Carrier water cooled split
Hi Guys anybody know anything about these units I have a system which Im trying to ID the Kw size
the only info I have is:
Indoor:40GKWX348W-703-40
Outdoor :07KD036C9
Ref: R22
cHEERS IN ADVANCE
-
08-06-2009, 11:00 PM #2
Re: Carrier water cooled split
That size, 36, is 9.4kW cooling.
Data table here
http://eto.carrier.com/litterature/t...&lang_id=1.pdf
If you want all the info on that model then start here...
http://eto.carrier.com/lit.asp
Click on 07KD in first box then select 'all types' in second box, press search.
Do similar if you want the indoor unit stuff as well.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
10-06-2009, 01:11 AM #3
Re: Carrier water cooled split
Carrier's nomenclature is based on 1,000's of Btu/hr. So the 07 (water cooled), KD model series, "036" is a nominal 36,000Btu/hr or 10.5kW. 9 or 913 or 903 at the end normally denotes a 3phase supply while 7 or 703 denotes 1 phase supply.
Not sure if you've got the indoor unit number right. 40 series units are DX fan coils, GKWX could be OK, but 348 does not look right. O48 would be my guess (48,000BTU/hr). The 703 is 1 phase.
Either way you are looking at a 9-10.5kW system.If in doubt read the instructions. If still in doubt follow them.
Similar Threads
-
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
pure water from air
By Lc_shi in forum New TechnologiesReplies: 32Last Post: 26-02-2009, 12:25 PM -
water cooled subcooler?
By star882 in forum Technical SpeculationsReplies: 1Last Post: 29-12-2007, 11:21 PM -
Making a simple water cooled condenser
By The MG Pony in forum FundamentalsReplies: 19Last Post: 01-08-2007, 11:02 AM -
Building a wine cabinet
By Rory in forum Technical DiscussionsReplies: 38Last Post: 13-07-2004, 08:28 PM