    York chiller with J body compressors
    Hi all, could someone PLEASE give me the torque settings for the electical terminal posts on the J body recip compressors. I have already broken two from over tightening!
    York in the the UK has been taken over by Johnson Controls and getting technical info a no way. I have the manuals for the chiller, but there aren`t any torque settings for any bolts. I am also replacing all the head and oil pump gaskets, so those settings would be a bonus.
    Many thanks!
  2. #2
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23
    Re: York chiller with J body compressors
    Hi Burrah Boy
    These are in LB.FT
    Terminal Block 34-40
    Terminal Stud (Nut) 20-25
    Oil Pump 27-32
    Access Cover / Top Head 78-90
    Good Luck
  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    70
    Posts
    4,700
    Rep Power
    47
    Burrah Boy
    You may have been misled?
    Because the early J comp studs are steel (copper coated).
    The later ones are Copper and it is not easy to tell.
    York recommend using a magnet to determine which type you have.
    Because of this there are 2 torque settings dependant upon which stud you have.
    The above torque is for steel and the copper is 19-22ft lbs
    Grizzly
  4. #4
    Join Date
    Mar 2008
    Location
    United Kingdom
    Age
    54
    Posts
    35
    Rep Power
    0
    Thanks Grizzly one! The ones I broke are the copper ones, and the new ones they sent seem to be steel!
  5. #5
    Join Date
    Mar 2008
    Location
    United Kingdom
    Age
    54
    Posts
    35
    Rep Power
    0
    Sorry, forgot to thank TESLA to!
  6. #6
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    70
    Posts
    4,700
    Rep Power
    47
    Burrah Boy.
    If you open the attached you will notice there is a gap between the top 2 nuts and the bottom one clamping the terminal post in place.
    It is quite common for the fitter to bottom out the 2 top nuts against the bottom one.
    Which will cause either the stud to shear or the baseplate to crack.
    Therefore it is very important to hold the middle nut in place away from the base nut, whilst tightening.
    This is a very common mistake!
    You may well be aware of this but someone may benefit from the extra knowledge?
    Grizzly
  7. #7
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    17
    Quote Originally Posted by Grizzly View Post
    Grizzly
    thats why i love to reed your posts Griz,i never fiele to old to learn something.
    Ice
  8. #8
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    70
    Posts
    4,700
    Rep Power
    47
    Quote Originally Posted by icecube51 View Post
    thats why i love to reed your posts Griz,i never feel to old to learn something.
    Ice
    You make me blush SIR!
    Sadly growing old is a heavy price to pay in the pursuit of knowledge!
    Hopefully we all benefit from our posts...
    Even if it's only to admit when we are wrong.
    Have a good day!
    Grizzly
  9. #9
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38
    Griz, you are a legend. Stand up and take a bow.
    magoo
  10. #10
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,451
    Rep Power
    41
    I'll second or third that, i'd definately be lost without him!
    al
Similar Threads
  1. York Chiller problems
    By ingherrera in forum Commercial
    Last Post: 26-07-2011, 03:10 PM
  2. Compressors - screw or reciprocating?
    By Josip in forum Industrial Compressors
    Last Post: 27-01-2009, 10:36 PM
  3. York Chiller startup when on Emergency Power
    By Apollo10 in forum Trouble Shooting
    Last Post: 22-12-2008, 07:13 PM
  4. need help on YORK chiller
    By nassersh in forum Commercial
    Last Post: 16-12-2008, 12:47 PM
  5. york chiller motor rotation error
    By cesarnino in forum Trouble Shooting
    Last Post: 13-12-2008, 03:43 PM
Posting Permissions
  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts