Results 1 to 4 of 4
  1. #1
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18
    Reseting e3 fault on vrv p series
    Hello
    I had some problem when reseting e3 fault on VRV III : impossible to reset by the remote control...or by power off even by the outdoor reset button...
    I called the french help line they said " you need a technical engineer to go on site he will reset the system " ok i said how much: " 300 euros ". Hope my system won't tripping on e3 next days !!!
    I finaly find a way: i send a nasty request to daikin europe extranet and finaly reach a very kind engineer by phone! the same day !!!
    The question is: how long will this business last !!!
    I work on daikin's product since 1986 and do not want help like just pushing a switch for 300 euros !!
    If someone's interesting in i can tell about this "special" reset...if not try the help line in your country...
    rgds
    cool#9
  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    70
    Posts
    4,702
    Rep Power
    47
    Re: Reseting e3 fault on vrv p series
    Hey cool#9
    I am up for it!
    Drop me a line please.
    I have to say it might be the Galic attitude?
    Coz in U.K. they are extremely helpful!
    Grizzly
  3. #3
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17
    you should be able to push the return button and it should reset if the high pressure switch has already reset.
  4. #4
    Join Date
    Oct 2006
    Location
    UK
    Age
    57
    Posts
    165
    Rep Power
    18
    Quote Originally Posted by cool#9 View Post
    Hello
    rgds
    cool#9
    Dear all,
    The VRVIII and ERX A series require you to unlock the high pressure trip by pressing the return button once on the outdoor unit. (something to do with an EU regulation)
    However you can go back to the old method by programming mode 2, code 15, setting binary 2 on the outdoor unit. Now you do not have to unlock the high pressure trip. Just reset from the indoor units in the normal way.
    Obi Wan
Similar Threads
  1. Sullair C Series and CB Series
    By Oz Fridgey in forum Industrial Compressors
    Last Post: 18-02-2009, 09:44 PM
  2. Daikin G series LO fault
    By Tim_l in forum Air Conditioning
    Last Post: 30-11-2008, 09:44 PM
  3. New to RE and needing Daikin Help
    By Owen in forum Air Conditioning
    Last Post: 25-09-2008, 06:55 PM
  4. Fault with Tango cassette