) an error of 3 or 4 degrees due to bad data could cause the compressors to run hot or flood.Last edited by US Iceman; 14-04-2008 at 03:36 PM. Reason: added details
16-04-2008, 10:14 PM #58
17-04-2008, 09:02 AM #59
19-04-2008, 12:07 AM #60
So on a large capacity system then, with the correct valve orifice installed, but an incorrectly set superheat operating at 3K superheat, the valve would fully close to prevent liquid entering the compressor? What if it is a large packaged unit with a very short suction line and a loss of duty over the evaporator? After the valve has closed there will still be a large amount of liquid in the evaporator and with no duty to heat the refrigerant, liquid will enter the compressor for a short period.
I agree in principal with what you say, but with the precursor that the TXV should be set up by the commissioning engineer and only be left at the factory set adjustment if it has been tested and found to be acceptable, or, as required by the system designer/manufacturer.
If the valves are always correct then maybe I shouldn't bother to check the superheat if I have a reasonable head pressure and 5k of subcooling at the valve inlet.
I think it is too easy for all of us, (including me), to generalise about how each system we encounter would operate in such circumstances. There are too many variables from system to system. I don't think any of us here sit on fence. Some, like me feel each valve should be checked and adjusted, others feel they should be left alone. A case for agreeing to disagree, but it is an interesting debateMy tools. Screw driver, Hammer & a Condom:
If you can't fix it, hit it. If you can't hit it, F**k it!
19-04-2008, 02:46 AM #61
Let's compromise and say the TXV's should only be adjusted when you have a very good reason and understand what you are doing. Otherwise leave them alone.
19-04-2008, 12:51 PM #62
This has to be the last comment really on this debate as I think all reasons for and against the adjustment of t.e.v s have been made. But everyone has their own beliefs on this subject and must decide for themslves whenever if or why the valve should be adjusted. I personally do not interfere with the adjustment screw but i select different orifice sizes. A most interesting debate.
19-04-2008, 10:00 PM #63
Thanks guys. A very good debate. No winners or losers though
20-04-2008, 02:18 AM #64
Are you throwing in the towel?
This was a good discussion and now it's recorded for posterity for one and all.If all else fails, ask for help.
20-04-2008, 01:14 PM #65
21-04-2008, 09:50 PM #66
Hello guys
I am new here
But I think superheat should be checked (and adjusted if needed)on commissioning because you can never be shore what they did in the factory
16-06-2008, 07:04 PM #67
Commissioning is about adjusting the system components to achieve the rated capacity and capability of the system. However, there is a logic in this same process. MRcoolingMAGIC, hits it directly. During start-ups the system/room is hot. You have to allow the system to stabilize down to operating conditions reasonably close to what the norm might be.
At that point you can adjust the pressure switches, thermostats, etc. And during this time CHECK the evaporator & suction superheats (but don't adjust them yet!).
If you try to adjust a TXV during pull-down of the load you will be on the job for weeks trying to fix it.!If all else fails, ask for help.
21-06-2008, 10:00 AM #68
[quote=US Iceman;96656]Aha! Now we are getting down to the real basics.
You cannot get more evaporator superheat than you have temperature difference between the entering air temperature and the saturated evaporating temperature. . . Therefore, if someone tells you they have the valve set for 15°F (8.3°K) of superheat, ask them to prove it!
Oh that wonderful word "superheat" just how it evokes a discussion.
Maybe we should first all agree to the definition of superheat and what it actually is? Because I'll bet my new digital gauges that we get more than one answer to this question.
Who wants to start?
30-06-2008, 05:41 AM #69
[quote=nevgee;110646]
OK I'll bite
To measure evaporator superheat:
1) Record the actual temperature at the TXV bulb.
2) Record the evaporating pressure at the TXV bulb.
3) Convert the evaporating pressure to temperature by using those handy pocket pressure/temperature cards. These cards/charts show the saturation pressure/temperature relationship for those refrigerants.
4) Subtract the temperature you converted on the pressure/temperature card from the actual temperature you recorded at the TXV bulb.
5) The difference is the actual evaporator superheat
as you can see this is a copy and paste, the thing that is not mentioned in this is the swing you get as your TXV opens and closes with demand. It takes time to set a valve properly you have to watch the case and use your lowest temp reading and check your pressure on that swing. If you have electronic SORIT valves your pressure also changes with demand.
To set the valves properly takes time. And to answer the begining of this thread. YES every valve should be checked for proper superheat before a store is turned over.
30-06-2008, 09:51 AM #70
13-07-2008, 05:38 AM #71
The system has to be in a stable condition to adjust the TXV when you have to do it. No capacity changes, no changes in the evaporating pressure, nothing. Any chnage leads to a potentially unstable valve setting.
If the system operation is unstable, then this is what you end up doing:
You just wear yourself out and don't get anywhere.If all else fails, ask for help.
14-07-2008, 11:46 PM #72
I totally agree US Iceman, we spend the first week with vacuums, leak checking, gassing up, making sure all the fans are running and there are no flood backs to the compressors ect. then we leave for a week sometimes two these are new store startups so we can do that. When we get back to the store the gas and oil has found its place, that is when we start superheats. We get them as close as possible at that point, sometimes once the cases are loaded some more adjustments are needed but not much or many.
15-07-2008, 12:15 AM #73
Originally Posted by iceburg
What effect does the added mass of the product in the cases have? It helps to stabilize the loads thus reducing any erratic swings that may occur. Reducing the swings also helps to stabilize the loads, and hence smooth out the operation of the refrigeration system.
It's the same thing as an empty refrigerator. Open the door on an empty fridge and the temperatures shoot up. Open the door on a full fridge and the temperatures are moderated due to the added mass.If all else fails, ask for help.
14-06-2009, 06:17 AM #74
I'm not sure that a "newby" should be posting in this older thread, but (unfortunately) that link has gone "404". I do see wonderful Threads on this BBoard, which probably provide even better information... but is that Sporlan PDF still available anywhere else? Meanwhile- I have question, and it's exactly this topic: "TXV, stay with factory-provided non-adjustable, or replace it with an Adjustable, sized smaller to match compressor?"
Here's my sad history. I'm in USA, a homeowner with pretty much a new installation. (R410A) It's "pretty much new" due to a tech from a now-fired company trying to fix hunting and inadequate cooling, on a second call-back, by adding more charge, and more charge, and more charge... And it all blew up after he left. (Probably the Evap first, but the Compressor quickly followed.) Now to the point and question: I'm definitely not DIY, and my new tech (new company) seems way more competent. But I think that my configuration DOES call for upgrade of the factory-installed TXV to an adjustable, smaller sized TXV for several reasons:
- The Evaporator Coil (from USA company 'Advanced Distributor Products') is oversized relative to compressor (17.5 kW versus 12.25 kW), for efficiency reasons.
- altitude 5200 ft (yes, WAY up).
- lineset > 50 ft, with about seven 90 degree turns (some "sharp", others "soft").
ADP supplies this Evaporator Coil with an R410a TXV. It's a nonadjustable Emerson, the older Type-A, not the brand new Type-C. (So it's == Alco, IIRC.) Factory labels the part to be nominally capable of anything from 12.25 kW (42,000 BTUH) to the full Evaporator rating of 17.5 kW (60,000 BTUH). My Trane compressor is labeled at the absolute bottom of this range.
So, I'm thinking that the TXV had better be operating nearly closed most of the time.
And I don't like that idea, or the thought of it maybe trying to open up so wide as to generate bubbles in the incoming liquid line (from the less capable compressor). I saw severe hunting before, after the first recharge... although other service errors, including crud left in the lines, may have played a role at that time too.
The only way to tune this one-size-fits-all Emerson is by adding or removing charge. (subcooling OR superheat, not both). And the flowrate "curve" is probably too "steep" anyway.) So I'm inclined to buy a Danfoss TR6 "universal upgrade" kit for him to swap in, before doing the final N2 blow-out and charging. Nominal size 4 tons (14.0 kW). Although some of you say that Danfoss makes 'em a lot "bigger" than the BTUH rating, I think that this would still be a better match for the 12.25 kW compressor than the factory-provided Emerson. (And even if the slope is still too "steep", at least some adjustment can be done via spring tension.) Should I maybe buy the Danfoss kit all the way down at "3 tons" nominal size?
The one thing I won't like to do to the new guy is to make him charge it up, run, and test using the factory provided Emerson-- then find that I'm HATING the performance measurements, make him recover it all, then replace the TXV, then re-do the vacuum test and blow out with N2 (again) and re-vacuum (again), initial charge up (again), stabilize for measurements and charge adjustment (again), make changes, wait for it to stabilize (again) ... not a good way to win friends. So I'm inclined to ask him to take it out, replace it with the Danfoss right at the start of the call. BTW, Trane also discontinued the "factory authorized service" relationship with my original installers, and my "new" guys are Trane's current representatives here.
Thanks for reading all this. BTW, it's A/C only (not a Heat pump), and outdoor temps here in Reno do exceed 100F (several times each year). But humidity is extremely low, all I need is the cooling.
14-06-2009, 06:52 AM #75
- Sep 2007
- Split Croatia
- 57
- 6,151
- 6
- 36
14-06-2009, 07:03 AM #76
All my installation's I Check superheat A/C 10-12F medium temp 8-10F low temp 6-8F this is what Copeland requires
also doing so you will make sure that you get the most out of the coil and customer saves on electricity by unit shouting off quicker
14-06-2009, 08:10 AM #77
^^ Thanks nike - good to see you around.
14-06-2009, 08:14 AM #78
- Sep 2007
- Split Croatia
- 57
- 6,151
- 6
- 36
14-06-2009, 09:15 AM #79
15-06-2009, 06:21 AM #80
Thanks, VERY much!
First, let me thank Nike for the link to all those "collected" downloads.
But second, I'd like to thank EVERYONE for the clear and full postings on this subject, in both this Thread and elsewhere on the forum. I'm going to proceed with the Danfoss TR6 "upgrade", at the slightly smaller nominal size of only 36,000 BTUH. (There seems to be a lot of agreement that the "slope" on Danfoss TXV's behaves a bit bigger than their labeled sizes, and there's a good deal of extra "headroom" available for hottest weather too.)
And, as you've all emphasized: No fine-tuning of the valve spring for "best" superheat until AFTER high-side pressures are exactly correct, with fairly conservative subcooling at the TXV inlet, during a lengthy run-in.
15-06-2009, 03:45 PM #81
I too am a Supermarket Fridgie and have been watching this disscussion with much relish ! In any given situation any of your scenarios are correct ! Brand new installations very seldomly does a t.x.v fail when new, however does any one give any consideration to the underpaid possibly underskilled fabricator putting these cabinets together in the factory? The T in T.X.V stands for thermostatic which relates to the crosscharged powerhead Controlling the metering of the valve in question! Surely a potentialy overheated power head would result in incorrect metering due to incorrect control pressures in the sensing bulb? I have seen powerheads where the liquid charge has ended up in the powerhead not the sensing bulb! I have also seen T.X.V's where the control pins are bent/siezed, we do not live in a perfect world, unless your the guy taking the O.E.M part out of the box dont trust it. Super heats should be checked , but adjustment comes down to the installation ! Infact I have noticed a growing trend in cabinet manufacturers putting non-adjustable T.X.V'S in there cabinets ! Gee I wonder why ? Because the average apprentice/junior tradesman are not sufficently trained to competetly understand how to either correctly check/adjust correctly a superheat on an average commercial installation! We are not talking about a commisioning engineer with 10+yrs experience we are talking about the Engineers sent to maintain these systems over nuemerous years! One incorrect adjustment every six months over ten yrs can be pretty detrimental to a markets performance! Training costs money and time 4 years and your Qualified Yeah right 10 years minium!
How do you check a superheat on a rack-system with a floating suction pressure ? The answer is you check it the same way as you would on any other refrigeration system, (not gonna get in to basics) however more leeway should be given to your superheat a range of 4-6 KTD above your SST ! Set it forget it walkaway, comeback the next day (unless your lucky enough to have data logging equipment in your kit) However this doesnt take into account cabinets that due to poor design running perfectly acceptable superheats will not actually control the cabinet temperature, What do you do then, change the orifice size up? Perhaps due to a gap in orifice sizing this doubles the capacity of the valve. Not suitable, valve hunting! Perhaps you run a superheat of 1KTD and adjust your defrost perameters to suit ! Lets face facts no one is gonna let you redesign the wheel, that costs money, they naint gonna pay! I have seen market quotes almost halved once the consultants have stripped out all your control gear such as E.P.R'S and sorit valves, decent controls etc.
As for old markets if ya onto makin money for your boss just change it, owner/manager at least knows you've done something, with out you rambling on about heat added after your subcooled refrigerant entering BLAH BLAH BLAH If it worked for 5 years and doesn't now....
Sorry for the long winded post!
15-06-2009, 04:54 PM #82
15-06-2009, 05:07 PM #83
Re: save time while preventing from poison
Hi everybody Is there anything available in the market that can show the quantity of refrigerant charged in a system by just connecting it in to the system? plz. comment.
15-06-2009, 06:10 PM #84
No, there is no way to tell the amount of refrigerant in a system short of removing the charge and weighing it.
You can however tell if there is too much or too little refrigerant in the system by using temperature and pressure measurements to first confirm sufficient airflow through both coils, then check subcooling and superheat (with the refrigerated space at or near it's design temp).
15-06-2009, 06:28 PM #85
To get back to the subject:
When the superheat is low, the least likely cause is the TXV adjustment.
When the superheat is high, the least likely cause is the TXV adjustment.
Once adjusted properly (at commissioning, if needed) the TXV almost never loses it's adjustment.
If the superheat is not what you think it should be, look elsewhere for the problem.
15-06-2009, 06:38 PM #86
18-06-2009, 07:48 AM #87
Re: We're adjusting, and I TXV's To Adjust or Not to Adjust - That is ....
Your 'guess' is the first place I'd look, too. But airflow is excellent, absolute bulb temps are excellent, humidity control and overall cooling are already pretty good. After today's commissioning, I'm willing to guess that it will be VERY close to optimal and it's VERY close to optimal after about one full twist towards more more flow, and maybe some recovery of coolant to reduce excess SC.
But thiswas as "close" as we were willing to go today; outdoor ambient temps were barely 80F today, the real "tuning" needs should be for standard conditions (As close as we want to "try" when ambient temps are so low-- barely 80F today.) Here's what we've got, and what we did:
42,000 BTUH compressor, Trane XL14i.
60,000 Evaporator, Advanced Distributor Products ("ADP")
Note: This is an ARI certified combination at SEER 14.00, although my electric costs always seemed a bit too high, even when new.
Upgrade: Danfoss "TR6" TEV, nominal size 36,000 BTUH.
All 3 components are new. (Lineset and Condenser Coil are unchanged.) We removed the ADP-provided TEV, installed the Danfoss. Also installed a Schrader valve near the evaporator, in front of the TEV, to check pressure/subcooling directly at the TEV (that's where it REALLY matters). As a frivolous enhancement, and because I had a small tube of the stuff lying around after a computer upgrade, I put some high quality thermal-transfer compound around the "contact line" between the Danfoss bulb and the return line, before wrapping it all up with insulation. (Arctic Silver #5. I figure, better thermal contact == better accuracy.)
We did have a concern which prevents "fine tuning" today: Outdoor temps barely reached 80F, and the lineset has almost 25 feet through my attic (over a 3-car garage). When the outdoor temp exceeds 100F, common in July, temps in that space can reach 120+. We might have to insulate the liquid line, even though that gives up advantageous heat loss from the naked copper in more moderate conditions. One thing's for sure: Today, the liquid line was able to give off plenty of heat to ambient, even in the attic.
Vapor line goes through that same attic, opf course, with only 3/8" "pipe noodles" as insulation. That's grossly inadequate and will be upgraded. Now remember, my house is at 5000+ ft, so we used a high altitude R410A pressure versus temp chart.
After installation and charge-up (done properly) we had our first surprise: Line set is almost 40 feet long, one way, at Trane-specified diameters, but upon start up, subcooling was almost 20F at the outdoor coil, and even higher in front of the TXV. But superheat was also excessive (28F, even with my cruddy "noodles" insulation), so we concluded that the first thing to do was adjust the TXV for more flow-- before recovering any "unneeded" refrigerant.
The need for "more flow" didn't surprise us at all-- big Evaporator, slightly undersized model of the Danfoss TR6. But the fact that the big Evaporator AND lengthy line set hadn't called for additional charge, IMMEDIATELY, upon the first start up, was a surprise. We'd expected to see lower pressure on the liquid line, but pressures were high-- at the TEV, and back at the outdoor Service tap too.
After 3/4 turn counterclockwise (more flow, less "excess" superheat), and 15 minutes of running time, superheat was stable at 16F (a bit to high, even for "lazy" commissioning, and far too much for optimum performance-- but going the right direction.) liquid pressure and subcooling fell by only a tiny bit. That's what we expected with R410A, but we chose to at least "ballpark" the superheat before recovering coolant from the factory charge. While he did a bit of coolant recovery (his department, I'm not licensed!) I loosened the TEV spring adjustment by another 1/4 turn.
And that's where we have left it: Superheat is now 13F, subcooling at the outdoor service port is 12F. Greater SC at the TEV, but some of that "excessive" SC at the TEV is partly due to heat loss along the naked line in low attic temperatures. I'll have him come back for final settings on a much hotter afternoon in July, when the attic nearly as hot as it can get (and both lines are insulated against that heat). At that time, we'll adjust for much tighter settings: About 4F subcooling (in front of the TEV), and about 6F superheat (in front of the compressor). Total Pressures are just slightly off from Trane design specs already. Just a few PSI on both sides (increase on Vapor side, decrease on liquid side.)
- - - my summary - - -
Well, it took considerable time and money. (TXV was only $70, but I also had to buy a pound of low temp, high-silver solder-- and in USA, it's almost impossible to obtain the old lead-based stuff. (So I bought J.W. Harris Stay-Brite #8, a non-lead non-cadmium premium product, at nearly $45 shipped.) I handed my installer the almost-full spool, as a gift, at the end of the install. But for a fully-equiped pro, the TEV and maybe a couple of new Service Ports are the only hardware items-- hundred bucks or so, unless you go with cheapo Schrader valves (and depend on no-loss adapterd for connecting/disconnecting measuring equipment while pressurized.)
Even with the all the finicky wet towel wrapping, he was done with the TEV in only 45 minutes. (I did provide a spare hand in the process, spraying water to keep the paper towels well soaked.) We did, however, make a major mistake with our install: ADP had mounted the non-adjustable "one size fits all" TEV inside the cabinet; and, without thinking enough, we put the new one exactly where the old one hads been.
WRONG! Each of the 3 adjustments required removal of the case panels, a bit hard to get at, with several minutes of flex-duct taping to seal all BIG gaps surrounding the FOUR (4, WTF ???) drainage connector sockets. (Rectangular cutouts in the panel for pairs of round PVC drainage connectors, huge amounts of leakage before taping.) And of course, removal of the panels requires that the A/C be shut down to avoid blowing indoor air all over the place. We should have mounted the new TEV in a segment of horizontal liquid line OUTSIDE of the evaporator coil case. So the "tuning steps" took almost two hours; run continously, when adjustment made while running, it would have taken barely 45 minutes.
ADP, in contrast, didn't even insulate the bulb of the "one-size-fits-all" TEV. And here's the instructions:
1. Run system for at least 10 minutes to allow pressure to stabilize.
2. Add or recover refrigerant until subcooling matches this table: Min=10F, Nominal=12F, Max=14F.
3. Then, if equipped, adjust the valve until the superheat matches this table: Min 8F, Nominal 10F, Max 12F.
My theory on this step is: you check the high side pressure and temp at the outdoor Service Point only to confirm that it isn't badly wrong or widely different than the pre-TEV measurements. Big looses of pressure imply restriction, (needing clean up or filter replacement), or perhaps a missed leak. (Shouldn't be there, though, because YOU CHECKED.) Any GAINS in temperature need to be prevented. Actual "tuning" of charge and SC should be based on measurement at the TEV, and more than 4F (excluding undependable temp losses in cool outdor conditions) is making the compressor work too hard, and wasting electricity.
But it's their step 3 where they really fell on their faces. "If equipped, adjust the valve until the superheat matches the table." They don't offer an adjustable TXV, you have to buy one yourself. As I just did. Furthermore, their installation guide says tht it's important to match the size of your compressor, but they sell only two sizes: One for everything up to 3.5 tons, And the other for 3.5 all the way to 5.
Adjustable spring tension alone can't make a TEV respond to varying conditions. You CAN crank the spring up or down for one set of conditions, but if the orrifice size is wrong, the adjustments won't work right-- you'll tend towards flooding in one direction, and tend towards starvation in the other. All the mfgrs make a much greater number of products than ADP offers: one size for 12,000 BTUH, another size for 18,000 BTUH, another size for 24,000 BTUH, and yet another size for 36,000 BTUH! ADP makes it easy to order, with just one product for R410a and the other for R22, but the one size can't really work well for all of these different compressor sizes.
It's already working quite well, and So I'm already delighted with the
18-06-2009, 08:17 AM #88
Oops! wrong title, unfinished post.
I somehow did a "submit" by accident while editing that title. Should have been "We're adjusting, love the results so far."
And the end wasn't really finished. It's already working quite well. But we can almost definitely take another 9F from that excess Superheat, after improving insulation, via raising flow. Maybe even more. And the subcooling (excess charge) can maybe take a hit too, although ambient temp loss along the liquid line won't be as good as it was today when outdoor temps go up a lot.
9F in superheat is just HUGE for efficiency. I expect the payback on this $70 device, plus $150 or so for the service call, to be less than 3 years.
The only real problem? I've only got about one turn left towards "more flow" on the 3-ton TR6, and this is not a replaceable-orrifice model. If I hit the end of adjustment, it's a complete swap-out to upgrade to the 4 ton. (But hey, this time we'd install it on the OUTSIDE the case! ).
18-06-2009, 09:06 AM #89
Yep, and so did the factory guys! The ADP pre-installed TXV was entirely screw-in: output to distributor, and low-side schrader port, AND input side. They even used a non-adjustable open-sided springsteel clamping piece for the bulb, to prevent some idiot from overtightening a traditional clamp and crushing something expensive.
The only thing the "monkeys" could do wrong, really, was crush or kink the the small tubes (the low-side pressure port, and/or the sensing bulb connector). No solder needed or allowed!
As you proclaimed, it was a non-adjustable: saves installation time to just assume it's good and RUN AWAY to the next commissioning job, and leaving way too much SH present reduces the chance of expensive callbacks for liquid-in-the-return-induced compressor damage.
Who will actually NOTICE that efficiency went to heck from a careless install, when the customer bought it according to a piece of paper which said "EER of 14.25" or "SEER 18.00" and never learned how critical it is for the installer to take time to tune their specific installation to reach that performance level?
Hardly anyone. except for customers like me.
BTW, they didn't insulate the sensing bulb, either. Takes time, time is money, and who's ever gonna know that insulation was needed in order to get decent temp measurements?
18-06-2009, 06:58 PM #90
With all due respect, "excellent" is an opinion, not a measurement.
Until I see the temperature of the air entering the coil and the temperature of the air leaving the coil, the airflow is still highly suspect... and if the airflow (through both coils) is not right, then the SC and SH will not be right. Airflow is crucial.Last edited by Gary; 18-06-2009 at 07:09 PM.
18-06-2009, 07:03 PM #91
18-06-2009, 07:13 PM #92
18-06-2009, 09:11 PM #93
The evaporator capacity is rated at 140% of the compressor capacity and the TXV is rated at 86% of the compressor capacity. This would indicate the suction pressure could be too high to do sufficient dehumidifying and the TXV would have to opened up to achieve sufficient flow capacity.
BTW, this should have been a separate thread for your discussion.If all else fails, ask for help.
19-06-2009, 05:04 PM #94
back to original title to adjust or not to adjust.adjust otherwise you would not be able to,why is this screw there ?
20-06-2009, 11:03 AM #95
of course TXV need to be set after case start up. Say you have 4 identical cases on a system all with external equalised valves and number 3 orifice and you start them up and wait for the sysytem to settle and come down to temperature. You can physically see some valves need to be set before you have even attached your gauges and thermocouple. Some coils look like they arent doing a thing and some a flooding back. connect gauges and what do you see? too much superheat and too little superheat respectively. answer? set the TX valve.
Everything You Need To Know About TXV's
By marc5180 in forum FundamentalsReplies: 12Last Post: 06-03-2008, 11:12 AM -
How to test TXVs' capacity
By liujunwei in forum FundamentalsReplies: 3Last Post: 28-01-2008, 09:03 AM -
How to adjust head on a water cooled condenser
By kengineering in forum Technical SpeculationsReplies: 5Last Post: 30-05-2007, 10:37 PM -
Basics of TXV's
By US Iceman in forum FundamentalsReplies: 5Last Post: 21-05-2007, 03:27 PM -
heat pump capacity adjust
By Lc_shi in forum FundamentalsReplies: 5Last Post: 14-02-2006, 07:32 AM